my elec boys said most 100 amp service could handle double so yer ok man not to code but ok.... crank it..........
Your "electricty boys" are referring to a 2 phase 120 v breaker in which case yes each phase does have 100 amps. What they mean by this is that typically a house has a 100a breaker. And usually you actually have two separate wires coming in. Each of these wires is capable of supplying 100a at 120 v. That means if your running 110 you actually have 200a before one pole or the other maxes out and flips the breaker.
If a 3 phase has 3 hots legs, does that mean equipment wired at 220/240 use 2 legs and equipment at 120v use one hot leg?
The three legs have to each be 120 for this to be true.
A three-phase 100A service has 3 hot legs, L1, L2, and L3. Each is capable of supplying 100A
This is true for some 3 phase but not all. Be Careful and read inside the breaker box. If you have a "C high leg" or a high leg or anything of the sort than that third leg is in a different voltage than 120. If such is the case you can not use this leg without the use of a transformer or equipment that runs at that voltage.
He mentioned he had a 208 volt 3 phase. I pretty sure that means L1 is 120 L2 is 120 and L3 is 208 v.
so noone88 to answer your original question, "am i maximizeing my power?"
the answer is no. If you wanted to do that you'd have to pull 100 amps of 208 and 100 amps of 240. Consider purchasing equipment that runs on 208.
Any reason why your running 220 and not 120?
A common myth is that you can run more lights with 240. That is not true. The only benefit is you can run a thinner wire to your sub panel. In the US the hassle just isn't worth it to me