Away for 48 hours. Major malfunction or poor planning?.
High heat created deathly results for girls. 15 x 1000w with AC unit room temp raised to 130 AC frozen solid. What would you set the temp to for maintaining 77 at top of buckets?
 
highland420

highland420

58
8
AC unit may have lack of adequate refrigerant. Ordered pressure testing kit, hose kit and refrigerant refill . If low charge, will recharge and monitor room for 72 hours with all lights running.
 
deacon1503

deacon1503

1,224
113
Frozen coils or lines are bc of either low air flow or low refrigerant. Double check your superheat.
 
Oom pah pah

Oom pah pah

Loompa Farms
580
243
Is the ac running out doors in cold temps .I ve seen a window unit freeze up because it was running in the winter. High temp shutoffs are a valuable piece of insurance.
 
highland420

highland420

58
8
An expensive learning experience in the making. It appears that a kink in the refrigerant tubing caused problem. Now my compressor high limit pressure sensor has tripped. The plan is to replace the tubing and bleed of refrigerant and evaluate the situation.

NOTE TO SELF: Do not try to rush the end of the job when you are physically and mentally drained.
 
highland420

highland420

58
8
Power issue. Don't get the wrong fuses. Double check the power supply. Now she's cooling awesome.
 