indogro

Posts
66
Reactions
30
Joined
Aug 16, 2012
Points
18
Apr 23, 2013
#421
My rental home has 200 amps of power coming in. with a 100amp sub panel going to an outside workshop.

I'm interested in having a 200 amp panel connected directly to the workshop, and 200 amps for the home.

Does anyone have any experience doing this? Do I need an electrician, or must I have PG&E do this themselves?
 
Quote Reply

KUSHPILES

Posts
138
Reactions
167
Joined
Mar 31, 2013
Points
43
Apr 23, 2013
#422
You need your local power provider to aprove a service upgrade to the residence. Then they come in and cut the power, you have your electrician do the work on your end and they reconnect you when all is done. Sometimes thats much easier said than done, the last servie upgrade I did, the tube the old 150 amp main was run through going to the house pannel was cracked and roots from a tree blocked the way, so they had to re-dig a trench and lay a new 300 amp wire to the new pannel. This included 3 BC hydro trucks, a gas company had to OK everything before they could dig, and another BC hydro contractor there to dig-NOT stealthy.

On this same job, 6 other houses on the blocks power got cut for like 4 hours as the main at the road was older and couldn't handle the 300 amps as well, so a couple neighbours complained as the power company is supposed to give notice on outages.

Normally its straight forward to do a service upgrade but theres an example of what can go wrong..
 
Reactions: reloader and ttystikk
Quote Reply

indogro

Posts
66
Reactions
30
Joined
Aug 16, 2012
Points
18
Apr 23, 2013
#423
my incoming power line is not buried, but off a pole. 200 amps comin in. I'm looking to get an additional 200 amp panel directly to the shop, straight from the pole. I assume only the power company can connect that to the shop from the pole, not my electrician. OR do I need to get 300 amps to the house, (100 amp upgrade) and then split off from my sub panel?

Can I do this as a renter, or do I need the landlord to do it since I will need PG&E to connect an additional 200 amps to the property?

Thank you!
 
Quote Reply

KUSHPILES

Posts
138
Reactions
167
Joined
Mar 31, 2013
Points
43
Apr 23, 2013
#424
indogro said:
my incoming power line is not buried, but off a pole. 200 amps comin in. I'm looking to get an additional 200 amp panel directly to the shop, straight from the pole. I assume only the power company can connect that to the shop from the pole, not my electrician. OR do I need to get 300 amps to the house, (100 amp upgrade) and then split off from my sub panel?

Can I do this as a renter, or do I need the landlord to do it since I will need PG&E to connect an additional 200 amps to the property?

Thank you!
Click to expand...
Im not sure if you have to go to the house first or not in your situation, I can tell you for sure that you can absolutely not do this as a renter. Where im from, the home owner has to get a building permit of some kind before anything can happen. Thats about all I can say on this subject, but you would without a doubt have to consult the home owner.
 
Reactions: fishwhistle and ttystikk
Quote Reply

ttystikk

Posts
6,891
Reactions
8,392
Joined
Jan 4, 2011
Points
313
Apr 24, 2013
#425
I run a 16 light op, plus another 2k over veg and moms. The chiller, hot tub and electric stove all see use, and I'm on only 100amp service.

I could run a 40 light op with 200 amps. I'm just curious about how much bigger you really want to get without being 'legal'? ... at least legal as defined as being a licensed commercial mmj producer...
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Apr 27, 2013
#426
I've looked and can't seem to find the info I need. I want to run a lumatek 600 and a lumatek 1000 ballast on the same 20 amp circuit. the circuit is 12/2. Will the lumatek 600, and 1000 draw more than 16 amps?
 
Quote Reply

ttystikk

Posts
6,891
Reactions
8,392
Joined
Jan 4, 2011
Points
313
Apr 28, 2013
#427
SodaLicious said:
I've looked and can't seem to find the info I need. I want to run a lumatek 600 and a lumatek 1000 ballast on the same 20 amp circuit. the circuit is 12/2. Will the lumatek 600, and 1000 draw more than 16 amps?
Click to expand...

Volts x Amps = Watts. Since this is an algebra equation, you can solve for amps. Add up all the wattage you want on the circuit, divide by your line voltage, and voilà! Total amps! Be sure that you don't load the circuit over 80% with stuff that will be left running continuously, like lights.
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
May 15, 2013
#428
ttystikk said:
I run a 16 light op, plus another 2k over veg and moms. The chiller, hot tub and electric stove all see use, and I'm on only 100amp service.

I could run a 40 light op with 200 amps. I'm just curious about how much bigger you really want to get without being 'legal'? ... at least legal as defined as being a licensed commercial mmj producer...
Click to expand...
Are those 16 lights 1ks and on a flip?
 
Reactions: ttystikk
Quote Reply
U

Underground

Posts
215
Reactions
42
Joined
Oct 15, 2010
Points
28
May 15, 2013
#429
ttystikk said:
Volts x Amps = Watts. Since this is an algebra equation, you can solve for amps. Add up all the wattage you want on the circuit, divide by your line voltage, and voilà! Total amps! Be sure that you don't load the circuit over 80% with stuff that will be left running continuously, like lights.
Click to expand...
I would add to that that most mag ballasts have a 90% power factor. So take the total amps and multiply by the reciprocal of the power factor (1/.9= 1.111) And most of these ballast have a power factor of 50% before PF is corrected with capacitor. (1/.5=2) 1600/120= 13.333 but will actually draw 14.81 at 120volts. Or 26.666 if the capacitors were to pop. In some cases the lights will still run but at lower output. But will draw more current. A ballast is an inductive load. A capacitor is a capacitive load. In an inductive load, the current lags the voltage. In a capacitive load, the current leads the voltage. Which draws more power. Capacitors are added to inductive loads to correct the power factor, bringing the current closer to the voltage in the waveform. It also prevents over saturation of the iron core. That's why with some ballasts if the capacitor blows, the core of the ballast will overheat and blow the transformer.
 
Reactions: ttystikk
Quote Reply

ttystikk

Posts
6,891
Reactions
8,392
Joined
Jan 4, 2011
Points
313
May 16, 2013
#430
Thanks to underground for dropping far more knowledge than I possess. I'm going to Re read that...
 
Quote Reply

ttystikk

Posts
6,891
Reactions
8,392
Joined
Jan 4, 2011
Points
313
May 16, 2013
#431
fishwhistle said:
Are those 16 lights 1ks and on a flip?
Click to expand...

Yes on thouies, and scheduled like a flip so no more than 8kW plus veg are ever on at any time. I just don't use a flip box to achieve this.

And yes, because I'll get asked, it's all cooled by just two tons of chilling.
 
Quote Reply

Herb Forester

Posts
766
Reactions
1,442
Joined
May 6, 2013
Points
143
May 22, 2013
#432
I'm setting up a room with 3-phase 120/208v. This is new for me, although I've wired plenty of 120/240v single-phase circuits. Can anyone help me better understand how to balance the legs properly, and how to calculate total available amperage?

My ballasts and AC unit are 208v ready, and I'll also have some 120v breakers in the same subpanel.

Here's some other discussion I found on the subject: https://www.thcfarmer.com/community/threads/new-to-3-phase-208v.30680/
 
Quote Reply

Herb Forester

Posts
766
Reactions
1,442
Joined
May 6, 2013
Points
143
May 22, 2013
#433
Here's the panel I'm using. It has 12 breaker spaces with tabs for balancing the load (A-B, B-C, A-C).

 
Quote Reply
U

Underground

Posts
215
Reactions
42
Joined
Oct 15, 2010
Points
28
May 25, 2013
#434
Tabs for balancing the load? Which loads are 3 phase? Which are single phase 120 and which are single phase 208? If you are trying to balance just be sure not to switch any of the conductors of the 3 phase loads that have motors. And if they are phase rotation dependent, make sure you test and have CW phase rotation. You shouldn't really need to worry about balancing such a small panel though. Especially with only 12 ckts.
 
Reactions: Herb Forester
Quote Reply

Herb Forester

Posts
766
Reactions
1,442
Joined
May 6, 2013
Points
143
May 26, 2013
#435
Underground said:
Tabs for balancing the load? Which loads are 3 phase? Which are single phase 120 and which are single phase 208? If you are trying to balance just be sure not to switch any of the conductors of the 3 phase loads that have motors. And if they are phase rotation dependent, make sure you test and have CW phase rotation. You shouldn't really need to worry about balancing such a small panel though. Especially with only 12 ckts.
Click to expand...
By tabs I just meant there are 3 breaker contact-points for each phase, allowing for 6 2-pole breakers or up to 12 120v breakers. My 208v circuits are light controller and AC, and a few 120v for pumps, dehuey, environment/co2, etc. Good to know about the motors, not an issue in this situation though.

I did some research and think I understand 208y better now. The additional amperage capacity (compared to 240v single phase) is nice, but to take advantage of it I might need to run a ballast or two on 120v (two legs will be at 80% already). Here's a reference that made sense to me:



So do I understand you correctly that if even with two legs maxxed at 80% with 208v, it's not so crucial to balance the third leg with equivalent 120v amps? And which would be better if I only have two 2-pole breakers carrying that 80% load, 1) both breakers on the same two legs, or 2) only one common leg with each breaker using one of the remaining two legs?

Thanks for your help!
 
Quote Reply
M

mk michael

Posts
1
Joined
Jun 11, 2013
Points
1
Jun 11, 2013
#436
Anyone know anything about gree terra line mini splits. They are cheap and have a low Seer Rating. curious if they last.
 
Quote Reply
U

Underground

Posts
215
Reactions
42
Joined
Oct 15, 2010
Points
28
Jun 11, 2013
#437
Just keep it close enough for gov't work. Loads vary all the time. No you don't need to max the third just because A and B are maxed.
 
Reactions: Herb Forester
Quote Reply
A

advanced396

Posts
84
Reactions
71
Joined
Sep 21, 2010
Points
18
Jun 18, 2013
#438
Question
I'am setting up a new place. It has a 10 KVA transformer & 150 amp main breaker was wondering if I can run 16 1000 watt lights on a flip box so totaling 32 lights on off. With 5 tons ac for each room for a total of 10 tons of air. I will be running digital ballast on 240V
 
Quote Reply

Animal Chin

Supporter
Posts
1,451
Reactions
3,353
Joined
Aug 17, 2012
Points
263
Jun 19, 2013
#439
I'm hooking up a sub panel directly behind my main. I'm even connecting them with a nipple lol that's how close. My question is can I use my mains ground?
 
Quote Reply
N

Ne Obliviscaris

Posts
82
Reactions
30
Joined
May 11, 2011
Points
8
Jun 26, 2013
#440
Have any of you guys ever run 3 1000w lights off a 240v 20amp breaker?

I'm moving to a new spot and there's only room in the fusebox for two 240v breakers. I want to run 6 1000's which means three per breaker.

According to my math each light is running at 5amps (actually a little less) at 240v and so I should be able to run 3 at 15amps which is below the 80% capacity you're supposed to cap your draw at.

I realize that ballasts draw more at start up, but as long as I stagger them all by 15 minutes, I should be all good, correct?

Thanks in advance for your help.
 
Quote Reply
Page 22 of 71 · Replies 421–440 of 1,407
Prev
  • 1
  • …
  • 20
  • 21
  • 22
  • 23
  • 24
  • …
  • 71
Next
First Prev 22 of 71 Next Last

Thread info

Replies 1,406
Views 327,208
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • LB in the Lungroom Reboot
    • Latest: Lockebox
    • 11 minutes ago
    Grow Diaries
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Hossgrows
    • 25 minutes ago
    General Outdoor Growing
  • I’m Week 4 into Flowering
    • Latest: April14th2014
    • Today at 5:38 AM
    General Indoor Growing
  • B
    Virginia Growers Thread - Everything VA
    • Latest: Budtirement
    • Today at 4:48 AM
    Basic Growing Information
  • S
    So Close to Harvest yet problems have started
    • Latest: SavannA
    • Today at 2:52 AM
    Cannabis Infirmary
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?