terrapin11 said:
View attachment 692551 actually, looks like i have a 250v outlet connected to a 30a.
i was looking to purchase an adapter cord to run from that 250v outlet to plug my two phantom II digital ballasts into.

will this adapter cord work?
Click to expand...

I would not use that I would just take the plug out and install what you want
and it is a 30 amp circuit looks like there's a neutral there also but you won't need it for your 240v ballasts
I would rather take that wire out of the 4s box and install a 30 small sub panel
You could get your ballast and even a 120 V
Hb
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 18, 2017
#1,142
hiboy said:
I would not use that I would just take the plug out and install what you want
and it is a 30 amp circuit looks like there's a neutral there also but you won't need it for your 240v ballasts
I would rather take that wire out of the 4s box and install a 30 small sub panel
You could get your ballast and even a 120 V
Hb
Click to expand...
interesting.
is there any way to use this current outlet?
avoiding replacement and further installation?
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,143
terrapin11 said:
interesting.
is there any way to use this current outlet?
avoiding replacement and further installation?
Click to expand...
Doesn't look like the middle tab which is the ground matches up
You would have to get an oven cord and want to J box and then put your other outlet in and it's not worth all the trouble it's going to just change the cover plate on the box to what you need
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,144
hiboy said:
Doesn't look like the middle tab which is the ground matches up
You would have to get an oven cord and want to J box and then put your other outlet in and it's not worth all the trouble it's going to just change the cover plate on the box to what you need
Click to expand...
thing is, i rent.
i'm just trying to understand and figure out a way, if possible, to use what is already in place to run a couple 600w lights.
are you saying to shut off the 30amp breaker that the 250v outlet is connected to, and replace and install a 120v standard outlet?
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,145
or a 240v outlet?
i just don't know nearly enough to be adding a circuit, nor is that an option since i'm renting (if i owned i'd just hire an electrician of course, put the lights on a dedicated circuit)
 
Last edited: Apr 19, 2017
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,146
terrapin11 said:
or a 240v outlet?
i just don't know nearly enough to be adding a circuit, nor is that an option since i'm renting (if i owned i'd just hire an electrician of course, put the lights on a dedicated circuit)
Click to expand...


You're not adding a circuit you're only reconfiguring the plug so all it is is taking the cover off of that box and the plug out and install the correct plug for yourself
Or you could get the correct cord and plug it in and then connect to a timeclock a T103 Intermatic
but this does take some knowledge
not a lot but a little
and yes if you turn the breaker off that whole line is dead for you to work on
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,147
hiboy said:
You're not adding a circuit you're only reconfiguring the plug so all it is is taking the cover off of that box and the plug out and install the correct plug for yourself
Or you could get the correct cord and plug it in and then connect to a timeclock a T103 Intermatic
but this does take some knowledge
not a lot but a little
and yes if you turn the breaker off that whole line is dead for you to work on
Click to expand...
ok. so if i take out the 250v outlet, and replace that with a 120v outlet, connected to the same 30a breaker-that would be the easiest way to get my lights up and running?
i've never replaced an outlet before; the 250v has 4 wires attached in back, correct?
how does that translate to connecting those wires to a 120v?
or would it be more efficient to install a 240v outlet and get a heavy duty extension cord to run the ballasts from the 240v outlet?
(i'd have to purchase 240v power cords for the ballasts, i've been using the 120v power cords they came w/ in my previous grows).
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,148
alright, i am thinking swapping out the 4 prong 250v outlet for a 120v outlet is the way to go.
that should work fine, no?
so a 120v outlet on a 30amp circuit (dedicated dryer circuit...i live in the mountains, air drying is nice haha), will run the two 600w HPS lights and my 8,000btu a/c window unit.
hiboy what do you think? (besides me being a dumbass lol)
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,149
fuck, or can you not connect a 120v outlet to a 30amp circuit?
in that case, should i replace the 4 prong 250v w/ a 3 prong 240v?
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,150
terrapin11 said:
fuck, or can you not connect a 120v outlet to a 30amp circuit?
in that case, should i replace the 4 prong 250v w/ a 3 prong 240v?
Click to expand...
Your correct it's not safe to connect a 120 V outlet to a 30 amp breaker so you would have to change thevbreaker to a 20 amp breaker
that's very simple all you do is shut the main off and it's a screwdriver and you pull the breaker out
But I will advise it is electricity and I don't want anyone to do anything that's not within their skill
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,151
There are two hot wires one neutral and one ground
so you could actually get a double gang ring and install two outlets
one plug would be on each circuit and share the neutral and you would have two dedicated circuits there
one for your air conditioner and one for your lighting
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,152
hiboy said:
Your correct it's not safe to connect a 120 V outlet to a 30 amp breaker so you would have to change thevbreaker to a 20 amp breaker
that's very simple all you do is shut the main off and it's a screwdriver and you pull the breaker out
But I will advise it is electricity and I don't want anyone to do anything that's not within their skill
Click to expand...
so can i just put in a 3 prong 240v outlet?
i can't fuck w/ the breaker.
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,153
so, an outlet to fit this cord:

240v
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,154
terrapin11 said:
so can i just put in a 3 prong 240v outlet?
i can't fuck w/ the breaker.
Click to expand...
Yep
Should change breaker ( I have to say this or I will get ripped a new way one)
Will still work on a higher breaker
Hb
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,155
terrapin11 said:
so, an outlet to fit this cord:

240v
Click to expand...
that cord won't fit a 240v outlet
That cord looks like an extension for a light hood to ballast
Hb
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,156
hiboy said:
Yep
Should change breaker ( I have to say this or I will get ripped a new way one)
Will still work on a higher breaker
Hb
Click to expand...
how come i can't find a 3 prong 240v outlet on home depot's site, strange.

so here's a 240v power cord for a ballast:


that won't fit into the extension cord
link i posted?
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 19, 2017
#1,157
yeah, it's just not an ideal situation.
w/ my complete lack of knowledge and experience in terms of electrical, i am just going to let things be. better safe than sorry. like i said, i rent, so i am certainly not trying to fuck up someone's property and myself at the same time. lol.
i gotta get to a green state:)

thank you, HB, for your time and input.
greatly appreciated, sir.
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,158
terrapin11 said:
how come i can't find a 3 prong 240v outlet on home depot's site, strange.

so here's a 240v power cord for a ballast:


that won't fit into the extension cord
link i posted?
Click to expand...
Yes that is an extension cord for a 240 V outlet
I'll search for extension cord and a set up that would work for you but you have to have a little knowledge to build it
Hb
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,159
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 19, 2017
#1,160
 
Quote Reply
Page 58 of 71 · Replies 1,141–1,160 of 1,407
Prev
  • 1
  • …
  • 56
  • 57
  • 58
  • 59
  • 60
  • …
  • 71
Next
First Prev 58 of 71 Next Last

Thread info

Replies 1,406
Views 327,213
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • I’m Week 4 into Flowering
    • Latest: Gmix
    • 12 minutes ago
    General Indoor Growing
  • Some advice needed on outdoor growing...
    • Latest: BaldrickTX
    • 13 minutes ago
    General Outdoor Growing
  • how to Bubble washing and tips 2024
    • Latest: Leste
    • 16 minutes ago
    Concentrates & Processing
  • 2026 Outdoor Grows! let's see em!
    • Latest: GrowinShurts
    • 30 minutes ago
    General Outdoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Oldchucky
    • 41 minutes ago
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?