Just became aware of a problem that I experienced earlier in my grow that gave me a reset regarding our reliance on electricity and how to stay safe and maintain our grows.
So about a month from the end of my last grow I experienced a couple of unanticipated GFI trips, which at the time I assumed to be from some older timers (two years old). I reset the GFI circuit breaker several times over the course of a few days, then split up my lighting load between two available circuits. I bought two new timers and had no further problems. That is until I moved my clone tent and noticed the condition of the receptacle I’ve included a picture from.
I have test equipment (meggar, meg ohm meter) to determine the cause and found that the reason the GFI had tripped was the over current occurring because of an internal fault in the receptacle itself. No fault was found anywhere else.
This has caused me to add an important if overlooked step in our grows, checking equipment afterwards so we’re ready for the next season. It should include some visual inspection of all the extension cords and receptacles we’re plugging in all our equipment, as even that will uncover many problems and without the aid of more specialized elelctrical test equipment. It should also include as a minimum a test tripping of all GFI receptacles/and or circuit breakers we’re relying on. You can do that with an inexpensive circuit tester that has a GFI test button. Stay safe, test and examine your electrical cords and equipment at least once a year.
 

Attachments

  • unanticipated-and-unforeseen-electrical-problems.jpeg
    102.2 KB · Views: 145
  • unanticipated-and-unforeseen-electrical-problems-2.jpeg
    87.3 KB · Views: 144
  • unanticipated-and-unforeseen-electrical-problems-3.jpeg
    151.3 KB · Views: 153
Reactions: DemonTrich, kansabis, PharmHand and 3 others
Quote Reply

G gnome

Posts
20,448
Reactions
84,490
Joined
Feb 26, 2015
Points
638
Mar 25, 2018
#2
Dan789 said:
Just became aware of a problem that I experienced earlier in my grow that gave me a reset regarding our reliance on electricity and how to stay safe and maintain our grows.
So about a month from the end of my last grow I experienced a couple of unanticipated GFI trips, which at the time I assumed to be from some older timers (two years old). I reset the GFI circuit breaker several times over the course of a few days, then split up my lighting load between two available circuits. I bought two new timers and had no further problems. That is until I moved my clone tent and noticed the condition of the receptacle I’ve included a picture from.
I have test equipment (meggar, meg ohm meter) to determine the cause and found that the reason the GFI had tripped was the over current occurring because of an internal fault in the receptacle itself. No fault was found anywhere else.
This has caused me to add an important if overlooked step in our grows, checking equipment afterwards so we’re ready for the next season. It should include some visual inspection of all the extension cords and receptacles we’re plugging in all our equipment, as even that will uncover many problems and without the aid of more specialized elelctrical test equipment. It should also include as a minimum a test tripping of all GFI receptacles/and or circuit breakers we’re relying on. You can do that with an inexpensive circuit tester that has a GFI test button. Stay safe, test and examine your electrical cords and equipment at least once a year.
Click to expand...
Well, if ur gfi is repeatedly trippin ya dont wanna jjst keep resetting it. Looks like u were pullin too much juice from that 1 receptacle.
That outlet is only rated for 15A
 
Reactions: DemonTrich, Freshone and MirrorZen
Quote Reply

sixstring

Posts
7,079
Reactions
29,605
Joined
Jul 26, 2011
Points
313
Mar 25, 2018
#3
Wow this should never happen on a gfi protected line,is the GFI on this circuit 20amp and the actual circuit is 15amp? Not impressed with the condition of that wire either,the corrosion could have caused the initial problem.if a GFI or breaker trips once,no biggie,probably over loaded the line or had power co issues.if it trips a second time you have serious issues
 
Last edited: Apr 4, 2018
Reactions: dirkdaddy, DemonTrich, kansabis and 3 others
Quote Reply

MirrorZen

Posts
1,362
Reactions
3,491
Joined
Sep 13, 2016
Points
263
Mar 25, 2018
#4
Need a to watch thy amperage, and never exceed 75% of an outlets rating. Just stating the elephant.

Edit: but yes, safety first.
 
Reactions: DemonTrich and Freshone
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Mar 25, 2018
#5
The receptacle was internally shorted, it only had one 40 watt or less oscillating fan on it. If it had been overloaded where the c/b didn’t trip the silver screw would have been heated and discolored also. The wirenut with the melted portion on it was on the ground wire.
Regarding a tripping c/b no matter what type, IE regular or GFI jots do occur (just one of those things), by the time I had reset it for the third time, the shorting had melted enough inside the recept to clear and allow the breaker to reset. The caveat is, these were heavy duty, not the $.59 cent variety and about eight years old. The second compounding was that I had hidden this receptacle behind a tent, which preventing me from noticing that there was a problem. (Think about all the receptacles that you haven’t looked at in a few months/years?).

Big PS, I’m an retired Electrical contractor with many years experience, so this wasn’t some work done by someone who wasn’t qualified nor in a hurry to get it done, if a situation like this could happen to me, it can/will happen to anyone when you least expect it.
 
Reactions: DemonTrich, kansabis, sixstring and 4 others
Quote Reply

Freshone

Posts
1,620
Reactions
6,140
Joined
Jul 6, 2016
Points
263
Mar 26, 2018
#6
Ive seen similar before in homes,Were the side screws used for wiring or was the lazy way taken and the push in for the wires used?Ive see them come loose and arc many time when the push in were used and thats not under heavy load either.
 
Reactions: sixstring, Homesteader and G gnome
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Mar 26, 2018
#7
Here’s a little follow up, these two pics are, left side newly purchased Leviton receptacle, right side is also Leviton purchased a few years back, which was the same variety that faulted. Notice the new one has much more space between where the conductors terminate (yes under screws) and the frame which is tied to the grounding path.
Those back stab style receptacles mentioned, are what’s used most often in most new home, older home construction, and i certainly agree they shouldn’t be used at all.
 

Attachments

  • 487AC5DC-40F1-4461-B639-B5D28CA62DB8.jpeg
    96.2 KB · Views: 114
  • 0222EDD7-3F4F-4988-A179-90327FE8C3F9.jpeg
    94.4 KB · Views: 121
Reactions: kansabis, sixstring and madgrower
Quote Reply

madgrower

Posts
472
Reactions
727
Joined
Dec 21, 2017
Points
93
Mar 26, 2018
#8
Dan789 said:
Here’s a little follow up, these two pics are, left side newly purchased Leviton receptacle, right side is also Leviton purchased a few years back, which was the same variety that faulted. Notice the new one has much more space between where the conductors terminate (yes under screws) and the frame which is tied to the grounding path.
Those back stab style receptacles mentioned, are what’s used most often in most new home, older home construction, and i certainly agree they shouldn’t be used at all.
Click to expand...
Very useful information .most people don't even think about what's unseen
 
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Mar 26, 2018
#9
Yes, all the shit unseen inside the walls @madgrower. I’m beginning to rethink replacing the GFI c/bs I have in my grow area with arc-fault/GFI circuit breakers. They would have tripped and not been able to be reset until the problem was remedied. They would also detect nails or screw penetrations (hot to neutral faults) of the non metallic sheathed cable (romex) that’s commonly used inside the walls of our homes. Those style problems if that occurs can burn & heat up inside the wall until the house burns down without tripping a regular or GFI breaker/receptacle.
 
Reactions: Freshone, kansabis, sixstring and 1 other person
Quote Reply

madgrower

Posts
472
Reactions
727
Joined
Dec 21, 2017
Points
93
Mar 26, 2018
#10
Dan789 said:
Yes, all the shit unseen inside the walls @madgrower. I’m beginning to rethink replacing the GFI c/bs I have in my grow area with arc-fault/GFI circuit breakers. They would have tripped and not been able to be reset until the problem was remedied. They would also detect nails or screw penetrations (hot to neutral faults) of the non metallic sheathed cable (romex) that’s commonly used inside the walls of our homes. Those style problems if that occurs can burn & heat up inside the wall until the house burns down without tripping a regular or GFI breaker/receptacle.
Click to expand...
That's what I did .I couldn't dasy chain them because they must have detected a fault so they are all on separate breakers now
 
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Mar 26, 2018
#11
If that occurs in the future on other circuits, you can break the circuit in half and see if it resets (to help locate the fault), a fault can also come from something that’s plugged in. Ultimately your individual arc fault GFI c/b’s gives the best protection, and is easiest to troubleshoot.
Ideal makes a circuit analyzer that can also help determine other problems, but it’s a couple hundred bucks and hard to justify for the few times it would be necessary. I’ve got a whole bag full of meters and such legacy’d from when I was working and now for JIC.
 
Reactions: sixstring and madgrower
Quote Reply

madgrower

Posts
472
Reactions
727
Joined
Dec 21, 2017
Points
93
Mar 26, 2018
#12
Best thing that I did Imo is that I got a 240 volt timer with a 30 amp breaker and have 4 lights hooked to that there's a 110 plug hooked to it too for fans
 
Quote Reply
Page 1 of 1 · Replies 1–12 of 12
1

Thread info

Replies 11
Views 1,307
Started Mar 25, 2018
Latest post Mar 26, 2018
Starter Dan789
Forum Basic Growing Information

Latest posts

  • D
    2026 Outdoor Grows! let's see em!
    • Latest: danmac69
    • 12 minutes ago
    General Outdoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Oldchucky
    • 28 minutes ago
    General Outdoor Growing
  • The Nepali Highland Growers thread.
    • Latest: grayoldnproud
    • 35 minutes ago
    Grow Diaries
  • H
    Rainbow Kush - first time auto grow
    • Latest: HIWATT
    • 44 minutes ago
    Grow Diaries
  • Storing seeds for long term
    • Latest: Strainshow2.0
    • 49 minutes ago
    Advanced Techniques & Problems
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Basic Growing Information
  • Unanticipated And Unforeseen Electrical Problems
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?