4
Joined
Aug 19, 2014
Points
3
Aug 20, 2014
#21
midwestdensies said:
Ever consider gavita 750s and turn up to 830w? Probably similar spread on. 4x4 trays. Then saving watts and helping efficiency.
Note in the room were running 9 600w gavitas. So 5400 watts but some t5s in mom area. Were sealed too 2 car garage space essentially. We also Have seperate panel for ac. Dehueys use a lot of space up and all. Can peep my thread for some rundown. Mwd new room new year
Click to expand...
I have thrown the idea around but I think for now Ari cooled cool tubes is the route I will go "Bongo" mentioned that at full tilt summer I should be only pushing 120 amps give or take few amps. Is that realistic I am working on adding up all the equipment in amps right now.
 
Quote Reply

Dunge

Posts
2,233
Reactions
3,710
Joined
Aug 8, 2010
Points
263
Aug 20, 2014
#22
Custom X said:
Well currently it has 200 amp 3 phase and a 100 amp single and a 125 single we were considering upgrading the 125 single to 200 amp. Right now he wants an equipment schedule to see if the 200 amp panel is going to be sufficient.
Click to expand...
This is a real question, so sorry if it sounds a bit torllish but, why would a single phase panel be connected to three phase source?
Seems to me that a three phase panel can do it all, and single phase panels would only make balancing the load more complicated.
What am I missing here?
Is balancing not as important as I think?
 
Reactions: bongobongo
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 20, 2014
#23
well this a bit new to me but the warehouse is located on a nursery the warehouse has 125 amp single phase and the nursery use 100 amp single and three phase 200 amp
 
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 20, 2014
#24
all right guys this is the equipment schedule for voltage and amperage. Is this a realistic value??



  1. Equipment Voltage Amperage


  2. (20) Wall mounted 16 in Oscillating fans 3 speed 120 V .71/.54/.48
  1. (4) 8 in Booster fans 120V .5

  2. (4) 12 in Booster Fans 120V 1.5

  3. (2) 12 in Inline fans 120V 3.2

  4. (4) 10in inline fans 120V 2.07

  5. (3) 8 in inline fans 120V 1.72

  6. (2) 6 in inline 120V 0.97

  7. (2) co2 regulator 120V 1.0

  8. (2) Saturn five environmental controllers 120V 15.0

  9. (2) 12000,BTU mini split AC units 110-120V 9.5

  10. (2) ½ hp inline water pumps 110V 2.5

  11. (2) Dehumidifiers 115V 4.8

  12. (17) 1,000 W Lights 240V 4.6

  13. (4) 2x4 T5 4 bulb lights 120V 1.98

  14. (1)Fluorescent Shop Light 120V 1.0

  15. MLC 16DX lighting controller Hooked up with an 80 Amp line


added up I have 194.76 amps
 
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 20, 2014
#25
Dunge said:
This is a real question, so sorry if it sounds a bit torllish but, why would a single phase panel be connected to three phase source?
Seems to me that a three phase panel can do it all, and single phase panels would only make balancing the load more complicated.
What am I missing here?
Is balancing not as important as I think?
Click to expand...
I think is because three phase is only needed for large equipment its over kill for most things.
 
Quote Reply

purpleberry

Posts
633
Reactions
233
Joined
Mar 11, 2009
Points
43
Aug 20, 2014
#26
bongobongo said:
Ehhh, I disagree. I'd rather have them on a closed loop and need a smaller ac. That's just me though. Too much humidity. And on top of that he's using co2. You can push these
Plants to insanity g/watt with a cooled hoods and sealed rooms with co2
Click to expand...
What does humidity and co2 have to do with anything? It actually lowers the humidity with bare bulbs, and of course the room would be sealed with co2 and bare bulbs. And I hit 1g watt plus running bare bulb.
Look at how many inline fans and how many amps they take up, move those amps to ac. I believe the reason people increase yield with gavitas is partially due to the fact they ditch air cooled hoods. Ive taken a room and put in a bigger ac, ditched the glass and seen yields go up. I never hit 1g watt before I did that.
 
Reactions: nicolajanjak and Custom X
Quote Reply

bongobongo

Supporter
Posts
729
Reactions
1,185
Joined
Apr 15, 2011
Points
143
Aug 20, 2014
#27
You only need two 12" Inlines to cool 16k. Your going overboard using more. I'd rather keep my bulbs air cooled on a closed loop to keep my heat out of the room and run my AC unit less to save power. It's give or take, but in this situation I would use a closed loop on hoods. You could just as easily run them open and use 24k split. I guess I'm so familiar with the running of ducting and cutting holes it isn't that big of deal... Two lines of hoods and ducting, 2 12s exiting the building.
 
Reactions: Custom X
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 27, 2014
#28
Hey Guys sorry its been a bit but we are going to ditch the fans it looks like and throw 48,000 BTU in one room with 12/ 1000 lights utilizing hoods and a bare bulb. After much research and nit picking I decided this will be the most cost effective and easy way to hande our cooling needs. And with two 24,000 mini split units we should be good. It will be a sealed room for the most part however we will be utilizing an exhaust fan in the case of any heating emergency. Which will be regulated with a thrmostat. as well as an intake. Any oppinions on if we will need more AC to cool 12,000 kw ? If we utilize an intake and exhausr in the event of high peaks on our lights.


So 48,000 BTU of AC, two Ten inch intak and outake fans, 1 10" Phresh intake hepa filter, 2 50 pint a day Dehumidfiers, 8 Wall mounted 16" fans, 4 burner co2 regulator, 12,000 watts for lighting, and fuly irrigated garden. Any oppininons on amp draw??

Or any oppinions at all would be much appreciated.

Thanks Guys,

Custom
 
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 27, 2014
#29
Any ideas on good Bare bulb hoods??
 
Reactions: Growproper
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 27, 2014
#30
As well as AC model selection or brand?
 
Quote Reply

Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Aug 27, 2014
#31
I would do a 5 ton york split unit for 12k barebulb, I use adjust a wings.

If buying new go with the double ended tech stuff, I'm switching over to it, it rocks.
 
Reactions: masshole61
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Aug 27, 2014
#32
Billyboat said:
I would do a 5 ton york split unit for 12k barebulb, I use adjust a wings.

If buying new go with the double ended tech stuff, I'm switching over to it, it rocks.
Click to expand...

Right on so you are talkking Gavita or Double ended fixtures. With the better spectrum.
 
Reactions: midwestdensies
Quote Reply

Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Aug 27, 2014
#33
Gavita is doubled ended, well except for their one 600w bulb.
 
Quote Reply
M

MarcoTC

Posts
16
Reactions
4
Joined
Aug 18, 2014
Points
3
Sep 4, 2014
#34
Maybe helpful..... as for AC's, I'm currently looking into these for myself:
These go for $2100 with air handler included.

They also have a 13 Seer version:
Cheaper ($1800) because they don't come with a TXV.

I'm wondering about the DE bulbs though. I love them but don't they run hotter? Normally, I calculate 5000BTU per 1000 Watts but I'm not sure if that's the same for DE's.
 
Quote Reply

Custom X

Posts
17
Reactions
4
Joined
Aug 19, 2014
Points
3
Sep 5, 2014
#35
Hey guys sorry its been awhile a bit of an update. We are going to go Bare Bulb and only one room for now. We are trying to determine if we should go with a upgraded 200 amp service to 400 amp service. or if we should just have a new meter put in with new 200 or 400 amp service. As far as upgrade goes a devoted 4oo amp service may be the best way to go just trying to work out the cost has anyone had to upgrade service before. Perhaps give me an idea of what i am in for, or if I should just look for another building if it is not feasable.
 
Reactions: Burned Haze
Quote Reply

QLTYlab

Posts
199
Reactions
414
Joined
May 1, 2014
Points
63
Sep 19, 2014
#36
if you are even considering the extra amp capacity, do it. your options will be much more open as you progress and learn the space better. also seems like something you would not want to do once up and running.
 
Reactions: Burned Haze
Quote Reply
Page 2 of 2 · Replies 21–36 of 36
Prev
  • 1
  • 2
First Prev 2 of 2

Thread info

Replies 35
Views 5,327
Started Aug 19, 2014
Latest post Sep 19, 2014
Starter Custom X
Forum Growroom Design & Setup

Latest posts

  • Outdoor Gardeners / Growers. Let's Talk-Show Gardens-Soil-Methods-Pests-Critters-Gardening Kind Of Stuff!
    • Latest: grayoldnproud
    • 29 minutes ago
    Other Pics
  • 40 days into cure , no change in smell or flavor
    • Latest: Hotblondz13
    • 49 minutes ago
    Cannabis Infirmary
  • B
    New grower need advice on my plant
    • Latest: Brian804
    • 59 minutes ago
    Basic Growing Information
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: grayoldnproud
    • Today at 5:19 PM
    General Outdoor Growing
  • I
    Mars Hydro API reverse engineered
    • Latest: Inzemix
    • Today at 5:18 PM
    Growroom Design & Setup
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • 16,000 W Dream Room
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?