Ok electrical question. So I ran a 10/2 from a 30 amp 240 v pushmatic breaker, the 10/2 goes to a 30 amp GE water heater timer and from the timer I want to wire two Nema 6-20 receptacles. Here is the problem they dont make a small sized Nema 6-30 receptacle the highest is the 20 amp ones. I am running 4 600w lights off of it pulling 11 amps. My question, is it fine to run the two Nema 6-20 receptacles on the 30 amp circuit or should I chalk it up and downsize the pushmatic breaker to 20amp 2 pole? See i wanted to keep the 30amp breaker in so I can upgrade in the future with more lights. I see all other lighting controllers doing the same running lower rated receptacles on higher amp breakers such as C.A.P MLC4.