fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Apr 1, 2014
#521
Damn dude where the hell have you been?lol.
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 2, 2014
#522
fishwhistle said:
Damn dude where the hell have you been?lol.
Click to expand...
No shit huh...almost 2 years..
Twins changed my life no doubt. .... life changing events. Trying to get back in the old mind set .
I'm glad the threads still up. Amazed to see some of the ol school names.
Rockin a super strain Larry right now!!
 
Reactions: OGONLY, cheech, fishwhistle and 1 other person
Quote Reply
Z

ZombieSlave

Posts
157
Reactions
42
Joined
Jan 8, 2012
Points
28
Apr 2, 2014
#523
Hello and thanks for the great thread,

Quick question: I am running 10-4 from my main to my sub, the breaker I should be using is 30 amp or 40amp?

I just want to make sure it trips in case I go over board.

Thanks again
 
Quote Reply

HookedonPonics

Posts
543
Reactions
840
Joined
Nov 3, 2010
Points
93
Apr 2, 2014
#524
Hey guys I have a large custom lighting controller running two rooms my question is, one of my rooms is 50' from where the controller is. I really didnt want to buy a new controller and wire a new plug, etc. Can I make 50' runs out of 12 gauge romex from the lighting controller to the ballasts and it still be safe and work correctly? Does anyone make ballast power cords that long out the box?
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 2, 2014
#525
hiboy said:
That looks like a fpe panel.no quads available for it. U should be able to raise that right side up for a 240v breaker. Have an electrician look at it. U dont want to screw up ur phasing.
hb
Click to expand...
The picture is rotated 90 degrees to the left, so just to be sure, you mean slide the bottom over in order to have two adjacent spots open, yes? Presumably at least one of the breakers isn't even used given the splice, and I believe the center two on the right/bottom are connected, though I don't recall what goes to what. :/ *fail*

EDIT: *fail* The two connected breakers almost certainly go to the through wall AC which has it's own circuit and a... not normal plug, I'm unsure of the specific name at the moment. :/
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Apr 2, 2014
#526
hiboy said:
No shit huh...almost 2 years..
Twins changed my life no doubt. .... life changing events. Trying to get back in the old mind set .
I'm glad the threads still up. Amazed to see some of the ol school names.
Rockin a super strain Larry right now!!
Click to expand...
Congrats bro and glad all is well.
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 2, 2014
#527
yes you want two spaces opened by each other
bibbles said:
The picture is rotated 90 degrees to the left, so just to be sure, you mean slide the bottom over in order to have two adjacent spots open, yes? Presumably at least one of the breakers isn't even used given the splice, and I believe the center two on the right/bottom are connected, though I don't recall what goes to what. :/ *fail*

EDIT: *fail* The two connected breakers almost certainly go to the through wall AC which has it's own circuit and a... not normal plug, I'm unsure of the specific name at the moment. :/
Click to expand...
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 3, 2014
#528
[quits te="ZombieSlave, post: 1229547, member: 35639"]Hello and thanks for the great thread,

Quick question: I am running 10-4 from my main to my sub, the breaker I should be using is 30 amp or 40amp?

I just want to make sure it trips in case I go over board.

Thanks again[/quote]
If Its a black red white copper with a orange sheathe its 10/3 romex and should be on a 30 amp 2 pole breaker.
hb
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 6, 2014
#529
So, how can I figure out the available amperage to my box? It's an apartment, the lines seem to run to the meters and then some locked down "high voltage" boxes. Other than basing it on the size of the lines running into my box, I'm not really sure?
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 6, 2014
#530
The guage looks like 1 or 0, assuming "conductor diameter" includes the insulation.
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 7, 2014
#531
bibbles said:
The guage looks like 1 or 0, assuming "conductor diameter" includes the insulation.
Click to expand...
Where the meter is located u should see a main double breaker with ur unit # on it (hopefully) and that is what is feeding ur sub panel in ur apartment. Max I would think is 100 amps if ur lucky
Hb
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 7, 2014
#532
hiboy said:
Where the meter is located u should see a main double breaker with ur unit # on it (hopefully) and that is what is feeding ur sub panel in ur apartment. Max I would think is 100 amps if ur lucky
Hb
Click to expand...
Hah, I looked earlier but didn't see the numbers - 100 amps 120-240 V.A.C.; 50 amps maximum - I assume this means 100 total, 50 max per breaker, yes?
 
Quote Reply

Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Apr 7, 2014
#533
I have a 3 phase 208v question for ya. This is based off 100 amp 3 phase subpanel just running lights.

I currently am running 2 powerboxs at 35 amps each on "legs" AB and CA and would like to add another powerbox to "legs" BC, that would also draw 35 amps.

On paper that gives me a balanced load of 70 amps on "legs" A,B,C.

Am I correct, @hiboy
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 10, 2014
#534
bibbles said:
Hah, I looked earlier but didn't see the numbers - 100 amps 120-240 V.A.C.; 50 amps maximum - I assume this means 100 total, 50 max per breaker, yes?
Click to expand...
U can put 100 amps each phase. Of course u should follow the 80% rule.
Hb
 
Reactions: bibbles
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 10, 2014
#535
Billyboat said:
I have a 3 phase 208v question for ya. This is based off 100 amp 3 phase subpanel just running lights.

I currently am running 2 powerboxs at 35 amps each on "legs" AB and CA and would like to add another powerbox to "legs" BC, that would also draw 35 amps.

On paper that gives me a balanced load of 70 amps on "legs" A,B,C.

Am I correct, @hiboy
Click to expand...
Yes u are correct!
U will be balanced nicely
Hb
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 10, 2014
#536
hiboy said:
U can put 100 amps each phase. Of course u should follow the 80% rule.
Hb
Click to expand...
I don't think that'll be an issue, but I'm gonna be checking things outside of the room today, and shuffling breakers around as needed. One more question: It looks like I'm gonna be using two 120v ACs (12amps/ea), rather than a single 240v unit (12amps), and I've been waffling between a single 50amp 240v circuit for everything, and two 30amp circuits, a 120v for the two ACs, and a 240v for my (4) lights and fans. I figure that if each AC is on a different phase, the load will effectively be the same as a single 240v unit, yeah? What would you suggest?
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
Apr 10, 2014
#537
Er, two ACs on opposite phases of the 50amp 240v circuit at 12amps each, rather than a single 240v unit pulling 12amps on both phases, versus giving them their own 30amp 120v circuit. If the former will work as I imagine, it'll save the time and money of running an additional circuit, as well as more evenly distribute the load, yes? I'd be pulling about 32amps on each phase with my lights and ACs, rather than 20 on each for the lights, plus 24 on one via the extra circuit.

EDIT: Hm, I need to check the amperage of the stuff outside of the room, if I can put the fridge, et al, on one phase, then the ACs on the other phase, it may actually work out better than splitting them between two phases... it would still be good to know if that'll work though! :D

Thanks again!
 
Last edited: Apr 10, 2014
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Apr 11, 2014
#538
hiboy gave me permission to help you guys if he was busy. Sounds like you're gaining ground on figuring this out. Just a couple of thoughts..
After you get the 50 amp installed in your panel and run that to a new subpanel..you'll use a 30 amp double pole for your lights. That leaves room for either one 20amp double pole or 2 15amp 120v breakers. That will be up to your needs per appliance. There is no code for 30 amp 120v in a residential dwelling...it's either a 15 or 20 amp. I think the 20 amp double pole..being the better choice. Just make sure to be under your 80% usage rule..and if you use the 2 120volt breakers that they are in fact on different phases (i.e. stacked together...as it may be).
When I move old wiring around..especially in a panel, I try to disturb as little as possible, as old wiring has more risk of the sheath splitting or cracking. Best to not "jumble" around too much in there. Your panel should be balanced as is...Hiboy just wants to be sure that by moving everything up on the one side doesn't put it out of balance...as you know every other breaker on each side of your panel is at different phases...connected to different buses.
Hopefully the big guy will pop in to help confirm.
 
Quote Reply

Frostynugman

Posts
1,192
Reactions
2,748
Joined
Dec 13, 2013
Points
263
Apr 11, 2014
#539
Does anybody know of any savy electricians in Colorado that would install a sub panel. If someone could PM me asap that would be nice nothing major maybe like a 15 amp or 30 amp sub panel? Thanks all really need the help
 
Quote Reply

Frostynugman

Posts
1,192
Reactions
2,748
Joined
Dec 13, 2013
Points
263
Apr 11, 2014
#540
Found the electrician. thanks!
 
Quote Reply
Page 27 of 71 · Replies 521–540 of 1,407
Prev
  • 1
  • …
  • 25
  • 26
  • 27
  • 28
  • 29
  • …
  • 71
Next
First Prev 27 of 71 Next Last

Thread info

Replies 1,406
Views 327,221
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • I’m Week 4 into Flowering
    • Latest: Gmix
    • 1 minute ago
    General Indoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Oldchucky
    • 1 minute ago
    General Outdoor Growing
  • how to Bubble washing and tips 2024
    • Latest: Oldchucky
    • 7 minutes ago
    Concentrates & Processing
  • 2026 Outdoor Grows! let's see em!
    • Latest: Tahoekushcat
    • 14 minutes ago
    General Outdoor Growing
  • Some advice needed on outdoor growing...
    • Latest: BaldrickTX
    • 23 minutes ago
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?