Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Jul 1, 2015
#681
I also ran 1/0 for a 300 foot run 4 wire and it was more then enough for the 150 amps I needed from it.
fishwhistle said:
1/0 is plenty,i ran it 225' for 125 amps so 160 is cake,I used to have 2 4k rooms flipping back and forth and a veg room all with minis with no issues,now i only run one flower and veg.I did not run a neutral but instead i established a new ground near the sub panel by driving a new 10' ground rod.I know power companies use aluminum but id stick to copper,get ready for a shock when you buy it.
I just pulled my receipt $1590.25 for 2 240' cuts of 1/0,Also get it a little longer than you think you need too,Its a bitch pulling that stuff and you lose a little in the twists and turns of the conduit.
PM me if you have questions or i can help.
Click to expand...

Agreed!

I ran 1/0 300' 4 wire, for a 125 amp sub panel and it worked great. I ran the same size for both legs, neutral, and ground, I figured it was the safest bet since it was such a long run.
 
Reactions: CelticEBE and fishwhistle
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Jul 1, 2015
#682
I mis-spoke above i did run 3-1/0 wires,2 hots and a neutral but no ground,established a new one at the sub.
 
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Jul 18, 2015
#683
Hey guys. Wanted to get some of your opinions on how to do things the safest way possible and also wanted to make sure the way my electrician wired up my room years ago was the safest/most efficient way possible. Because as of lately I have been floating around this particular thread and some things have caught my eye. I have been considering boosting my flower room from 6.6k to 8k and I want to make sure I have enough juice to do so safely as I have a 200 amp maim breaker. When he originally wired up my room I told him I was most likely going to run 7 1ks. He wired me up 4 20 amp breakers each with two 110 outlets and A 30 amp breaker with 3 220 outlets with 12-3 wiring. This is what I'm confused about and here are my questions.

1. I'm sure he didn't know about the Titan controllers but couldn't he have just ran a thicker gauge wire on my 220 line so I could handle more lights on my 220 line? If my math is correct, a 220 ballast draws 4.5 amps approx. so three 1ks drawing 4.5 amps each would only put me at 13.5 amps out of 30?

2. This is kind of a dumb question but say u have 20 lights and your maxed out on power cause your running them at 110 drawing 9 amps ea. if u switched them all to 220 could u now run 40 lights?

Currently I have my 3 1 ks plugged into my 220 line and 5 other 1ks plugged throughout multiple 110 outlets. I had a dryer 30 amp that I wasn't using so recently I wired in a couple 220 outlets to that just so I could get some of my 1ks off 110. ( I haven't got to plug more than one 1k into the new 220 line yet cause I'm waiting to harvest as I don't wanna work above the plants ATM.)

This gets me to my main question. Should I just run two 30 amp breakers with how many 1k lights on each line? Or should I just say fuck that and rip out both 30 amp breakers and put in a 50 amp with a Titan Helios?

Also my electrician told me that the 220 line he installed was good for 3600 watts. Does this seem right? Remember it only has 12 3 wiring
 

Attachments

  • image.jpg
    93.1 KB · Views: 217
Last edited: Jul 18, 2015
Quote Reply

Olyver

Posts
343
Reactions
237
Joined
Apr 19, 2009
Points
43
Jul 18, 2015
#684
CelticEBE said:
OK, got a couple of questions for you experienced sparky types.

I'm about to trench some power to my workshop. 125 amps on a 160' run.

According to this page. I need 1/0 copper, or 2/0 aluminum.
http://www.paigewire.com/pumpWireCalc.aspx

My question is this. I will be running a FLIP, so there will be a constant draw on the line. Should I go one size above what is recommended?

Also, can I get away with a smaller neutral?

Thanks in advance for any input.
Click to expand...

If you're running a flip you need to power off/on the ballast for each 12 hour flip cycle, instead of leaving the ballasts on a flipping hot.
 
Reactions: CelticEBE
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jul 18, 2015
#685
Olyver said:
If you're running a flip you need to power off/on the ballast for each 12 hour flip cycle, instead of leaving the ballasts on a flipping hot.
Click to expand...
I realize that. I have run flips before. What I meant by the constant draw, was that it won't be like a traditional set up where the draw is minimal during lights out.
 
Quote Reply
B

Burned Haze

Guest
Jul 20, 2015
#686
Howdy, I just upgraded my grow to a 320amp unlimited tap rule and added a 200 amp service for the lab area ! just stuck on this last question before I add my controller .

* Purchased ( 2) Helios 7 , one for each side of room so lights wire can reach the controller easier & be outside the room and safe!( bigger titan controllers were ripe offs anyways )

* (10 De's total, 5 De's per controller) 1000w nanolux de setup. Going to divide them by 2 but that does not mean anything, Might upgrade to 12 lights someday but probably not.

The ? : What Size Wire should I use from the controller to the 200 amp panel (25-35 ft ,depending on which one ) . It's sad Titan did not state the obvious shit on the back of their manual cause they are not hiding nor helping anyone but stalling the project cause this is my 3th controller from them ( none damaged & non bitchin lol)

room specs : 20.5 wide x 35 long x 12 tall
 
Quote Reply

shemshemet

Posts
623
Reactions
1,404
Joined
Feb 17, 2015
Points
143
Aug 8, 2015
#687
If one were to have a stand alone garage with no electric to it, say about 50 from a house, would it be difficult to get it some power?

Also, what would it take if it were feasible?

Got a few more follow up questions as well.

Edit: By power I mean I want to run up to (2 ea) 1000 watt lights, and a veg area to match (~600 watt lights). This is a soil grow, so really only need fans and misc equip
 
Quote Reply

Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Aug 8, 2015
#688
shemshemet said:
If one were to have a stand alone garage with no electric to it, say about 50 from a house, would it be difficult to get it some power?

Also, what would it take if it were feasible?

Got a few more follow up questions as well.

Edit: By power I mean I want to run up to (2 ea) 1000 watt lights, and a veg area to match (~600 watt lights). This is a soil grow, so really only need fans and misc equip
Click to expand...

Depends on your definition of difficult. Dig a trench, and run the wires...
 
Reactions: fishwhistle, sixstring and shemshemet
Quote Reply

shemshemet

Posts
623
Reactions
1,404
Joined
Feb 17, 2015
Points
143
Aug 8, 2015
#689
What would I connect the wires to at the house and at the garage?

Would I need to modify whats happening at the source?
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Aug 8, 2015
#690
shemshemet said:
What would I connect the wires to at the house and at the garage?

Would I need to modify whats happening at the source?
Click to expand...
The wires would connect to a new breaker in the main panel and a new subpanel in the shop.
You need to make sure you have the available power at your main panel before doing anything.You also need to have room in the main panel to add a new breaker.If thats good then you would need to trench and bury the wire in conduit.You would need the proper size wire for the amount of amps you want to use in the shop PLUS take into account the distance of the run for voltage drop and a subpanel in the garage.If you do all that you could probably just hire an electrician to do the final hookup at the panels,good luck!
 
Quote Reply

Michal

Posts
31
Reactions
35
Joined
May 28, 2013
Points
18
Aug 8, 2015
#691
Hire a sparky either way (you don't sound very confident or experienced), they're an invaluable resource. Many do small jobs for beer if they can explain the labour (digging, wire pulling, etc).
 
Reactions: sixstring
Quote Reply
H

hightide99

Posts
9
Joined
Aug 9, 2015
Points
1
Aug 9, 2015
#692
Hey guys I would really appreciate your input THC FARMER here goes...

I have a 30 x 70 garage converted into living room fully insulated etc. It has central air from the Home A/C unit. The converted garage room has its own Electrical Circuit Box ,separate from the main house box, with (1) 30 am breaker and (2) 20 amp breakers. The circuit box says 100 AMP MAX. By the box I also have a 240 connection not being used. The room is no longer in use so I have a tent with (1) 400 watt MH and (1) 600 watt HPS inside a 8 X 8 tent. I also have four inline 6" fans, 4-5 oscillating fans various sizes, along with a 14,000 BTU Portable A/C. I also have a TV, and CPU in the room aswell. I have not had any issues with this set up as far as blowing breakers goes. My question is if I plan on adding 1-2 more 600 watt HPS ballasts will I run into any problems with the breaker box popping the breakers? Also will I need to get a light controller like the
Helios 1 - 120 Volt 4 Light Timer? The room is not in use during summer hours , so mostly from Oct-March
any advice would be awesome.
I am just not sure IF i will run into any issues if I add 1 or 2 more 600 watt hps lights to my setup. THANKS ALL INFO WELCOMED THANKS

PS The rooms wiring is fairly new and up to date THANKS
 
Quote Reply

BluBryChez

Posts
7
Reactions
2
Joined
Oct 16, 2013
Points
3
Sep 7, 2015
#693
Here is my new project. I'll start a log and keep you guys posted on everything. Roughly 4000 sqr. Feet. Existing 10 ton ac unit. 4-13x14 office rooms w/ 12 foot ceilings. EAch room has an AC drop and intake. I'll take more pics today when I crack open that big service panel
 
Quote Reply

BluBryChez

Posts
7
Reactions
2
Joined
Oct 16, 2013
Points
3
Sep 8, 2015
#694
StickiestAbyss said:
10-1000watt magnetic ballast all on 240 volts, 2-460 cfm duct fans 110v, 3 oscillating wall mount fans 110v. (a/c is on separate sub panel so its out of the equation) what awg wire do i need to use for this sub panel?
Click to expand...
^^^this was me in 2012.. Don't know what happen to this account. Lost my e-mail account for this screen name or something.. Anyways. This is me now! Lol. Been an interesting 3 years I gotta say.. Been killing it. And had some major mistakes. Defiantly a learning curve. Upgraded to a new location with a new set of issues. Mostly electrical. I'll be posting under my new identity. Stay tuned for cool pics!
 
Quote Reply

BluBryChez

Posts
7
Reactions
2
Joined
Oct 16, 2013
Points
3
Sep 8, 2015
#695
BluBryChez said:
Here is my new project. I'll start a log and keep you guys posted on everything. Roughly 4000 sqr. Feet. Existing 10 ton ac unit. 4-13x14 office rooms w/ 12 foot ceilings. EAch room has an AC drop and intake. I'll take more pics today when I crack open that big service panel View attachment 534482 View attachment 534483
Click to expand...
 

Attachments

  • image.jpg
    109.3 KB · Views: 184
  • image.jpg
    128.1 KB · Views: 185
  • image.jpg
    146.7 KB · Views: 191
  • image.jpg
    101.9 KB · Views: 193
  • image.jpg
    140 KB · Views: 204
  • image.jpg
    148.9 KB · Views: 184
Quote Reply

BluBryChez

Posts
7
Reactions
2
Joined
Oct 16, 2013
Points
3
Sep 8, 2015
#696
hightide99 said:
Hey guys I would really appreciate your input THC FARMER here goes...

I have a 30 x 70 garage converted into living room fully insulated etc. It has central air from the Home A/C unit. The converted garage room has its own Electrical Circuit Box ,separate from the main house box, with (1) 30 am breaker and (2) 20 amp breakers. The circuit box says 100 AMP MAX. By the box I also have a 240 connection not being used. The room is no longer in use so I have a tent with (1) 400 watt MH and (1) 600 watt HPS inside a 8 X 8 tent. I also have four inline 6" fans, 4-5 oscillating fans various sizes, along with a 14,000 BTU Portable A/C. I also have a TV, and CPU in the room aswell. I have not had any issues with this set up as far as blowing breakers goes. My question is if I plan on adding 1-2 more 600 watt HPS ballasts will I run into any problems with the breaker box popping the breakers? Also will I need to get a light controller like the
Helios 1 - 120 Volt 4 Light Timer? The room is not in use during summer hours , so mostly from Oct-March
any advice would be awesome.
I am just not sure IF i will run into any issues if I add 1 or 2 more 600 watt hps lights to my setup. THANKS ALL INFO WELCOMED THANKS

PS The rooms wiring is fairly new and up to date THANKS
Click to expand...

Got any room in that sub panel for more breakers? It is a sub and not a servic? Does the main house (if you are branched off of its power) have a 200 amp service panel? Let's assume that you have 100 amps available for now. But you might want to check so that you don't over load..
Ok. On my 100 amp service panel. I am running 2-9 light (1000's) rooms 12 & 12. One goes off the other comes on. On each room I have a 24,000 btu ac unit. Each room has its own 60 amp sub. On a
 
Quote Reply

BluBryChez

Posts
7
Reactions
2
Joined
Oct 16, 2013
Points
3
Sep 8, 2015
#697
hightide99 said:
Hey guys I would really appreciate your input THC FARMER here goes...

I have a 30 x 70 garage converted into living room fully insulated etc. It has central air from the Home A/C unit. The converted garage room has its own Electrical Circuit Box ,separate from the main house box, with (1) 30 am breaker and (2) 20 amp breakers. The circuit box says 100 AMP MAX. By the box I also have a 240 connection not being used. The room is no longer in use so I have a tent with (1) 400 watt MH and (1) 600 watt HPS inside a 8 X 8 tent. I also have four inline 6" fans, 4-5 oscillating fans various sizes, along with a 14,000 BTU Portable A/C. I also have a TV, and CPU in the room aswell. I have not had any issues with this set up as far as blowing breakers goes. My question is if I plan on adding 1-2 more 600 watt HPS ballasts will I run into any problems with the breaker box popping the breakers? Also will I need to get a light controller like the
Helios 1 - 120 Volt 4 Light Timer? The room is not in use during summer hours , so mostly from Oct-March
any advice would be awesome.
I am just not sure IF i will run into any issues if I add 1 or 2 more 600 watt hps lights to my setup. THANKS ALL INFO WELCOMED THANKS

PS The rooms wiring is fairly new and up to date THANKS
Click to expand...
BluBryChez said:
Got any room in that sub panel for more breakers? It is a sub and not a servic? Does the main house (if you are branched off of its power) have a 200 amp service panel? Let's assume that you have 100 amps available for now. But you might want to check so that you don't over load..
Ok. On my 100 amp service panel. I am running 2-9 light (1000's) rooms 12 & 12. One goes off the other comes on. On each room I have a 24,000 btu ac unit. Each room has its own 60 amp sub branched off of the main 100 amp.. All the lights and AC are running on 240. The only time I had an issue running like this is when I hired an "electrician" to wire in a small t-5 veg room for me.. He flipped everything on at once and the ac units both kicked at the same time.. Fried the wire right off the weather head! F@ckn @ss hole. I fired him! Now I wire all my everything myself. The pg&e guy chuckled as he ran a new line for me. Real Ninja right here eh?!
So... take a pic of those panels so we can tell you if its a service panel or a sub. Also I'm curious to know if that 30 amp breaker is connected to that 240 you spoke of. So pics please??
Click to expand...
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Oct 4, 2015
#698
Well I'm back on here for a little bit the kids are for now and I have a hair more free time I'll try to keep up on my post and questions if needed thanks guys
 
Reactions: fishwhistle
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Oct 4, 2015
#699
Whats up trouble?
 
Quote Reply
M

mrgrowbigbud

Posts
13
Reactions
4
Joined
Oct 2, 2015
Points
3
Oct 11, 2015
#700
RELOADER212 said:
IS it safe to hookup a dual 15 amp timer to a 1000w and the other end a 600w and a couple of fans?
I know it is close to the max amps but not sure exactly how close. I currenly have it set up that way using 2 600's, but I aquired a 1000w ballast and wanted to see how it worked. Dont 6oow use about 5 amps and 1000W about 8.5?
Thanks
Click to expand...
It depends if you are on 220 or 110 .110 almost dubbles your amps.and if you have magnettic or digital ballast.you should be fine if you are running on 220 if not you are probably a little high on amps and should put the fans on seprate breaker.
 
Quote Reply
Page 35 of 71 · Replies 681–700 of 1,407
Prev
  • 1
  • …
  • 33
  • 34
  • 35
  • 36
  • 37
  • …
  • 71
Next
First Prev 35 of 71 Next Last

Thread info

Replies 1,406
Views 327,206
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • I’m Week 4 into Flowering
    • Latest: April14th2014
    • 36 minutes ago
    General Indoor Growing
  • B
    Virginia Growers Thread - Everything VA
    • Latest: Budtirement
    • Today at 4:48 AM
    Basic Growing Information
  • S
    So Close to Harvest yet problems have started
    • Latest: SavannA
    • Today at 2:52 AM
    Cannabis Infirmary
  • how to Bubble washing and tips 2024
    • Latest: Oldchucky
    • Today at 1:47 AM
    Concentrates & Processing
  • T
    Grayoldnprouds chant of the ever circling Skeletal Family.
    • Latest: TheIslandIsGreen
    • Today at 12:48 AM
    Grow Diaries
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?