Grow Room Electrical

  • Thread starter Thread starter hiboy
  • Start date Start date Mar 20, 2012
  • Tagged users Tagged users None

Grow Room Electrical

hiboy Mar 20, 2012 1,406 Replies 327,206 Views
Page 45 of 71 · Replies 881–900 of 1,407
Prev
  • 1
  • …
  • 43
  • 44
  • 45
  • 46
  • 47
  • …
  • 71
Next
First Prev 45 of 71 Next Last

Fear

Posts
18
Reactions
31
Joined
Apr 13, 2016
Points
13
May 19, 2016
#881
Dude this wire chart is way over kill. There is hardly any voltage drop even at 200'. #4 for a 200' 20 amp run. Hahaha what a waist of time and money. Conduit has to be larger too. 1 1/2" for 100 amps which requires #2 copper. 200' you are safe to raise the wire size a single gauge for that distance.
 
Quote Reply

Fear

Posts
18
Reactions
31
Joined
Apr 13, 2016
Points
13
May 19, 2016
#882
Your HID lighting is the only thing i would oversize by one gauge if over 200'. Speaking as an electrical contractor and licensed Ca. Jorneyman.
 
Quote Reply

Surfr

Supporter
Just cruisin....
Posts
1,025
Reactions
1,224
Joined
Sep 25, 2010
Points
163
May 20, 2016
#883
What's up guys. So I have a spot that needs a 200amp panel swapped in. My buddy says it's already wired for 200 amps and all we need to do is replace the box. Can anyone confirm this? Thanks!
 

Attachments

  • image.jpeg
    137.7 KB · Views: 214
Last edited: May 20, 2016
Quote Reply

Fear

Posts
18
Reactions
31
Joined
Apr 13, 2016
Points
13
May 21, 2016
#884

That looks like #1 aluminum thw wire in your 3 phase panel 100 amp panel. Using the middle, use the 75°C column in all gauging all wire sizes. Breakers are typically rated for 75°C max fyi. So your feeders right now are rated for 100amps. (ninth down/six over)

Ok so for 200 amps I recommend 3/0 copper. Or you can use 250 mcm al. wire. The copper wire will require a 2" conduit and the al. wire will require 2 1/2" conduit. Al. Suck and 2 1/2" parts typically can't be purchased at your local hardware store either. Also by the looks of the lugs the panel might only be rated for 100 amps maybe 125amps.

3 phase panel gives you ample room for proper electrical distribution at 100 amps. Ive ran +11k watts in lights, ac, fans, pumps etc on less than 100amps on a single phase panel. Hope that helps.
 
Quote Reply

usstoner

Posts
1,106
Reactions
3,279
Joined
Jun 4, 2011
Points
263
May 21, 2016
#885
That's an old panel..looks like old rag wire...I'd upgrade...and what Fear said..
 
Reactions: Fear
Quote Reply

Surfr

Supporter
Just cruisin....
Posts
1,025
Reactions
1,224
Joined
Sep 25, 2010
Points
163
May 21, 2016
#886
Thanks fear, I really appreciate the info. I need at least 140 amps at this spot. I'm going to have my buddy who's a union electrician do all the work for me. I'll keep everyone updated on the progress!
 
Reactions: Fear
Quote Reply

Fear

Posts
18
Reactions
31
Joined
Apr 13, 2016
Points
13
May 24, 2016
#887
Surfr said:
Thanks fear, I really appreciate the info. I need at least 140 amps at this spot. I'm going to have my buddy who's a union electrician do all the work for me. I'll keep everyone updated on the progress!
Click to expand...
unfortunately they don't have a 140 panel. 60, 100, 125 and 200 amps is what panels are rated for. So to get 140 amps you will still need a 200 amp panel you will just have to downsize the breAker to what you need. My advice would be to just install the full 2hun. 2" emt and copper wire size 3/0. This way you can handle any future expansion.

Peace
 
Quote Reply
A

Apexgardens

Posts
1
Joined
May 22, 2016
Points
1
May 24, 2016
#888
haha wrong thread. Sorry guys.
 
Quote Reply

Surfr

Supporter
Just cruisin....
Posts
1,025
Reactions
1,224
Joined
Sep 25, 2010
Points
163
May 24, 2016
#889
Yeha I'm doing the 200 install. I was just saying I need at least 140 amps for what I'm running at this spot. Thanks again bro!
 
Reactions: Fear
Quote Reply

Fear

Posts
18
Reactions
31
Joined
Apr 13, 2016
Points
13
Jun 1, 2016
#890
No problem man just being thourough for anyone else who might need to do the same. Later on
 
Quote Reply

Cali clouds

Posts
267
Reactions
541
Joined
Mar 27, 2016
Points
93
Jun 3, 2016
#891
What's up guys, I'm looking at a spot with a 100a 3phase panel. I was hoping to get at least a 200a. Can the 3 phase be broken down to get more amps or is a 100a panel only good for 100a no matter what? Thanks
 
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jun 3, 2016
#892
which type of 3 phase is it?
480/277v
208/120v
240/120v (high leg corner ground delta)
 
Reactions: oscar169
Quote Reply

Cali clouds

Posts
267
Reactions
541
Joined
Mar 27, 2016
Points
93
Jun 3, 2016
#893
You just lost me lol I don't have a clue I'm guessing 240 but I could be wrong. I will ask the owner
 
Quote Reply

Humboldt.Rio

Posts
309
Reactions
525
Joined
Oct 16, 2012
Points
93
Jun 23, 2016
#894
Whatz up guys, need help with electrical. It's been awhile. I have 30amp breaker for 220 and a ground. So 3 wire. Two hot. One ground.

I have a 20amp 125v receptical. It has top and bottom with the bridge connected. I would like to use both.

I know brass side is hot, silver is ground. But since no neutral is being used. I just hook up one brass and one silver for each side using 110. Then ground.

Im just gonna run 3 600's so I'm well under 20 amps.

Is this all right?

Thanks in advance for the help.
 
Quote Reply

X.rm

Posts
216
Reactions
230
Joined
May 10, 2016
Points
43
Jun 24, 2016
#895
Humboldt.Rio said:
Whatz up guys, need help with electrical. It's been awhile. I have 30amp breaker for 220 and a ground. So 3 wire. Two hot. One ground.

I have a 20amp 125v receptical. It has top and bottom with the bridge connected. I would like to use both.

I know brass side is hot, silver is ground. But since no neutral is being used. I just hook up one brass and one silver for each side using 110. Then ground.

Im just gonna run 3 600's so I'm well under 20 amps.

Is this all right?

Thanks in advance for the help.
Click to expand...
You should be fine as far as amperage is concerned at 220v your amps are cut in half pretty much, at 220v three 600W your looking roughly at about 10 and a half amps. One thing you dont mention is wire gauge. If your using 220v make sure your extension cord is the apropriate gauge like a 10 gauge or so. You dont want them to overheat before the breaker does because it will pose a fire hazard. Best of luck.
 
Reactions: Humboldt.Rio
Quote Reply

Humboldt.Rio

Posts
309
Reactions
525
Joined
Oct 16, 2012
Points
93
Jun 24, 2016
#896
X.rm said:
You should be fine as far as amperage is concerned at 220v your amps are cut in half pretty much, at 220v three 600W your looking roughly at about 10 and a half amps. One thing you dont mention is wire gauge. If your using 220v make sure your extension cord is the apropriate gauge like a 10 gauge or so. You dont want them to overheat before the breaker does because it will pose a fire hazard. Best of luck.
Click to expand...
Its either 6 or 8

Cheers
 
Quote Reply

Humboldt.Rio

Posts
309
Reactions
525
Joined
Oct 16, 2012
Points
93
Jun 24, 2016
#897
Humboldt.Rio said:
Its either 6 or 8

Cheers
Click to expand...
So I just hooked everything up and just flicked one of the two breakers on and got a poof!! Scared the fuck out of me!

Ill attach pics as to what's going on.
Humboldt.Rio said:
Its either 6 or 8

Cheers
Click to expand...
 

Attachments

  • DSC_0470.JPG
    64.9 KB · Views: 87
Quote Reply

Humboldt.Rio

Posts
309
Reactions
525
Joined
Oct 16, 2012
Points
93
Jun 24, 2016
#898
Humboldt.Rio said:
So I just hooked everything up and just flicked one of the two breakers on and got a poof!! Scared the fuck out of me!

Ill attach pics as to what's going on.
Click to expand...
 

Attachments

  • DSC_0471.JPG
    67.1 KB · Views: 80
Quote Reply

Humboldt.Rio

Posts
309
Reactions
525
Joined
Oct 16, 2012
Points
93
Jun 24, 2016
#899
Thanks!
 

Attachments

  • DSC_0472.JPG
    72.5 KB · Views: 87
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jun 25, 2016
#900
Get solid wire and use the side screws.
 
Quote Reply
Page 45 of 71 · Replies 881–900 of 1,407
Prev
  • 1
  • …
  • 43
  • 44
  • 45
  • 46
  • 47
  • …
  • 71
Next
First Prev 45 of 71 Next Last

Thread info

Replies 1,406
Views 327,206
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • B
    Virginia Growers Thread - Everything VA
    • Latest: Budtirement
    • 26 minutes ago
    Basic Growing Information
  • S
    So Close to Harvest yet problems have started
    • Latest: SavannA
    • Today at 2:52 AM
    Cannabis Infirmary
  • how to Bubble washing and tips 2024
    • Latest: Oldchucky
    • Today at 1:47 AM
    Concentrates & Processing
  • T
    Grayoldnprouds chant of the ever circling Skeletal Family.
    • Latest: TheIslandIsGreen
    • Today at 12:48 AM
    Grow Diaries
  • T
    Any tips for my first guerilla grow?
    • Latest: TheIslandIsGreen
    • Today at 12:42 AM
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?