Jun 28, 2016
#901
So I have a little bit of electrical I'm trying to figure out. I have 2 greenbeams and a de on the way all 240v. I want to keep modifications to the electrical to the minimum. I have a unused dryer outlet it my basement wired to a dedicated 30amp 240v circuit. The dryer outlet is a Nema 14-30r 125v-250v 30amp outlet. I recently fished some 10-3 from that outlet to my grow room. I also purchased a 30/50a 125/250v Nema 14-30p male plug. Is it ok to wire the 10-3 to the plug to avoid having to take apart the receptale? Also all the receptacles for the light need to be 240v 20a correct? Is it safe to wire a 2 20amp receptacles to one another? I've been also looking at light controllers to solve this issue. This one in particular

Last thing I have a dedicated outlet 20a 120v circuit but only 15a receptacle I purchased some 14-2 to run from that outlet. Is that going to be ok as long as I put a duplex 15a receptacles on it?

I'm a eager to get things going and plan on getting a journal started here shortly. Thanks in advance.
 
Quote Reply

X.rm

Posts
216
Reactions
230
Joined
May 10, 2016
Points
43
Jun 29, 2016
#902
Quicksilv312 said:
So I have a little bit of electrical I'm trying to figure out. I have 2 greenbeams and a de on the way all 240v. I want to keep modifications to the electrical to the minimum. I have a unused dryer outlet it my basement wired to a dedicated 30amp 240v circuit. The dryer outlet is a Nema 14-30r 125v-250v 30amp outlet. I recently fished some 10-3 from that outlet to my grow room. I also purchased a 30/50a 125/250v Nema 14-30p male plug. Is it ok to wire the 10-3 to the plug to avoid having to take apart the receptale? Also all the receptacles for the light need to be 240v 20a correct? Is it safe to wire a 2 20amp receptacles to one another? I've been also looking at light controllers to solve this issue. This one in particular

Last thing I have a dedicated outlet 20a 120v circuit but only 15a receptacle I purchased some 14-2 to run from that outlet. Is that going to be ok as long as I put a duplex 15a receptacles on it?

I'm a eager to get things going and plan on getting a journal started here shortly. Thanks in advance.
Click to expand...
Im not an electrician and therefore my comments should just be taken as a personal experience account. I wouldn'twant to be accountable for misinformed advice. Having said that, i personally have used a preexisting 220v outlet to power several 1k lights, when you use 220v the amperage is reduced by 50% roughly. So with a 30amp circuit braker you coild easily use 5, 1k watt lights. What i have done is wire the actual outlet directly to an autopilot light controler with a relay trigger. The relay gos to a 110v outlet on a timer snd the ballasts straight to the light controller.
 
Reactions: Natural
Quote Reply

X.rm

Posts
216
Reactions
230
Joined
May 10, 2016
Points
43
Jun 29, 2016
#903
Always consult with a professional if at all possible. Best of luck to you.
 
Reactions: Natural
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jun 29, 2016
#904
Quicksilv312 said:
So I have a little bit of electrical I'm trying to figure out. I have 2 greenbeams and a de on the way all 240v. I want to keep modifications to the electrical to the minimum. I have a unused dryer outlet it my basement wired to a dedicated 30amp 240v circuit. The dryer outlet is a Nema 14-30r 125v-250v 30amp outlet. I recently fished some 10-3 from that outlet to my grow room. I also purchased a 30/50a 125/250v Nema 14-30p male plug. Is it ok to wire the 10-3 to the plug to avoid having to take apart the receptale? Also all the receptacles for the light need to be 240v 20a correct? Is it safe to wire a 2 20amp receptacles to one another? I've been also looking at light controllers to solve this issue. This one in particular

Last thing I have a dedicated outlet 20a 120v circuit but only 15a receptacle I purchased some 14-2 to run from that outlet. Is that going to be ok as long as I put a duplex 15a receptacles on it?

I'm a eager to get things going and plan on getting a journal started here shortly. Thanks in advance.
Click to expand...

On the 220v dryer plug..
Your best bet is to use a controller to time the lights via a 120v trigger cord and relay, like Xrm does. But yes you can split-bolt wires as a junction for multiple outlets..take heed to wrap well and thick with quality electrical tape if you do...put the junctions, evenly spaced in a work box.
The other way is to wire a dryer end plug and that will exist as your junction to feed a controller. You do not need 10-3...10-2 grounded is enough. But since you already have it, 2 hots and a ground is all you will use..the neutral (white)will be capped at the controller side(new 220 receptacles are 10-3 by code these days to provide 120v such as a timer or added ground etc). In order to find out exactly which blades of the receptacle are hot and which is ground and neutral..you need to open the receptacle up and have a look. Wire Black and Red as hot..match your green to green(ground) and white to white (neutral)..then at the controller, hook up your hots and ground and cap the neutral.

Yes you can wire 15 amp 120v on 20 amp 120v circuit..just not the other way around. 14-2 should be okay..unless it is a ridiculously long run..or you intend to upgrade the receptacle to a 20 amp plug..then use 12-2.
 
Reactions: X.rm
Quote Reply
Q

Quicksilv312

Posts
2
Reactions
1
Joined
Jun 27, 2016
Points
3
Jun 29, 2016
#905
Thanks for the advice, I will pick up that light controller and just pick up the matching 30a receptacle for it. I will have a dedicated 30a 240v, a dedicated 15a 120v and a shared 15a 120v for the room. Should handle plenty of amps now.
 
Reactions: X.rm
Quote Reply

Savage Henry

Posts
960
Reactions
1,717
Joined
Sep 27, 2015
Points
143
Jul 19, 2016
#906
Hi all, I just picked up one of these: http://m.ebay.com/itm/110V-Digital-...-99-RH-HM-40-Type-US-/281762303023?nav=SEARCH

And I plan to use it to control a humidifier. Only issue is the humidifier runs at 8 amps and the switch on the above controller is only rated for 5 amps. From what I understand this can be remedied with a 10-15amp relay but I am at a loss on choosing one and installing it.

Seems like a fairly simple maneuver I just have no experience wiring electronics.

Thanks!
 
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 19, 2016
#907
Savage Henry said:
Hi all, I just picked up one of these: http://m.ebay.com/itm/110V-Digital-...-99-RH-HM-40-Type-US-/281762303023?nav=SEARCH

And I plan to use it to control a humidifier. Only issue is the humidifier runs at 8 amps and the switch on the above controller is only rated for 5 amps. From what I understand this can be remedied with a 10-15amp relay but I am at a loss on choosing one and installing it.

Seems like a fairly simple maneuver I just have no experience wiring electronics.

Thanks!
Click to expand...
IMO the more contacts and junctions you have the higher the risk of failure. This is a simple fix..instead of buying the relay..just buy a higher rated humidistat and make clean work of it.
https://www.amazon.com/docooler-Dig...ywords=Digital+Air+Humidity+Controller+10+amp

BTW..relays can be simple animals that usually include simple schematics..unless it is a broad range use device, in which case it can seem very complicated. Here's a quick look to appease your curiosity.
https://www.hvacquick.com/howtos/howto_relay.php
 
Reactions: Savage Henry
Quote Reply

Savage Henry

Posts
960
Reactions
1,717
Joined
Sep 27, 2015
Points
143
Jul 20, 2016
#908
Natural said:
IMO the more contacts and junctions you have the higher the risk of failure. This is a simple fix..instead of buying the relay..just buy a higher rated humidistat and make clean work of it.
https://www.amazon.com/docooler-Dig...ywords=Digital+Air+Humidity+Controller+10+amp

BTW..relays can be simple animals that usually include simple schematics..unless it is a broad range use device, in which case it can seem very complicated. Here's a quick look to appease your curiosity.
https://www.hvacquick.com/howtos/howto_relay.php
Click to expand...

Word. Thanks, boss. This is what happens when I impulse buy, didn't occur to me until I got the thing in the mail to check the amperage of the humidifier. Chalk that move up to an excess of espesso and smoke in the am.

I see your point with the probability of failure increasing with each added component, but let's say I was to tinker with this anyway, would you recommend a solid state or coil relay?

I may have to put in a photosensor switch as well so the thing doesn't kick on during lights out, but I'll check to see how it restarts if I simply plug it into a timer first.
 
Quote Reply

X.rm

Posts
216
Reactions
230
Joined
May 10, 2016
Points
43
Jul 20, 2016
#909
Savage Henry said:
Hi all, I just picked up one of these: http://m.ebay.com/itm/110V-Digital-...-99-RH-HM-40-Type-US-/281762303023?nav=SEARCH

And I plan to use it to control a humidifier. Only issue is the humidifier runs at 8 amps and the switch on the above controller is only rated for 5 amps. From what I understand this can be remedied with a 10-15amp relay but I am at a loss on choosing one and installing it.

Seems like a fairly simple maneuver I just have no experience wiring electronics.

Thanks!
Click to expand...
Try to find some one with experience to do it.
 
Quote Reply

X.rm

Posts
216
Reactions
230
Joined
May 10, 2016
Points
43
Jul 20, 2016
#910
Savage Henry said:
Word. Thanks, boss. This is what happens when I impulse buy, didn't occur to me until I got the thing in the mail to check the amperage of the humidifier. Chalk that move up to an excess of espesso and smoke in the am.

I see your point with the probability of failure increasing with each added component, but let's say I was to tinker with this anyway, would you recommend a solid state or coil relay?

I may have to put in a photosensor switch as well so the thing doesn't kick on during lights out, but I'll check to see how it restarts if I simply plug it into a timer first.
Click to expand...
At lights out is usually when humidity spikes. Lights go out , plants transpire ,hot air rises and humidity spikes. Get a thermostat that records highest and lowest tempd for each day
 
Quote Reply

Savage Henry

Posts
960
Reactions
1,717
Joined
Sep 27, 2015
Points
143
Jul 20, 2016
#911
X.rm said:
At lights out is usually when humidity spikes. Lights go out , plants transpire ,hot air rises and humidity spikes. Get a thermostat that records highest and lowest tempd for each day
Click to expand...

For sure, man, already on that. I'm just trying to rig up a humidifier so I can dial in my vpd when the lights are on.:)
 
Reactions: X.rm
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 20, 2016
#912
Savage Henry said:
Word. Thanks, boss. This is what happens when I impulse buy, didn't occur to me until I got the thing in the mail to check the amperage of the humidifier. Chalk that move up to an excess of espesso and smoke in the am.

I see your point with the probability of failure increasing with each added component, but let's say I was to tinker with this anyway, would you recommend a solid state or coil relay?

I may have to put in a photosensor switch as well so the thing doesn't kick on during lights out, but I'll check to see how it restarts if I simply plug it into a timer first.
Click to expand...
I wouldn't..but the electromechanical one won't rob the load and be affected by high temps as much. I only use relays in automotive settings and have not fiddled with HVAC relays as much. You might get better advice in the AC/HVAC thread from Johnboy.
Have you seen this video..not sure if the chinese manual is correct or wrong after watching it and reading the comments. But might lend you some insight if you were planning on wiring the humidistat as a relay with a separate power source as opposed to wiring in place of factory control board.
 
Reactions: Savage Henry
Quote Reply

newbie1

Posts
105
Reactions
103
Joined
May 12, 2016
Points
28
Jul 20, 2016
#913
Hi folks. I got a slight problem maybe someone can help with. I have a 600 watt dimable ballast that has stopped working, its brand new so got a new one on the way, no probs there, apart from plants sitting in day light room and light schedule been messed up :-( The thing is im thinking this could either be a manufacturers fault or something im running has caused it, if the latter i need to sort it as obviously i dont want to blow another :-( So ive first checked all electrics and all is fine, ive also looked inside the contactor that is a ECOTECHNICS POWERSTAR LIGHTING CONTACTOR RELAY, sorry bout caps, just copied and pasted :) when i look inside it has 2 wires going nowhere, they have contacts on the end to attach somewhere but there are no free conacts and no where else for them to go. Has any one taken one of these appart bfore and if so is it normal to have 2 wires going nowhere. Many thanks NUBE
 
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 20, 2016
#914
newbie1 said:
Hi folks. I got a slight problem maybe someone can help with. I have a 600 watt dimable ballast that has stopped working, its brand new so got a new one on the way, no probs there, apart from plants sitting in day light room and light schedule been messed up :-( The thing is im thinking this could either be a manufacturers fault or something im running has caused it, if the latter i need to sort it as obviously i dont want to blow another :-( So ive first checked all electrics and all is fine, ive also looked inside the contactor that is a ECOTECHNICS POWERSTAR LIGHTING CONTACTOR RELAY, sorry bout caps, just copied and pasted :) when i look inside it has 2 wires going nowhere, they have contacts on the end to attach somewhere but there are no free conacts and no where else for them to go. Has any one taken one of these appart bfore and if so is it normal to have 2 wires going nowhere. Many thanks NUBE
Click to expand...
I have no idear if your relay killed your ballast. The specs on that ecotechnic seem pretty lightweight with no arc protection.
Get a heavy duty ballast timer instead. like one of these..
https://www.amazon.co.uk/Aquariam-Reptile-House-Heater-Switch/dp/B00GEUTVWI

http://www.ebay.co.uk/itm/PLUG-AND-...-600W-GROW-LIGHTS-FOR-GROW-TENT-/270732866707
 
Quote Reply

newbie1

Posts
105
Reactions
103
Joined
May 12, 2016
Points
28
Jul 20, 2016
#915
Thanks for reply @Natural :) Ive got this timer (pic) that i think is a heavy duty. (Its not this make but the same type) If i have one of these is it okay to run straight from wall socket
 

Attachments

  • s-l500.jpg
    16.8 KB · Views: 365
Last edited: Jul 20, 2016
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 20, 2016
#916
newbie1 said:
Thanks for reply @Natural :) Ive got this timer (pic) that i think is a heavy duty. (Its not this make but the same type) If i have one of these is it okay to run straight from wall socket
Click to expand...
I'm not very familiar with UK type timers in general, as I'm in the States, but as long as it's rated high enough to run the amps on your ballast I don't see a problem with it.
 
Quote Reply
S

SmokeyMcP0t

Posts
4
Joined
Jun 11, 2011
Points
1
Jul 22, 2016
#917
Hello, I am looking for help wiring a Ranco ETC temp controller back on to a 5 ton CHillking Chiller. I am unsure which connections need to go where inside the ranco controller . Power and temp are on but I do not know how to use the ranco controller to turn on the compressor, what to connect to common, and n/o or n/c
 

Attachments

  • ranco.jpg
    112.6 KB · Views: 653
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 22, 2016
#918
SmokeyMcP0t said:
Hello, I am looking for help wiring a Ranco ETC temp controller back on to a 5 ton CHillking Chiller. I am unsure which connections need to go where inside the ranco controller . Power and temp are on but I do not know how to use the ranco controller to turn on the compressor, what to connect to common, and n/o or n/c
Click to expand...
According to the pdf here it will depend on the supply voltage.
Inspect the wiring diagram. The "load" indication always describes the device being powered, in this case your chiller. The wire going to "COM" and also branching to the "load" device is going to be common or white. Apparently "C" seems to indicate where the sensor interrupts the voltage line in some of the diagrams. Diagram 4 is typical for 120volt wiring and figure 5 is for 240v. I don't see them using N/C in any of the diagrams. If you need further explanation I suggest calling Ranco in Plain City.
 
Quote Reply
S

SmokeyMcP0t

Posts
4
Joined
Jun 11, 2011
Points
1
Jul 22, 2016
#919
Is there an easy way to determine my supply voltage? And a further explanation of what that is. This controller is powered on by means of a standard wall outlet (on the far right block using the inputs labeled 120 and common). But the chiller is installed on 220. I have a few live wires I can test but I am unsure what to look for on a multi meter. So You are saying I positively need a branching wire ?I planned to use figure six but I am unsure which wire would be considered what. I hope this makes sense, thanks for your help. I can take whatever pictures necessary
 
Quote Reply

Natural

Posts
2,536
Reactions
4,395
Joined
Apr 21, 2011
Points
263
Jul 22, 2016
#920
Well from the looks of it you have the power to the controller wired correctly..which is 120v. You answered your question about the chiller being 240v. In this case you won't need to branch the common as you have 2 different voltages and will use fig 6.
Your picture is misleading as I cannot determine what wire that is feeding up through the bottom along with your control "power cord".
240v typically has 2 hots and a ground, there is no need for a common wire. Although, it is code to install 4 wire 240v now..which means 2 hots a ground and a neutral. In most cases the neutral is used to run an lcd panel or timer of a high voltage device such as a dryer or stove. The neutral allows one leg to be utilized to provide the need for 120v in addition to the main power which is 240. Devices such as ballasts only require 2 hots and a ground for over-load safety. I'm not exactly sure the requirement for a chiller. But by looking at the tabs where you wire in the chiller should tell the tale.
The problem I'm having with this diagram, is that it is not indicated whether or not it is only showing the 2 hot wires feeding the chiller aka "load" or whether it includes the ground wire. An educated guess is that it is only showing both hot wires of the 240v (which is basically 2 wires at 120v). In that thinking, where the 2 hot wires coming from the panel to your chiller go are simple. First..one wire goes continuously to the chiller and one gets wired into "C" and continues out of "N/O" to the device.
I would double check with the manufacturer that this is correct. These companies are used to questions like this. Do you follow me?
 
Quote Reply
Page 46 of 71 · Replies 901–920 of 1,407
Prev
  • 1
  • …
  • 44
  • 45
  • 46
  • 47
  • 48
  • …
  • 71
Next
First Prev 46 of 71 Next Last

Thread info

Replies 1,406
Views 327,209
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • Jealousy (feminized) from Seed Supreme
    • Latest: jadins_journey
    • 44 minutes ago
    Grow Diaries
  • Grayoldnprouds chant of the ever circling Skeletal Family.
    • Latest: grayoldnproud
    • 49 minutes ago
    Grow Diaries
  • Drinking from a Cattle Trough
    • Latest: jadins_journey
    • 53 minutes ago
    Grow Diaries
  • 2026 Outdoor Grows! let's see em!
    • Latest: Leste
    • 53 minutes ago
    General Outdoor Growing
  • D
    Humidity!! help me avoid rot and mildew
    • Latest: dr.thumbgreen
    • 56 minutes ago
    Cannabis Infirmary
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?