#1,121
Dan789 said:
So that protection is for electrical surge as in if your home was struck by lightning. Most have some type thermal trip integrated, but not all. Otherwise lots of people use them, I've got several under my desk with a plethora of cords for my computer and ancillary crap. For our growing endeavors where we may not be watching 24/7 or even in the same room is my only concern with untended electrical apparatus. Lights, fans, tubes that can explode, ballasts that can do the same rupturing their insulation and innards all over. I've seen some controllers that have heat or smoke inputs that will shutdown all the power when/if something like a high heat or smoke situation arises. That would be ideal from an electrical safety outlook. Peace.
Click to expand...
Newer construction and electrical codes have these "Arc fault" c/b for most of the 15 & 20 amp circuits supplied, those offer more "arc" style protection to supplied electrical devices. (they don't do anything for smoke) But they're (Arc-fault c/b's) a little temperamental in some situations and some early brands had false tripping issues. Neither here nor there, as they aren't to widely adopted yet.
 
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Apr 4, 2017
#1,122
tinderthumbs said:
ill re ask the ? I had

so I have a 100wat inline fan plugged in to a power bar with a surg protection rated to hold up to 3000 jul of power

with it be ok
Click to expand...
It should be fine to supply the miniscule load of the fan, it will only protect you from lightning (electrical surge) damaging the fan and anything else you have plugged into it. That's all the protection it provides, hope that clarifies what I was saying. Let me know if I've answered your question.
 
Reactions: hiboy and tinderthumbs
Quote Reply

tinderthumbs

Posts
3,712
Reactions
5,844
Joined
Aug 18, 2016
Points
263
Apr 4, 2017
#1,123
Dan789 said:
It should be fine to supply the miniscule load of the fan, it will only protect you from lightning (electrical surge) damaging the fan and anything else you have plugged into it. That's all the protection it provides, hope that clarifies what I was saying. Let me know if I've answered your question.
Click to expand...

I bought it bc I had a ton of cfls plugged in to it took them all put up 600wat mh on the plug next it but not the power bar
only thing I have plugged in to it is the fan

im only asking bc I see it says don't ever run a heater on a power bar but think that is bc the pull so much power???
 
Quote Reply

Ownzu77

Posts
29
Reactions
56
Joined
Jun 18, 2016
Points
13
Apr 4, 2017
#1,124
Dan789 said:
So your asking is it ok using a power strip to supply a exhaust fan, that trips said protection device? No. find the problem, check for a wiring fault, most likely check everything you've done.
The power box above is an construction site distribution system, not associated with power strips.
Click to expand...

As far as I know you won't find a powerbox on a construction site, they are niche boxes for cannabis growers. Google dpc 8000 to see the model I use. The chord that's on it is the thickest I've seen, it was 4 dollars a foot.
 
Reactions: tinderthumbs
Quote Reply

tinderthumbs

Posts
3,712
Reactions
5,844
Joined
Aug 18, 2016
Points
263
Apr 4, 2017
#1,125
how many watts can a 15 amp pull before getting hot and poping??
 
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Apr 4, 2017
#1,126
Ownzu77 said:
As far as I know you won't find a powerbox on a construction site, they are niche boxes for cannabis growers. Google dpc 8000 to see the model I use. The chord that's on it is the thickest I've seen, it was 4 dollars a foot.
Click to expand...
Thanks for clarifying my erroneous assumption. Wow $4/ft. and $ 400 for the box (timer, one relay, four plugs, metal enclosure probably $100 in parts) is taking advantage of you/community. Just as a reference range cord can be obtained from any electrical supply in lengths, but then there's the connection to the plug and cracking the cover of the device, which then will void any warrantee.
I don't see any individual circuit/plug c/b (circuit breakers) so it's relying on the 50/2 c/b that your connecting to. That said it's a much better situation, but still you've got the cord issues.
 
Quote Reply

Ownzu77

Posts
29
Reactions
56
Joined
Jun 18, 2016
Points
13
Apr 4, 2017
#1,127
Thank you very much for taking time to understand my situation and try to help me . It means a lot. I'm trying to understand how it might play out, he sees the chords, interprets them as a subistute for permanent wiring? What if I say they are temporary for 90 days? And what about the room immediately adjacent to the kitchen, the power box can easily reach the next room but it has to pass by what used to be a door way but is really just an open room partition at this point. And do they really even violate people for residential extension chords? I can't find any examples .

And what are my rights as a tenant to switch the bedroom outlets to 240s? Would save me some headache but then how do I power the accessories without an extension chord lol...
 
Quote Reply

Dan789

Posts
2,954
Reactions
5,123
Joined
Mar 6, 2017
Points
263
Apr 4, 2017
#1,128
That's outside my limited expertise (lol). Maybe another in the community has some input on tenants rights.
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 5, 2017
#1,129
tinderthumbs said:
hell thought id ask is it ok to put a exfan/inline in to a power strip I paid good money for it does 3000 jul before over loading
Click to expand...
No problem with a power strip (surge protector?) if its rated ti handle it
Hb
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 5, 2017
#1,130
Ownzu77 said:
Thank you very much for taking time to understand my situation and try to help me . It means a lot. I'm trying to understand how it might play out, he sees the chords, interprets them as a subistute for permanent wiring? What if I say they are temporary for 90 days? And what about the room immediately adjacent to the kitchen, the power box can easily reach the next room but it has to pass by what used to be a door way but is really just an open room partition at this point. And do they really even violate people for residential extension chords? I can't find any examples .

And what are my rights as a tenant to switch the bedroom outlets to 240s? Would save me some headache but then how do I power the accessories without an extension chord lol...
Click to expand...

Why don't you just unplug them if the landlord wants to come in
Probably not a good idea to make any changes to the dwelling since you would be responsible is any problems occur
Hb
 
Quote Reply

lurrabq

Posts
54
Reactions
71
Joined
Oct 24, 2014
Points
18
Apr 5, 2017
#1,131
tinderthumbs said:
how many watts can a 15 amp pull before getting hot and poping??
Click to expand...
1440 watts would be what the code would allow. The circuit breaker will carry that as long as there are no motors being started. Remember, you have some ballast loss in the lights that adds to the circuit total wattage
 
Reactions: Dan789
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 5, 2017
#1,132
lurrabq said:
1440 watts would be what the code would allow. The circuit breaker will carry that as long as there are no motors being started. Remember, you have some ballast loss in the lights that adds to the circuit total wattage
Click to expand...
I wouldn't say that's actually correct
1440 watts is the amount that a 15 amp breaker should have maxed out with a continuous load of more than three hours but it would take more wattage for it to trip
Placing more wattage on a break or will just have the breaker we're out quicker but it will trip if there is a safety or heat issue as long as everything is operating correctly
Hb
 
Reactions: GLGC.MI, fatawa and tinderthumbs
Quote Reply

lurrabq

Posts
54
Reactions
71
Joined
Oct 24, 2014
Points
18
Apr 7, 2017
#1,133
hiboy said:
I wouldn't say that's actually correct
1440 watts is the amount that a 15 amp breaker should have maxed out with a continuous load of more than three hours but it would take more wattage for it to trip
Placing more wattage on a break or will just have the breaker we're out quicker but it will trip if there is a safety or heat
Hb
Click to expand...
No explanation necessary for me. Just trying to convey some basics to the guy with the issue. I've designed much more complex systems for longer than I want to admit.
 
Last edited: Apr 7, 2017
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 9, 2017
#1,134
240v outlet is connected to a 30amp breaker
240v x 30amp=7200 total kw

80%=5760 watts that can be used.

is this correct?
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 9, 2017
#1,135
terrapin11 said:
240v outlet is connected to a 30amp breaker
240v x 30amp=7200 total kw

80%=5760 watts that can be used.

is this correct?
Click to expand...
No
You can have a 240 V breaker on many different amperage sizes it depends on your draw is
Hb
 
Reactions: fatawa
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 9, 2017
#1,136
hiboy said:
No
You can have a 240 V breaker on many different amperage sizes it depends on your draw is
Hb
Click to expand...

ok.
i would like to power two 600w lights (powered by phantom digital ballasts)
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 9, 2017
#1,137
terrapin11 said:
ok.
i would like to power two 600w lights (powered by phantom digital ballasts)
Click to expand...
You can put them both on 120 V or 240 V either one will hold
Hb
 
Reactions: terrapin11
Quote Reply

GLGC.MI

Posts
143
Reactions
218
Joined
Oct 1, 2016
Points
43
Apr 16, 2017
#1,138
GLGC.MI said:
Lost power on the circuit shown. Won't come back. No idea what to do. Moved lights to another set of plugs but I'm still without juice to a lot of the building.
Click to expand...
Alright. Got electricity sorted out. But now I wanna know if I can wire in another sub-50a if I already have 200 to the house. Did an electricity map and let's just say the wiring is... unorthodox. Lol. So I wanna a fresh box to play on. Is that to much draw for a residence? Like to much from the main line?
 
Quote Reply

hiboy

Posts
2,347
Reactions
971
Joined
Dec 2, 2010
Points
113
Apr 17, 2017
#1,139
GLGC.MI said:
Alright. Got electricity sorted out. But now I wanna know if I can wire in another sub-50a if I already have 200 to the house. Did an electricity map and let's just say the wiring is... unorthodox. Lol. So I wanna a fresh box to play on. Is that to much draw for a residence? Like to much from the main line?
Click to expand...
Hard to say without being there
But most likely you will have no problems
Install #6 wire to your sub panel
If there is an overload on your 200 it will trip so you should be safe
Hb
 
Quote Reply
T

terrapin11

Posts
19
Joined
Mar 30, 2017
Points
1
Apr 18, 2017
#1,140
actually, looks like i have a 250v outlet connected to a 30a.
i was looking to purchase an adapter cord to run from that 250v outlet to plug my two phantom II digital ballasts into.

will this adapter cord work?
 
Quote Reply
Page 57 of 71 · Replies 1,121–1,140 of 1,407
Prev
  • 1
  • …
  • 55
  • 56
  • 57
  • 58
  • 59
  • …
  • 71
Next
First Prev 57 of 71 Next Last

Thread info

Replies 1,406
Views 327,221
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Oldchucky
    • A moment ago
    General Outdoor Growing
  • how to Bubble washing and tips 2024
    • Latest: Oldchucky
    • 6 minutes ago
    Concentrates & Processing
  • 2026 Outdoor Grows! let's see em!
    • Latest: Tahoekushcat
    • 13 minutes ago
    General Outdoor Growing
  • Some advice needed on outdoor growing...
    • Latest: BaldrickTX
    • 22 minutes ago
    General Outdoor Growing
  • C
    How Little PPM can they handle?
    • Latest: ClemSP
    • 43 minutes ago
    Basic Growing Information
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?