Yes I'm sorry i meant 6 600s and I'm in California.?? say what? 600 - 600watt lights. or 6 - 600w. A 3600 w total 2 - 20 amp 120 v circuits will do the lights A/C & Dehu will depend on room size, the amount of plants, heat generated, exhaust +++. 1 -15 amp circuit should cover your A/C or Dehu and there is enough room left on the 2 - 20 amps for fans & intake & exhaust . Will you need heat for lights off time.. add another 15 amp circuit.
Are you in the USA? Canada? electrical requirements are different in other parts of the world with the voltage supplied.
So you're saying 2 20amp and 2 15amp circuts should cover everything.
What would i say to an electrician to install it.can't say I'm growing.