burnt as in melted? or just loose/no more good?Of course.. now I wonder when the breaker burnt... yikes..!
burnt as in melted? or just loose/no more good?
did you replace it or just adjust it?
Melted... :(
I replaced but am not sure why it melted.... The wire is 8 gauge, the power box is 50 AMP and so is the breaker...
I am only running 30 AMPS worth of lights.... or so.
only using about 30 amps... and the power box and breaker - both 50...weird, sounds like faulty breaker...do you have separate breakers for each plug? or just one main breaker? 50 amp breaker should handle 40amps continuous load .... more than that could lead to it eventually melting from heat...sounds like there was some resistance in the breaker for it to melt down, lucky no fire man
i just had mine custom built @ dxhydro, love having it custom, have a separate breaker for each outlet, plus dual voltage/amp meters on each main feed wire...should be comming in the main any day now...i made sure it was over built, that guy kept talking about how powerbox is cheaply built, so i made sure he overbuilt my unit
Do you check your lugs inside your Powerbox? One of mine came loose and arched and burnt/melted everything inside.I have 5 different powerboxes.. Everyone of them still works.. All are still in use. I have a 6 light..8 yrs old.. 8 light... 2yrs old...10 light 5 years old.., 12 light... 5 years old and their new 24 light. Never had any problems other than a battery going out on the built in timer.. All other problems have ended up being due to a breaker gone bad or a lug coming loose after a few years of use from heat.