Help! Powerbox 12000 Light Controller Wont Turn On The Lights Today!!!!

  • Thread starter Thread starter miko
  • Start date Start date Jun 8, 2015
  • Tagged users Tagged users None

Help! Powerbox 12000 Light Controller Wont Turn On The Lights Today!!!!

miko Jun 8, 2015 21 Replies 4,479 Views
Page 1 of 2 · Replies 1–20 of 22
  • 1
  • 2
Next
1 of 2 Next Last

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 8, 2015
#1
Anyone have any ideas , please share.

Have this great box and it wont turn on the lights.

Worked great for a year and was pretty expensive. I am sure it is under warranty, but worried about plants having no light for 4 days...

Few things:

It's getting power.
The green lights on the controller are all working.
Its CLICKING, meaning its trying to tell it to power them ON.
Manual Mode doesn't work either, telling me something inside broke.

All that is new recently is a ceramic 315 Watt light added, but been working fine a few weeks.. so unrelated I think.

Anyone have any ideas?
Or just get the replacement asap and swap it out?
 
Quote Reply

Greeneye04

Posts
263
Reactions
443
Joined
Dec 22, 2012
Points
63
Jun 8, 2015
#2
Check the breaker and make sure both lugs are tight.. I had a similar issue where over time one of the hot wires had come loose in the panel. And I was only getting 120 not 220. Or use a voltage meter to check at power box .
 
Reactions: ivyboy1225, GrowGod and miko
Quote Reply

Greeneye04

Posts
263
Reactions
443
Joined
Dec 22, 2012
Points
63
Jun 8, 2015
#3
Is there still power to the timer? Are there 120 plugs on the box as well? And are they working?
 
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 8, 2015
#4
going to check, breaker was flipped, and this could be the issue. Be back...
 
Reactions: HeLLMuTT and GrowGod
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 8, 2015
#5
Yes. Breaker was Burnt... Fixed..! Thank you..
 
Reactions: burn4me, ivyboy1225, GrowGod and 1 other person
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 8, 2015
#6
Of course.. now I wonder when the breaker burnt... yikes..!
 
Quote Reply

Joe Fresh

Posts
1,036
Reactions
2,291
Joined
Dec 25, 2013
Points
263
Jun 8, 2015
#7
miko said:
Of course.. now I wonder when the breaker burnt... yikes..!
Click to expand...
burnt as in melted? or just loose/no more good?

did you replace it or just adjust it?
 
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 8, 2015
#8
Joe Fresh said:
burnt as in melted? or just loose/no more good?

did you replace it or just adjust it?
Click to expand...

Melted... :(

I replaced but am not sure why it melted.... The wire is 8 gauge, the power box is 50 AMP and so is the breaker...
I am only running 30 AMPS worth of lights.... or so.
 
Quote Reply

Joe Fresh

Posts
1,036
Reactions
2,291
Joined
Dec 25, 2013
Points
263
Jun 8, 2015
#9
miko said:
Melted... :(

I replaced but am not sure why it melted.... The wire is 8 gauge, the power box is 50 AMP and so is the breaker...
I am only running 30 AMPS worth of lights.... or so.
Click to expand...

weird, sounds like faulty breaker...do you have separate breakers for each plug? or just one main breaker? 50 amp breaker should handle 40amps continuous load .... more than that could lead to it eventually melting from heat...sounds like there was some resistance in the breaker for it to melt down, lucky no fire man

i just had mine custom built @ dxhydro, love having it custom, have a separate breaker for each outlet, plus dual voltage/amp meters on each main feed wire...should be comming in the main any day now...i made sure it was over built, that guy kept talking about how powerbox is cheaply built, so i made sure he overbuilt my unit
 
Reactions: miko and oregonmellow
Quote Reply
B

Bangarang

Posts
220
Reactions
109
Joined
Jul 8, 2013
Points
43
Jun 8, 2015
#10
I hate to say it but PowerBox produces some sketchy gear. I replaced my 6 year old CAP 8 light controller with a new Power box to only have the powerbox not even make it a whole year. I have to give them credit on building the boxes out of metal because if that wire would have burnt in plastic it would have been the end of me. Yet why did my wire arc and burn up the whole inside of my Powerbox?
 
Reactions: waayne, Olyver and Joe Fresh
Quote Reply

Olyver

Posts
343
Reactions
237
Joined
Apr 19, 2009
Points
43
Jun 11, 2015
#11
Powerbox is crap, they are not ESA authorized and do not comply with CEC and NEC.
 
Reactions: Joe Fresh and waayne
Quote Reply

Billyboat

Moderator
Posts
970
Reactions
4,037
Joined
Mar 2, 2014
Points
243
Jun 11, 2015
#12
I hate powerbox....

The Titan Helio's work very well for me.
 
Reactions: miko and ivyboy1225
Quote Reply

ivyboy1225

Posts
94
Reactions
85
Joined
Nov 5, 2014
Points
18
Jun 11, 2015
#13
2nd Titan imo.
 
Reactions: miko
Quote Reply

burn4me

Posts
1,779
Reactions
3,715
Joined
Jan 24, 2014
Points
263
Jun 12, 2015
#14

Just in case! I have one mounted right on top of my box
 
Reactions: miko and Joe Fresh
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 12, 2015
#15
Joe Fresh said:
weird, sounds like faulty breaker...do you have separate breakers for each plug? or just one main breaker? 50 amp breaker should handle 40amps continuous load .... more than that could lead to it eventually melting from heat...sounds like there was some resistance in the breaker for it to melt down, lucky no fire man

i just had mine custom built @ dxhydro, love having it custom, have a separate breaker for each outlet, plus dual voltage/amp meters on each main feed wire...should be comming in the main any day now...i made sure it was over built, that guy kept talking about how powerbox is cheaply built, so i made sure he overbuilt my unit
Click to expand...
only using about 30 amps... and the power box and breaker - both 50...
Maybe just a lose wire..
 
Reactions: Greeneye04
Quote Reply

miko

Posts
1,328
Reactions
4,990
Joined
Apr 21, 2014
Points
263
Jun 12, 2015
#16
Just so we aint throwing power box under the bus here..

It wasn't the issue. Its a solid beast of a box and been running great for 2 years.

Just wanted to throw that out there.

The breaker panel was the problem.

Peace~
 
Quote Reply

Greeneye04

Posts
263
Reactions
443
Joined
Dec 22, 2012
Points
63
Jun 12, 2015
#17
I have 5 different powerboxes.. Everyone of them still works.. All are still in use. I have a 6 light..8 yrs old.. 8 light... 2yrs old...10 light 5 years old.., 12 light... 5 years old and their new 24 light. Never had any problems other than a battery going out on the built in timer.. All other problems have ended up being due to a breaker gone bad or a lug coming loose after a few years of use from heat.
 
Quote Reply
B

Bangarang

Posts
220
Reactions
109
Joined
Jul 8, 2013
Points
43
Jun 12, 2015
#18
Greeneye04 said:
I have 5 different powerboxes.. Everyone of them still works.. All are still in use. I have a 6 light..8 yrs old.. 8 light... 2yrs old...10 light 5 years old.., 12 light... 5 years old and their new 24 light. Never had any problems other than a battery going out on the built in timer.. All other problems have ended up being due to a breaker gone bad or a lug coming loose after a few years of use from heat.
Click to expand...
Do you check your lugs inside your Powerbox? One of mine came loose and arched and burnt/melted everything inside.
 
Reactions: G gnome
Quote Reply

G gnome

Posts
20,448
Reactions
84,490
Joined
Feb 26, 2015
Points
638
Jun 12, 2015
#19
Im gonna venture to say one of ur hot legs arched out and melted.
Try to run something else thats 2 phase
 
Quote Reply

xX Kid Twist Xx

Supporter
Premium Member
Posts
3,581
Reactions
2,678
Joined
Mar 10, 2009
Points
263
Jun 12, 2015
#20
i have been using powerbox for about 5 years myself. they will build them anyway requested pretty much. 2 hots and a nuetral as i requested even though it is not code. but the regular ones are up to snuff and have worked great for us, all 4 in differnt spots.
 
Quote Reply
Page 1 of 2 · Replies 1–20 of 22
  • 1
  • 2
Next
1 of 2 Next Last

Thread info

Replies 21
Views 4,479
Started Jun 8, 2015
Latest post Jun 12, 2015
Starter miko
Forum General Indoor Growing

Latest posts

  • I’m Week 4 into Flowering
    • Latest: April14th2014
    • 19 minutes ago
    General Indoor Growing
  • S
    Second grow - trying hydro in coco.
    • Latest: spase
    • 35 minutes ago
    Grow Diaries
  • Eternal Sun 2026 outdoor garden grow
    • Latest: Beazy
    • Today at 12:30 AM
    General Outdoor Growing
  • 40 days into cure , no change in smell or flavor
    • Latest: logic
    • Yesterday at 11:38 PM
    Cannabis Infirmary
  • 2026 Outdoor Grows! let's see em!
    • Latest: EternalSun
    • Yesterday at 11:36 PM
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • General Indoor Growing
  • Help! Powerbox 12000 Light Controller Wont Turn On The Lights Today!!!!
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?