weed farmer.. reread the top post. I wrote you can put another light on that 20 amp two pole.. that means 240v... two pole..
you could even squeeze it on a 120v
and its not any easier wiring 240v vs 120v... just a change of wire color.
AND WEEDFARM WHY THE HECK ARE YOU ASKING A QUESTION LIKE YOU DID WHEN YOU HAVE DESIGNED YOUR AWESOMEEEEEEE MULTII $$$$ PROJECTS.....
Dont bother replying just stay outta my thread..
:very_first_smiley:
You are right, you did say DP, my mistake
I asked because I wanted to be 100% sure of your point when you said it would save on "electrical costs" before I corrected you
This doesnt matter if its a small grow or a large 10K grow.
As others have stated a 1000w ballast could pull 1100 watts. That is 9.16 amps for one ballast or 18.3 amps for 2 ballasts. A 20A breaker at 80% is 16A. At 18.3 amps you are clearly over, and remember the 80% is code. And to be technical even at 1000 watts thats 8.3A or 16.6 amps for two ballasts, still over.
Surely you arent suggesting people ignore a code that is in place to protect people? Growers trying to stay under the radar and mostly growing illegally, surely do not need to be be pushing the limit and exceeding safety standards.
Your argument that a 1000W ballast should only pull 1000W is so weak. It shows your lack of electrical experience or knowledge.
You aren't telling people, hey you are a tad over, you may be OK, make your own decision You are just telling them its fine, when clearly its not
You started a thread, telling people you will give them advice. It is clear you do not have the knowledge or experience. You want to tell people they can piss on their plants or spray kool-aid on the leaves, fine (not that you have). But giving bad electrical advice could land someone in jail or dead. I will not stand by and allow that.
Ok let me clarify something.... running 240v with a/c, h.d. pumps will save you money vs 120v. I am checking on the ballast comsuption of power to see if it matters. peace
Let ME clarify. No it will not. Larger devices are run on 240 due to the power needed to run them. OHMS law buddy. A 240V device running 15Amps would require 30A on 120, larger wire, etc would be required.
Running 240 allows you to run more devices on a given wire size, less wire to install, less labor, etc.
And you need to check on ballast consumption?? 20 years experience and you cant