I am preparing for a 20x20' space and plan on using 16 LED units that are about 1100 watts each. I am new to indoor growing and I am pretty inept with in electrical so what I am going to ask will probably sound stupid.

What is the proper way to power these lights?

Is it OK to have a dedicated 20 amp breaker for each individual light and timer with the remaining load to power ancillary equipment (fans, filters, etc)?
 
Reactions: Powerstroke, cannafarmer420, HighVoltageSparky and 1 other person
Quote Reply

GNick55

Staff
Supporter
Posts
15,379
Reactions
49,214
Joined
Jan 11, 2020
Points
438
Jun 28, 2023
#2
Durio_OG said:
I am preparing for a 20x20' space and plan on using 16 LED units that are about 1100 watts each. I am new to indoor growing and I am pretty inept with in electrical so what I am going to ask will probably sound stupid.

What is the proper way to power these lights?

Is it OK to have a dedicated 20 amp breaker for each individual light and timer with the remaining load to power ancillary equipment (fans, filters, etc)?
Click to expand...

someone will chime in to help you out..
 
Reactions: cannafarmer420 and Mikedin
Quote Reply

Deadstill

Supporter
Have Dick, Will Travel
Posts
2,777
Reactions
8,080
Joined
Oct 28, 2018
Points
263
Jun 28, 2023
#3
Durio_OG said:
I am preparing for a 20x20' space and plan on using 16 LED units that are about 1100 watts each. I am new to indoor growing and I am pretty inept with in electrical so what I am going to ask will probably sound stupid.

What is the proper way to power these lights?

Is it OK to have a dedicated 20 amp breaker for each individual light and timer with the remaining load to power ancillary equipment (fans, filters, etc)?
Click to expand...

Howdy, and welcome to the Farm!

First of all, are these lights actually drawing 1100 watts? Usually they say something like "1200 watt LED light" but what they actually mean is "equivalent to standard 1200 watt light" - and generally these lights only draw somewhere between 80-100 watts, actual power usage..

I could be wrong, and it has been a long time since I've purchased any LED lights, but this is generally the case. An LED light that actually draws 1100 watts sounds like it would be incredibly powerful.

As far as circuit breakers go, most people don't know this, but they only exist for 1 reason and 1 reason alone. To protect the wiring in your walls from getting too hot and starting a fire, and nothing more.

I've run about 13 or 14 of Mars Hydro's older blurple "1000 watt equivalent LEDs" off of one single 20 amp breaker without any trips.

Perhaps someone with a little more electrical savvy will chime in, but I think you'll be alright.
 
Reactions: wadesweeds, Sunasun and GNick55
Quote Reply

Dub_City405

Posts
919
Reactions
1,211
Joined
Jan 7, 2021
Points
143
Jun 28, 2023
#4
No he does not run 14 lights off 1 breaker with his high ass. Unless the 1 break is connect with a 120 Amp breaker.

Get a control box. That is in the room you can plug all the lights into. Then just run the control box to your breaker. Make sure you have open slots in your breaker box first. It's gonna be based on your Amp usage not your watts.
 
Last edited: Jun 28, 2023
Reactions: Ezdeezy89, cannafarmer420, HighVoltageSparky and 1 other person
Quote Reply

Sunasun

Posts
550
Reactions
986
Joined
Mar 4, 2022
Points
93
Jun 28, 2023
#5
20 amps x 120 volts = 2400 watts. 16 lights @ 100 watts a piece would be 1600 watts. Should be doable.
 
Reactions: wadesweeds, Madbud, GNick55 and 1 other person
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#6
Check actual consumption on lights. 16 lights X 1,1KW = 17 KW.
This is a ridiculous amount of energy. You running first grow in a automated building? :: = )

Also, note that LED has high start energy, surgy energy or whatever. Meaning, lets say your fuse is 10 Amps.
Also, LED lights will pull nominal watts times TEN. in surge energy

1100 watts one light - Amps = Watts/voltage - 1100/230 = 4,78 Amps
Wow, so with one light, we're pulling half of what one 10A MCB should be able to handle, and also 4,78 X 10surge factor = 47 Amps the first milliseconds. Which is fine, but when you plug more lights, this surge energy will buiild and build, and the fuse will trip, not because you have too many amps on the fuse, but the surge energy is making the fuse trip.
I could go in to how o calculate if the surge energy will trip the fuse or not, but i've written too much already

Aaallll of this to say, check the marking on your equipment, this will tell you how much watts your stuff pulls, then it's easy to calculate how many lights per mcb, and also misc equipment.

Me personally, i have one fuse for two lights 5 Amps on a 16A fuse, plus extra stuff, but i also have a redundancy. Meaning dobbel of everything. One tripped fused will not screw you over.

I used to have trouble with the monkey fans shortcircuit, and trip my whole damn apartment!!
 
Reactions: brad2007
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#7
Sunasun said:
20 amps x 120 volts = 2400 watts. 16 lights @ 100 watts a piece would be 1600 watts. Should be doable.
Click to expand...
Ah yes, also the equation looks different if you're an American/Canadian, using your weak split winding 110 V
 
Reactions: brad2007, GNick55 and Sunasun
Quote Reply
I

imgrowing

Posts
450
Reactions
1,062
Joined
Jun 5, 2023
Points
143
Jun 28, 2023
#8
how many amps do those lights draw?
 
Reactions: GNick55 and Sunasun
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#9
Deadstill said:
Howdy, and welcome to the Farm!

First of all, are these lights actually drawing 1100 watts? Usually they say something like "1200 watt LED light" but what they actually mean is "equivalent to standard 1200 watt light" - and generally these lights only draw somewhere between 80-100 watts, actual power usage..

I could be wrong, and it has been a long time since I've purchased any LED lights, but this is generally the case. An LED light that actually draws 1100 watts sounds like it would be incredibly powerful.

As far as circuit breakers go, most people don't know this, but they only exist for 1 reason and 1 reason alone. To protect the wiring in your walls from getting too hot and starting a fire, and nothing more.

I've run about 13 or 14 of Mars Hydro's older blurple "1000 watt equivalent LEDs" off of one single 20 amp breaker without any trips.

Perhaps someone with a little more electrical savvy will chime in, but I think you'll be alright.
Click to expand...
"As far as circuit breakers go, most people don't know this, but they only exist for 1 reason and 1 reason alone. To protect the wiring in your walls from getting too hot and starting a fire, and nothing more."

This is as accurate as you can get buddy boy. Good job mate, i've worked with sparkies who never cared to learn this very fundamental fact. You must have some voltage inside you somewhere : = )

All there is to do is segregate the lights evenly on some MCB's, connecting everything to one fuse is... Risky. If everything ends well, great.
However, it is "bad" form to adhere to this philosophy. Try to think about, if one thing fails, do i still have a barrier to protect plants / humans?

This is assuming this gentleman has a solid fusebox. Just waiting for the man to send over pictures, or at least respond? : = )


And whoever came up with 1000Watt HPS equivalent LED 100 Watts needs a damn good thrashing.
 
Reactions: BillyBanchan, GNick55, Sunasun and 1 other person
Quote Reply

Deadstill

Supporter
Have Dick, Will Travel
Posts
2,777
Reactions
8,080
Joined
Oct 28, 2018
Points
263
Jun 28, 2023
#10
HighVoltageSparky said:
"As far as circuit breakers go, most people don't know this, but they only exist for 1 reason and 1 reason alone. To protect the wiring in your walls from getting too hot and starting a fire, and nothing more."

This is as accurate as you can get buddy boy. Good job mate, i've worked with sparkies who never cared to learn this very fundamental fact. You must have some voltage inside you somewhere : = )

All there is to do is segregate the lights evenly on some MCB's, connecting everything to one fuse is... Risky. If everything ends well, great.
However, it is "bad" form to adhere to this philosophy. Try to think about, if one thing fails, do i still have a barrier to protect plants / humans?

This is assuming this gentleman has a solid fusebox. Just waiting for the man to send over pictures, or at least respond? : = )


And whoever came up with 1000Watt HPS equivalent LED 100 Watts needs a damn good thrashing.
Click to expand...
Yeah I used to deal a lot with electrical when I was an automotive tech, but I haven't messed with it much in a long time, and as they say, use it or lose it.

I could be wrong on the actual number of lights I ran off of 1 20 amp breaker, it's been a few years, but the lights I had did not use very much power at all. Yeah, they advertise as 1000w equivalent but they're nowhere near that in actual power usage.

It's like when you go to Walmart and all the lightbulbs, on the box, say for example, "75 watt" in big letters, and then below that it says something like "11 watts used"

To the OP - If you can't find the actual energy used on the lights themselves or the box they came in, I highly recommend you get a meter, similar to this one - https://www.amazon.com/VIVOSUN-Cons...60&sprefix=energy+usage+meter,aps,169&sr=8-13
plug one of your lights into it, and find out. But I highly doubt for your setup a 20 amp breaker per light, will be necessary. If you were running MH/HPS, yes, but not with LEDs.
 
Reactions: Sunasun, GNick55 and HighVoltageSparky
Quote Reply

Mikedin

Living Soil Student
Posts
12,345
Reactions
54,843
Joined
Apr 13, 2022
Points
438
Jun 28, 2023
#11
I’m assuming he’s taking about true 1,000w bar style lights not the 100w “1,000w equivelent” lights

Need light specs
 
Reactions: BillyBanchan, brad2007, Sunasun and 2 others
Quote Reply

Deadstill

Supporter
Have Dick, Will Travel
Posts
2,777
Reactions
8,080
Joined
Oct 28, 2018
Points
263
Jun 28, 2023
#12
Mikedin said:
I’m assuming he’s taking about true 1,000w bar style lights not the 100w “1,000w equivelent” lights

Need light specs
Click to expand...
Yeah, see I haven't had the opportunity to use one of those bar style lights yet. I'm glad the LED grow light industry is making good progress, though! The 1000w equiv. lights don't put out nearly the same PAR as a 1,000w MH/HPS, especially the double enders.

I think a lot of people buy lights from Amazon thinking they got some "great deal" on an LED light only to find out they're 2 steps above a candle
 
Reactions: brad2007, Mikedin and HighVoltageSparky
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#13
Deadstill said:
Yeah, see I haven't had the opportunity to use one of those bar style lights yet. I'm glad the LED grow light industry is making good progress, though! The 1000w equiv. lights don't put out nearly the same PAR as a 1,000w MH/HPS, especially the double enders.

I think a lot of people buy lights from Amazon thinking they got some "great deal" on an LED light only to find out they're 2 steps above a candle
Click to expand...
Bro, it should be illegal. Thankfully they're dirt cheap, and doesn't need more dillydally to hook up.

If the thread guy could only give us info on the lights and perhaps his fusebox : - (
 
Reactions: Deadstill
Quote Reply

GNick55

Staff
Supporter
Posts
15,379
Reactions
49,214
Joined
Jan 11, 2020
Points
438
Jun 28, 2023
#14
Deadstill said:
Yeah, see I haven't had the opportunity to use one of those bar style lights yet. I'm glad the LED grow light industry is making good progress, though! The 1000w equiv. lights don't put out nearly the same PAR as a 1,000w MH/HPS, especially the double enders.

I think a lot of people buy lights from Amazon thinking they got some "great deal" on an LED light only to find out they're 2 steps above a candle
Click to expand...
first of all nothing of any quality is available on amazon..
not a single item i have for growing is from amazon..
 
Quote Reply

Mikedin

Living Soil Student
Posts
12,345
Reactions
54,843
Joined
Apr 13, 2022
Points
438
Jun 28, 2023
#15
Deadstill said:
Yeah, see I haven't had the opportunity to use one of those bar style lights yet. I'm glad the LED grow light industry is making good progress, though! The 1000w equiv. lights don't put out nearly the same PAR as a 1,000w MH/HPS, especially the double enders.

I think a lot of people buy lights from Amazon thinking they got some "great deal" on an LED light only to find out they're 2 steps above a candle
Click to expand...
Haha yeah I have 2 of those they can put out a decent harvest but nothing comparable to the bar styles like the
Spiderfarmer G1000

Link isint working but this light for example
 

Attachments

  • IMG_6190.png
    91.3 KB · Views: 13
Reactions: brad2007 and Deadstill
Quote Reply

Deadstill

Supporter
Have Dick, Will Travel
Posts
2,777
Reactions
8,080
Joined
Oct 28, 2018
Points
263
Jun 28, 2023
#16
Mikedin said:
Haha yeah I have 2 of those they can put out a decent harvest but nothing comparable to the bar styles like the
SPIDER FARMER G1000W LED Grow Lights for 4x4ft/5x5ft Coverage Full Spectrum Dimmable Daisy Chain 1000W Commercial LED Growing Lamp Bar Style 2.9 umol/J Vertical Farming Co2 https://a.co/d/8Dk8nHZ
Click to expand...
Right on, I may have to invest in a few of these eventually. I've mostly switched to outdoor growing, now, since I switched my focus to industrial hemp, the only indoor growing I do now is to start seedlings. Also being mostly OTG (off-the-grid) running a grow room 24/7/365 isn't ideal.
 
Reactions: Mikedin and GNick55
Quote Reply

Oldchucky

Supporter
Posts
14,482
Reactions
48,871
Joined
May 4, 2021
Points
438
Jun 28, 2023
#17
Hire a licensed electrician!
 
Reactions: wadesweeds, Sunasun, Mikedin and 3 others
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#18
Well, i wrote down some numbers for OP, for he when gets back.

If we assume one light is really 1100Watts, that's 10A per light @110V.

However, putting two lights, 20A, on a 20A MCB is bad form. You don't want to pull more than 80-85% of the rated amperage on the fuse. Hypothetically, you would be pulling max amps out of that poor MCB. That assumes you're pulling max (Watts) on both fixtures. This, the grower could adjust himself, lower the lights, dim the power to get a more sensible power pull via the MCB. Around 16A.

And I haven't even gotten to the startcurrent from two lights, assumes 80-100 times nominal amperages, we're looking at 180-200A startcurrent (Max power from lights)
A standard 20A breaker (Characteristic C) has a limit of what amperages it will let through(in a set amount of time) before tripping. For startcurrent this is called I4 value.

Characteristic C breakers should hold rated I nominel X 5 = 100A
Actually, it could be 5-10 times rated Amps, this is MCB specific.

Plain as day, two lights 20A equal ish to 200 A startcurrent <100A I4 equation not satisfied.
You could dim the lights, yeah, but this is a napkin calculation what you need, or not need to think about. Only one, MAYBE two lights, which you make sure of that you don't pull more what is "safe"

OP has to come back to us, what fuses, amperage, info on lights, need specs and everything.
 
Reactions: Dub_City405
Quote Reply

GuySmiley

Posts
170
Reactions
304
Joined
Nov 30, 2020
Points
63
Jun 28, 2023
#19
What person that is "..new to indoor growing" starts off with a 20' x 20' grow room and 16 lights?
 
Reactions: Sunasun, F.Dupp and HighVoltageSparky
Quote Reply

HighVoltageSparky

Posts
30
Reactions
44
Joined
Dec 27, 2022
Points
18
Jun 28, 2023
#20
GuySmiley said:
What person that is "..new to indoor growing" starts off with a 20' x 20' grow room and 16 lights?
Click to expand...
Go big or go home? The guy seems to have some green fingers, maybe he trives on the challenge?

If so, I can respect that
 
Reactions: Sunasun, Boo1965, 1diesel1 and 1 other person
Quote Reply
Page 1 of 4 · Replies 1–20 of 77
  • 1
  • 2
  • 3
  • 4
Next
1 of 4 Next Last

Thread info

Replies 76
Views 7,270
Started Jun 28, 2023
Latest post Jun 30, 2023
Starter Durio_OG
Forum Growroom Design & Setup

Latest posts

  • D
    Help, i thought i was over watering but not sure
    • Latest: dr.thumbgreen
    • 1 minute ago
    Basic Growing Information
  • C
    420Captain first grow. How are they doing ?
    • Latest: crystoffer
    • 26 minutes ago
    Grow Diaries
  • Big Al’s 2025 season indoor/outdoor grow in misery
    • Latest: Leste
    • 40 minutes ago
    Grow Diaries
  • Virginia Growers Thread - Everything VA
    • Latest: IgnorRayMuss
    • 44 minutes ago
    Basic Growing Information
  • 2026 Outdoor Grows! let's see em!
    • Latest: SeedSupreme
    • 55 minutes ago
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Please help - electrical question
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?