Hey I'm wondering what the pro's recommend for electric contactors... 4 pole 20 amp. Thanks
 
Olyver

Olyver

343
43
There are few factors to consider when purchasing a contactor. How many ballast(s) do you want to power. The most important factor is don't be cheap and buy the same ones that CAP, Powerbox, DXHydro, Sunlight Supply, EZ-Box, etc, use. They purchase cheap no-name contactors that will probably have a loud hum when the coil is energized. Stick with brand names like SIEMENS, ABB, OMRON, Potter-Brumfeld, etc.

To be safe, double the FLA of the contactor, if you have 20A @ 240V, then use a 40A contactor.
 
chrometrichs

chrometrichs

390
18
Thanks olyver, my electrician needs to replace the ones he used originally, they hum pretty bad.
 
hiboy

hiboy

2,347
113
Your circuits determines how many poles , so the more breakers you want activated the more poles you need.
I would always overrate your contactor amperage, your breaker will trip on an overdraw. Why push your 20 amp contactor.
30 amp minimum on each pole. Also use a lighting contactor, not just a regular relay.