Im running a wire from my one room to fuse box. The lights can be powered by 120v or 240v by simply changing the powercord. My equipment is 3 1000 watt Quantum Ballasts. The equipment will run for about 12hrs a day. My question is with the formula. Since im going with a 240v will it bring the total amps to 12.5 cause of the formula 3000w/240v = 12.5amps. and then my 240v 30 amp breaker will be fine or do i have to go with 240v 8/2 gauge wire 40 amp breaker. thank you so much for your time and input. also is my wiring right? 10/2 for 240v 30amp breaker.
8/2 for 240v 40 amp breaker.
or do i have to run 10/3 or 8/3 for these lights.
 
10/2 and a 30 amp breaker will work fine for 3 1000 watt lights run on 240v.

You would use 10/3 only if you need 120v circuits also.
 
wouldnt it be safer to do 10/3 and better in the long run
 
Thanks for your response. Im getting mixed answers but i think im gonna go with the 10/2 30amp double breaker 240v. im not sure the difference in running 10/2 or 10/3.
 
i did some reading cause Ive been told 240v needs a 3 wire, so you can do 10/2 your black and white are hot then the the copper is your ground and neutral, but new laws have made it where you do a 240 you need a 3 wire, it up to you but electric is something you don't go cheap on or do it halfass......
 
To meet code you have to run 10/3 - the extra ground is nice, also, I always run GFI - just in case.. I've been zapped by 110vac at least 30 or 40 times, and it's not a big deal (not that I would do it for fun), but twice got zapped by 220vac and fuck.. not cool.

I use 40 or 60amp 'hot tub' GFI boxes, they run around 100 bucks at home depot, the one I'm using currently has a 60amp 220 GFI and came with a 15 amp 120vac breaker and room to add a second.
 
Not sure about quantum but Lumatek says not too hook up a neutral when using there ballasts in 240v. So u can use 10/2 in that case
 
I am not sure why you would use 10/3 for a 240 line. What do you do with the extra ground/neutral wire? Connect it to the ground/neutral bar? What do you connect the other end of the wire to?
 
A 10/2 is two conductors and a bare ground wire. A 10/3 is two "hot" conductors, 1-grounded conductor(white) and one bare ground wire. If you use the bare wire in a 10/2for a neutral you are running voltage through it to ground-not cool. If you run a 10/3 you can install a small sub panel in your grow area and run both 240 and 120 volt circuits on separate breakers but the white wires need to land on a neutral bar that is isolated from the ground. If you are only running a 240 volt circuit just use the 10/2-no neutral is needed.
 
This is what I have going on for my panel. Also 240v. I hope its clear enough to see. I'm not an electrical dude but I hope this helps you with reference.

-p3
 

Attachments

  • IMG_0067.JPG
    IMG_0067.JPG
    109.7 KB · Views: 1,923
I thought the minimum to run 15 amp draw would be a 12/3 wire. 10/3 makes more sense for the overhead, but the code minimum would be 12/3.

FWIW, you can also down-rate your neutrals too, but this depends on local code.
 
240V breaker & wire size

hi y'all
what would y'all say about hooking up a quantum 1000 on a 100A main panel running on 240V , what wire size would i need & a breaker, the panel is around 40' feet away
a 20A 2 pole breaker & 12-2 or 12-3 am i close
 
hi y'all
what would y'all say about hooking up a quantum 1000 on a 100A main panel running on 240V , what wire size would i need & a breaker, the panel is around 40' feet away
a 20A 2 pole breaker & 12-2 or 12-3 am i close



there are some variables and different ways to do this.

On 240 that ballast is drawing less than 5 amps. You will need a double pole breaker, and the appropriate sized wire. a 20A breaker and 12/2 wire will work.

this will allow you to run a dedicated outlet for the ballast
 
this is it: 10/3 not needed. what would u use that extra red wire for>? 3 x 1000 = 3000 watts divided by 230 not 240 is under 14 amps. you could run 12/2 since thats capable of handling that load. 10/2= black wire to breaker, white wire to breaker, copper grnd to grounding buss panel.
 
looking at your picture with the panel. I"ld take that black and red and put it in a breaker.. back feeding the panel and then you have means to kill all power right there. Safer... and sometimes you might need a quick shut offf. whatever breaker is at your main feeding the sub panel is the same size you should use in the sub
10 guage is 30 amp. 8 guage is 40 amp and 6 guage is 50...
 