i have a 100 amp main breaker thats full..... what size subpanel should i buy from homedepot?

sub panel will need to be able to handle

3k hps
25k btu ac
70 pint dehunidifier
and misc other things

a link would helpful as im also willing to order online...

thanks in advance...
 
If your main is full where will you put the breaker for the subpanel?100A panel may not support the homes use +a subpanel big enough to run what you want.3-1ks=approx 12-14 amps @240v,25k AC=20-25A approx.@240v,70 pint dehuey approx 7-8A@120v,take into account a 20% safety factor and you need approx. 50A just to run all your grow equipment.
 
If your main is full where will you put the breaker for the subpanel?100A panel may not support the homes use +a subpanel big enough to run what you want.3-1ks=approx 12-14 amps @240v,25k AC=20-25A approx.@240v,70 pint dehuey approx 7-8A@120v,take into account a 20% safety factor and you need approx. 50A just to run all your grow equipment.



by removing 2 of the 15A breakers that goes to to the flower room . these breakers/outletd are old and i figure i can remove these 2 , so i can add a double pole breaker/sub panel that will be able to handle everything ...
 