I might be able to manage a 25 light flip flop on a 200 amp would need to be tested obviously and not for medical as were at 86% of the 80% rule
basically figured what would be running at any given time not including heating as dehumidifiers do generate quite a bit, my climate would not need an ac basically just a shutdown during the warm months which is fine by me.
- Unsealed -
Flower 25x1000w = 104.2 amps
Veg 10x1000w = 41.7 amps
Veg 14" maxfan 1700 cfm 2x for cooling = 2.1 amps each
= 4.2 amps
Flower 16" maxfan 2436 cfm 4x for cooling each room = 1.5 amps each @ 240v
= 6 amps
Flower 14" maxfan 1700 cfm for odor during lights out = 2x 2.1 amps for each room
= 4.2 amps
Flower 2x Sante Fe Classic Dehumidifers 6.4 amps each and 2 in each room running during night cycle.
= 12.8 amps
173.1 amps total