lol scratch that..that's late night math. It's closer to 8 fixtures with 15 amp receptacles to be safe..but if these were pig-tailed that number could abide by the breaker/wire. Which is closer to 11 fixtures. Under-rated wire is more likely to fail a circuit before an undersized plug..but that is the question. "can a 15 amp 240v receptacle handle 20 amps of draw being daisy-chained?" If they were 120v the neutrals would be shared is the big difference.According to my math..your 15 amp circuit (15 amp plugs) can handle a total of roughly 10 fixtures. The 12 gauge wire is fine as long as the run of all wires doesn't exceed 50 feet total or you will suffer a voltage drop. Your weakest point in the whole system is the 15 amp receptacles..the wire and breaker are fine if under 5o feet total. So you must abide by the limit of your receptacles.
looks good with what you have for power draw,even f they all fired up at the same time .I've been digging around Mike Holt's site and I haven't found a definitive answer. The NEC isn't written for a 240V household. The critical factor is the through-current capacity of the receptacles but I haven't found a spec from the manufacturers.
I'm probably jaded from working with industrial 440V 3-phase but I don't see great hazard moving from 120 to 240VAC.
The actual load on my circuit could be (4 x 330W) + (5 x 325W) + (4 x 165W) = 3605W
3840W is the 80%
In other words..actual amp readings vs wattage rating? If so it makes sense, since most ballast powered lighting has high ramp-up loads..we're talking 30%-40% sometimes at peak for old magnetic types.The NEC notes that for lights using a ballast, loads should be calculated using the specified current, not power.
Natural, I hope you are not suggesting leaving a Kill-a-Watt plugged in. The instructions specifically forbid it and I've seen stoner photos of the results from not reading.
A specific example of a luminaire with ballast (driver) is Lumigrow Pro 325. The advertised and measured power is 325W. The sticker next to the IEC receptacle says 5 / 2.5 amps depending on 120V or 240V. That equals 600VA.
A Mike Holt forum post had an electrician working in Saudi Arabia where the household standard is 240V but they were contracted to work per the NEC. The concensus was that this is absurd, the NEC doesn't allow for 240V to replace 120V in a dwelling. The electrician had his superiors redefine the specifications. Someone in the Phillipines said their code modified NEC to allow 240V as the normal voltage in a dwelling.
Yeah what I'm setting up is just like @seaslug for the most part. I don't think I'm daisy chaining them though. There's a different 12awg cable running to each receptacle. Maybe it is daisy chaining. Not quite up to speed on the terminology. I pretty much made a light timer out of two intermatic timers and 8 duplex 240v receptacles and one single one. 5 on one circuit, 4 on the other. Took account for the continuous load. I was just over 80% so I made two circuits with two timers instead of all on one. It was still way cheaper than getting a timer but took a couple weeks worth of r & d to be comfortable enough to do it lol. Y'all answered my final question (hopefully), now it's time to finish putting up the show. It's been a Long time coming.
So reading through this thread again I'm second guessing something. If I have the circuit running through a 40a intermatic timer to the receptacles, do I have them on a breaker that equals the total load the circuit will be carrying (just under 30a) or a 15a breaker to match the receptacles?
Do you recommend pigtailing 120V receptacles?15 amp plugs no problem on 20 amp circuit.
No problem Daisy chaining 240 v outlets just don't exceed the draw of 16 amps. Definitely pigtail them.
Hb
Always. Takes the load off the outlet .Do you recommend pigtailing 120V receptacles?