Hey Farmers,
I need some advise on my panel and upgrades I'm considering.
I just rented a 1000 sq foot shop that has a 125amp, 120v/208v AC 4wire,
3 phase panel. I'm planning on running a sentinel HPH-8 light controller rated at 50amps. My question is to be safe I'm only running the main panel at 100amps and plan to run my ballast at 240v and all the other equipment on 120v (a/c, veg tent, etc.) The hph-8 has a 50 amp breaker but If I install it on say leg "A" of my 3 phase panel is that overloading the "A" LEG? Is the panel divided into 3 legs meaning each phase is 33.3 amps each? (My GE-panel reads : Delta phase "B" power leg DO NOT INSTALL 120v or 120/240v circuit breakers in phase leg "B" 208v to ground potential circuits marked in parenthesis. Ad rating 240v 3 phase 3wire for this system neutral is not used & only breakers rated at 240v AC are to be used.) Also I had an electrician buddy of mine do a quick check on the panel and he didn't get any power reading on leg "A"? Does this mean that leg "A" is fried and needs to be replaced? I have added every piece of equipment that will be installed and my total will be 96.8 amps total setup. So I am still under the 100amp max, what is the best way to help spread out power consumption so all will be well?
Thank you GUYS I have been reading on the farm for the last 2 days before I posted so I didn't want to ask a lazy question when the answer was already out there. Thanks all.... ( Sorry I originally posted this in infirmary section then realized all electrician questions were here. Sorry mods.)
I need some advise on my panel and upgrades I'm considering.
I just rented a 1000 sq foot shop that has a 125amp, 120v/208v AC 4wire,
3 phase panel. I'm planning on running a sentinel HPH-8 light controller rated at 50amps. My question is to be safe I'm only running the main panel at 100amps and plan to run my ballast at 240v and all the other equipment on 120v (a/c, veg tent, etc.) The hph-8 has a 50 amp breaker but If I install it on say leg "A" of my 3 phase panel is that overloading the "A" LEG? Is the panel divided into 3 legs meaning each phase is 33.3 amps each? (My GE-panel reads : Delta phase "B" power leg DO NOT INSTALL 120v or 120/240v circuit breakers in phase leg "B" 208v to ground potential circuits marked in parenthesis. Ad rating 240v 3 phase 3wire for this system neutral is not used & only breakers rated at 240v AC are to be used.) Also I had an electrician buddy of mine do a quick check on the panel and he didn't get any power reading on leg "A"? Does this mean that leg "A" is fried and needs to be replaced? I have added every piece of equipment that will be installed and my total will be 96.8 amps total setup. So I am still under the 100amp max, what is the best way to help spread out power consumption so all will be well?
Thank you GUYS I have been reading on the farm for the last 2 days before I posted so I didn't want to ask a lazy question when the answer was already out there. Thanks all.... ( Sorry I originally posted this in infirmary section then realized all electrician questions were here. Sorry mods.)