fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Feb 18, 2016
#1,701
John do you use any surge protection when you install?And if you use a shorter lineset say 10'-15' are you good to go with the pre charge in the unit or do you have to weigh some out for the shorter lineset?Thanks.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 19, 2016
#1,702
fishwhistle said:
John do you use any surge protection when you install?And if you use a shorter lineset say 10'-15' are you good to go with the pre charge in the unit or do you have to weigh some out for the shorter lineset?Thanks.
Click to expand...

I don't use any surge protection. No u don't have to remove any
 
Reactions: fishwhistle
Quote Reply

Goodolboy

Posts
51
Reactions
60
Joined
Feb 22, 2015
Points
18
Feb 19, 2016
#1,703
I want to make my central ac cool my room which is located in my garage which so is also where the blower unit for the ac is. So do I just redirect the return which I'm assuming is the top duct into my garage and then redirect the out put cold air which I assume is the bottom insulated duct into the same room "the garage " ? And then re wire the thermostat into the garage ? Thanks so much for any help as I do not wish to call an hvac guy to my house. Here's a picture of the unit
 

Attachments

  • IMG_20160218_200018444.jpg
    73.3 KB · Views: 242
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 20, 2016
#1,704
Goodolboy said:
I want to make my central ac cool my room which is located in my garage which so is also where the blower unit for the ac is. So do I just redirect the return which I'm assuming is the top duct into my garage and then redirect the out put cold air which I assume is the bottom insulated duct into the same room "the garage " ? And then re wire the thermostat into the garage ? Thanks so much for any help as I do not wish to call an hvac guy to my house. Here's a picture of the unit
Click to expand...

Are u sure that unit runs? My guess is if you use it for your grow it will die probably quickly. You have to relocate stat to garage and disconnect ducts to the house or you'll freeze them out.
 
Reactions: fishwhistle
Quote Reply

Goodolboy

Posts
51
Reactions
60
Joined
Feb 22, 2015
Points
18
Feb 21, 2016
#1,705
Yea I've ran her she's good to go. The unit is in the garage. So that's all I have to do is re route the two ducts and the thermostat and I'm good to go Cannabis John ? Thanks for your help.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 21, 2016
#1,706
Goodolboy said:
Yea I've ran her she's good to go. The unit is in the garage. So that's all I have to do is re route the two ducts and the thermostat and I'm good to go Cannabis John ? Thanks for your help.
Click to expand...

I didn't say it wouldn't run. I said it won't run long. Be prepared it will break soon. Plus how is it sized compared to what you need? If it's too big it will turn on and off a lot causing it to fail sooner. If it's too small it won't do the job. It'll tun all the time and still not cool. Get a pro to check it out or better yet put in a unit sized properly for grow.
 
Quote Reply

Goodolboy

Posts
51
Reactions
60
Joined
Feb 22, 2015
Points
18
Feb 21, 2016
#1,707
What size unit would you recommend for a 19 thousand watt room ?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 22, 2016
#1,708
Goodolboy said:
What size unit would you recommend for a 19 thousand watt room ?
Click to expand...

10 tons of cooling. Use 2 or more units to make 10 tons (2-5 tons works great)
 
Quote Reply

Goodolboy

Posts
51
Reactions
60
Joined
Feb 22, 2015
Points
18
Feb 23, 2016
#1,709
Awesome thanks c john for your help.
 
Quote Reply

windshear13

Posts
12
Reactions
2
Joined
Oct 20, 2015
Points
3
Feb 24, 2016
#1,710
Hi John.

I have spent a lot of time redesigning my 47' x 25' flower room and I have come up with the following design:

28 x 1000 watt Gavita DE
4 x Quest 155 Dehumidifiers
2 x 10 burner CO2 units

Will 10 tons of cooling be enough? I am looking at 5 ton conventional split units on NationalAirWarehouse.com. I'm looking at both Rheem and Trane. I have an authorized installer who will do the install work for me.

I would like to take a page out of the Excel Air handbook and have a supply plenum built for the top of the air handlers output that has a round flange which I could use to directly connect 45' of fabric ducting to try and evenly distribute the air throughout the room.

In your opinion will this configuration work? How do you feel about Rheem and Trane, and are there any general recommendations you would have for me in this situation?

I am also in Alaska, and it is typically ranges between 37 and 50 here through the winter, with occasional dips as low as 10. It rains a lot here as well. Will this need to be considered when selecting a unit?

Thank you so much for your help in these matters. We all appreciate it so much.
 
Last edited: Feb 24, 2016
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 25, 2016
#1,711
windshear13 said:
Hi John.

I have spent a lot of time redesigning my 47' x 25' flower room and I have come up with the following design:

28 x 1000 watt Gavita DE
4 x Quest 155 Dehumidifiers
2 x 10 burner CO2 units

Will 10 tons of cooling be enough? I am looking at 5 ton conventional split units on NationalAirWarehouse.com. I'm looking at both Rheem and Trane. I have an authorized installer who will do the install work for me.

I would like to take a page out of the Excel Air handbook and have a supply plenum built for the top of the air handlers output that has a round flange which I could use to directly connect 45' of fabric ducting to try and evenly distribute the air throughout the room.

In your opinion will this configuration work? How do you feel about Rheem and Trane, and are there any general recommendations you would have for me in this situation?

I am also in Alaska, and it is typically ranges between 37 and 50 here through the winter, with occasional dips as low as 10. It rains a lot here as well. Will this need to be considered when selecting a unit?

Thank you so much for your help in these matters. We all appreciate it so much.
Click to expand...

IMO 10 tons isn't enough. I recommend 14 tons for 28 lights. You'll need to add some type of low temperture operations switch or component for outside unit to produce a/c when temp outside is below manufactures recommendations. It's called low ambient ops. Don't neccesarily need duct work on units. I would hang air handlers from ceiling across narrow width of room evenly spaced apart blowing down length of room (47 foot dimension). The units should be 2-3 ft from wall where air is entering them. The amt of air they move in that relatively small space doesn't really require duct to properly distribute it. Trane is good but pricy. Rheem is ok
 
Reactions: windshear13
Quote Reply

windshear13

Posts
12
Reactions
2
Joined
Oct 20, 2015
Points
3
Feb 25, 2016
#1,712
Thanks for the great advice. You recommended York to me before, but my AC guy doesn't service them. Carrier is another option. How do you feel about carrier compared to the other 2?
 
Quote Reply

windshear13

Posts
12
Reactions
2
Joined
Oct 20, 2015
Points
3
Feb 25, 2016
#1,713
Also, would you consider 3 conventional splits as the best way to provide this level of cooling? Or is there a better option when you get into this range?

And you would place the 3 air handlers so they are all blowing the same direction, correct?

Thanks again.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 25, 2016
#1,714
windshear13 said:
Thanks for the great advice. You recommended York to me before, but my AC guy doesn't service them. Carrier is another option. How do you feel about carrier compared to the other 2?
Click to expand...

Carrier and Trane are similar.
 
Reactions: windshear13
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Feb 25, 2016
#1,715
windshear13 said:
Also, would you consider 3 conventional splits as the best way to provide this level of cooling? Or is there a better option when you get into this range?

And you would place the 3 air handlers so they are all blowing the same direction, correct?

Thanks again.
Click to expand...

Do 3 conventional splits. Easy install and multiple units help cause if one breaks done you still have 2 to run ur room at partial lights.
All 3 air handlers blow in same direction.
 
Reactions: windshear13
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Mar 6, 2016
#1,716
john check your PMs when you see this,thanks.
 
Quote Reply

windshear13

Posts
12
Reactions
2
Joined
Oct 20, 2015
Points
3
Mar 10, 2016
#1,717
Hi John. I have a follow up question regarding our veg area. We will be using 24 X 8 bulb t5's and 5 X 600 watt MH in parabolic reflectors plus a C02 burner. I am leaning towards another 5 ton unit for this area, but I would appreciate your opinion.

Thank you.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Mar 10, 2016
#1,718
windshear13 said:
Hi John. I have a follow up question regarding our veg area. We will be using 24 X 8 bulb t5's and 5 X 600 watt MH in parabolic reflectors plus a C02 burner. I am leaning towards another 5 ton unit for this area, but I would appreciate your opinion.

Thank you.
Click to expand...

How many watts are each of the T5 bulbs?
 
Quote Reply

windshear13

Posts
12
Reactions
2
Joined
Oct 20, 2015
Points
3
Mar 10, 2016
#1,719
They are 55 watts each, total of 440 per light. The total wattage of the room is approaching 13,000.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Mar 11, 2016
#1,720
windshear13 said:
They are 55 watts each, total of 440 per light. The total wattage of the room is approaching 13,000.
Click to expand...

5 ton will be close. I would do 2- 3 ton units
 
Quote Reply
Page 86 of 119 · Replies 1,701–1,720 of 2,371
Prev
  • 1
  • …
  • 84
  • 85
  • 86
  • 87
  • 88
  • …
  • 119
Next
First Prev 86 of 119 Next Last

Thread info

Replies 2,370
Views 421,631
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • 2026 Outdoor Grows! let's see em!
    • Latest: FarmerScotty
    • 7 minutes ago
    General Outdoor Growing
  • F
    First Auto grow gg4
    • Latest: fullyauto
    • 53 minutes ago
    Introduce Yourself
  • Blazing heat, smoke-filled skies, illegal! What could possibly go wrong?
    • Latest: Lockebox
    • Today at 4:52 AM
    General Outdoor Growing
  • S
    I have a question about vape pens
    • Latest: santosmaica
    • Today at 1:55 AM
    Concentrates & Processing
  • I’m Week 4 into Flowering
    • Latest: April14th2014
    • Today at 1:40 AM
    General Indoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?