#321
Classic Remix said:
quick question -

I have a 20 amp breaker that i want to throw approx 16-18 amps in, but im afraid of overloading it. i know it may not be code or whatever, but could i throw a 30 amp breaker on there instead, just so it wouldnt trip if there was a bigger flux over 80% of 20?? i know 30 amps run bigger gauge wire, but im not trying to run 30 amps, just 18 safely...

thanks!
Click to expand...

18 amps on a 20 amp breaker is 80%. You should be fine. I run 2 600's off one 20 amp breaker with 12/2 wire, and have had only one issue, the plug/receptacle was only rated for 15 amps with the 2 600's plugged into a power bar then the bar plugged into the receptacle, it melted a bit :oops:. Now I have a 20amp rated receptacle and have no issues.

PS

i ran my on 12/2 wire straight from the breaker to my plug box, no junctions anywhere. Make sure your 20 amp actually has 12/2 otherwise you will be loading the 14/2 past its capacity.
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Jan 23, 2013
#322
I see you cut math class to smoke a hooter huh:) soda,80% of 20amps is 16amps.The calculation would be 20x.80=16
 
Reactions: baba G, jkbeing and dan kherbs
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 23, 2013
#323
How'd you guess!! LOL My bad.
 
Reactions: fishwhistle
Quote Reply

Classic Remix

Posts
1,800
Reactions
4,064
Joined
Jun 17, 2012
Points
263
Jan 23, 2013
#324
which leaves my question re open! lol!
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 23, 2013
#325
Are you sure the breaker was never a 15 and been switched to a 20?
 
Quote Reply

Classic Remix

Posts
1,800
Reactions
4,064
Joined
Jun 17, 2012
Points
263
Jan 23, 2013
#326
yeah its always been a 20. it was originally in the house for the freezer in the basement.

i understand the gauge wire issues like i said, but if its rated for 20 amps a 30 amp breaker should simply just stop it from tripping right? cause it would never hit 20, it'd be a 1k digital ballast and a portable AC thats about 8-8.5 amps when fully running.... on every 12 off 12
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 23, 2013
#327
This is what I would do. I would run everything on the 20amp breaker as is for a week. If it doesn't trip by then it never will.IMO
 
Reactions: Classic Remix
Quote Reply

Classic Remix

Posts
1,800
Reactions
4,064
Joined
Jun 17, 2012
Points
263
Jan 23, 2013
#328
sounds good. i moved all my fans and bullshit to another breaker, just in case 100 watts helps here and there. which is will.

thanks mang!
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 23, 2013
#329
ya man, that 100 watts will make the world of difference. sorry not the watts, its the amps that add up.
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Jan 23, 2013
#330
 
Reactions: jkbeing
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 23, 2013
#331
what's that hooked up to it? no Breaker on there either. The purpose of your breaker is to protect that wire from something catastrophic like that from happening!
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Jan 23, 2013
#332
SodaLicious said:
what's that hooked up to it? no Breaker on there either. The purpose of your breaker is to protect that wire from something catastrophic like that from happening!
Click to expand...
Yeah well thats not going to happen if you have an oversized breaker hooked up to it right?The wire becomes the weak link and even if you dont replace the breaker with a larger one You are still here telling classic "go ahead and run an overloaded circuit'',A 1k digital ballast on 120v is gonna be 9.5-10 amps,his a/c he says is 8-8.5amps but both are going to spike on startup too and what about if/when they both startup together?You are not leaving ANY margin for safety at all,What if he has his kid sleeping in the next room when that shit lights up in the middle of the night?BAD ADVICE!
Couple things you can do here A)Use the 80% rule which limits you to sixteen amps on that circuit B)Run another circuit if you have the room/capacity in your panel,Preferably 240 which will cut your amp draw in half.
Electricity is an unforgiving bitch,you can pay now and do it right or you can pay later when your shit is ashes on the ground.
 
Reactions: baba G and jkbeing
Quote Reply

Classic Remix

Posts
1,800
Reactions
4,064
Joined
Jun 17, 2012
Points
263
Jan 24, 2013
#333
ended up throwing the AC on its own 15A....

so its all worked out... thanks guys!
 
Reactions: fishwhistle
Quote Reply

jkbeing

Posts
285
Reactions
356
Joined
Nov 11, 2011
Points
63
Jan 24, 2013
#334
Now imagine that wire doing that inside your wall! That happens to growops a few times a year where I live.
 
Reactions: fishwhistle
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 24, 2013
#335
fishwhistle said:
Yeah well thats not going to happen if you have an oversized breaker hooked up to it right?The wire becomes the weak link and even if you dont replace the breaker with a larger one You are still here telling classic "go ahead and run an overloaded circuit'',A 1k digital ballast on 120v is gonna be 9.5-10 amps,his a/c he says is 8-8.5amps but both are going to spike on startup too and what about if/when they both startup together?You are not leaving ANY margin for safety at all,What if he has his kid sleeping in the next room when that shit lights up in the middle of the night?BAD ADVICE!
Couple things you can do here A)Use the 80% rule which limits you to sixteen amps on that circuit B)Run another circuit if you have the room/capacity in your panel,Preferably 240 which will cut your amp draw in half.
Electricity is an unforgiving bitch,you can pay now and do it right or you can pay later when your shit is ashes on the ground.
Click to expand...


I get where your coming from, but I never said up the size of the breaker, I was just saying if it's 12/2 with a 20 amp fuse, plug your shit in if it blows the breaker then you need to find a solution. if it doesn't then your good. If there is 18 amps on the breaker at all times, and it doesn't heat up and trip, does that mean the wire is sitting in the wall getting hotter, and hotter until catastrophic failure like in the video?
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Jan 24, 2013
#336
When you buy a new lamp for the living room and it trips the breaker, do you think to yourself I must have exceeded 80% of the load capacity on the circuit? No probably not you plug it into another outlet. If you aren't supposed to run 18 amps on a 20 amp breaker, why isn't the wire being protected by an 18 amp breaker?
 
Quote Reply

fishwhistle

Posts
4,684
Reactions
10,449
Joined
May 4, 2011
Points
263
Jan 24, 2013
#337
Soda,im sure olyver will chime in here sometime,im a contractor not an electrician so i know just enough to be dangerous,lol.
One last time,here goes,For safetys sake you should only load a circuit to 80% which in this case was 16 amps.You may well be able to load it past twenty for all i know but its stupid to exceed the safety factor and not expect a bad outcome.
As for your lamp scenario,If i plug in a lamp and it throws the breaker and its not overloaded i would look for a short or possibly a weak/bad breaker that needs to be replaced,its rediculous to just plug it in another outlet which may in fact be hooked to the same breaker,how does this solve the problem?I want to know WTF is CAUSING the problem so i can fix it.
The reason you dont run a circuit drawing 18 amps with an 18 amp breaker is because you would be running that circuit at 100% and have NO safety factor at all,Imagine if you drove your car at MAX rpms from the second you started it until the second you turned it off,how long do you think it would last until you had a problem or it failed?
 
Reactions: baba G
Quote Reply

BCrocker

Posts
428
Reactions
57
Joined
May 26, 2011
Points
28
Jan 25, 2013
#338
Question...

Shop transformer on pole is 25 KW, ... Although we pull consistantly 150-170 amps out of it 24hrs a day. Why doesn't it blow?

I dont understand how kva, or kw works... except that 25 kw would be 25000 watts, would be divived by your voltage to give the ampage..? In this case it should be 113a.
 
Quote Reply

Dr.stickerdick

Posts
176
Reactions
26
Joined
Jan 10, 2009
Points
28
Feb 5, 2013
#339
BCrocker, your's has had me scratching my head. Where do you get 113 A ? 25 KVA single phase tranny @ 480v. = 156 amps. @ 240v. = 312 amps. With 75 KVA three phase @ 480 v.= 94 amps, with 240 v.= 181 amps. Peace Classic Remix, You really should know whether it is 16 or 18 amps. To determine wire and breaker size 18 a. @ 125% = 22.5 a. too much for 20 abreaker and # 12 ga. wire. 16 a. @ 125% = 20 a. ok for 20 a. breaker / # 12 ga. wire if not continuous load, but not with 80% rule on 20 a.breaker if continuous load. Going to 30 amp breaker ,,,,,,,,NO PHUCKING WAY Y Y Y Y.. Please never even think this way. Please. Peace
 
Quote Reply

SodaLicious

Posts
533
Reactions
230
Joined
Jul 5, 2011
Points
43
Feb 5, 2013
#340
fishwhistle said:
Soda,im sure olyver will chime in here sometime,im a contractor not an electrician so i know just enough to be dangerous,lol.
One last time,here goes,For safetys sake you should only load a circuit to 80% which in this case was 16 amps.You may well be able to load it past twenty for all i know but its stupid to exceed the safety factor and not expect a bad outcome.
As for your lamp scenario,If i plug in a lamp and it throws the breaker and its not overloaded i would look for a short or possibly a weak/bad breaker that needs to be replaced,its rediculous to just plug it in another outlet which may in fact be hooked to the same breaker,how does this solve the problem?I want to know WTF is CAUSING the problem so i can fix it.
The reason you dont run a circuit drawing 18 amps with an 18 amp breaker is because you would be running that circuit at 100% and have NO safety factor at all,Imagine if you drove your car at MAX rpms from the second you started it until the second you turned it off,how long do you think it would last until you had a problem or it failed?
Click to expand...


after this i will never speak of it again:-)

If your average joe, that isn't growing mj, or have any experience with electricity, moves into a new house, sets up his tv in the living room, and a couple of lamps, turns on the tv, and the breaker blows, does he panic and think that he must be running that circuit over 80%? Or does he simply unplug one of his lamps that is beside the couch, and now the tv doesn't pop the breaker. If he continues to use that TV on that circuit, that a 60watt light bulb added will blow the breaker, is he in danger? I am just saying that you can't tell me that every 15 amp breaker in your panel is drawing only 80%. How does the average joe know the difference between a freezer at 7 amps and a washing machine at 7 amps plugged into the same circuit, is over 80%, he knows it's safe because the breaker doesn't trip.
 
Reactions: Dr.stickerdick
Quote Reply
Page 17 of 71 · Replies 321–340 of 1,407
Prev
  • 1
  • …
  • 15
  • 16
  • 17
  • 18
  • 19
  • …
  • 71
Next
First Prev 17 of 71 Next Last

Thread info

Replies 1,406
Views 327,255
Started Mar 20, 2012
Latest post Mar 3, 2024
Starter hiboy
Forum Growroom Design & Setup

Latest posts

  • R
    Nutrient burn or is it a deficiency....
    • Latest: RR1313
    • A moment ago
    Basic Growing Information
  • Some advice needed on outdoor growing...
    • Latest: Galgrows
    • 5 minutes ago
    General Outdoor Growing
  • R
    New guy
    • Latest: RR1313
    • 9 minutes ago
    Introduce Yourself
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Galgrows
    • 9 minutes ago
    General Outdoor Growing
  • 40 days into cure , no change in smell or flavor
    • Latest: Galgrows
    • 10 minutes ago
    Cannabis Infirmary
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room Electrical
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?