i Have 26 1000 watt light going and they all run at 4.5 amp. Two 5 ton Ac units plus my house Ac

Is this 2 much for a 200 amp service
 
Quote Reply

OldManRiver

Posts
1,390
Reactions
2,880
Joined
Jul 20, 2017
Points
263
Aug 7, 2018
#2
You're probably alright. 100 amps for lights. You can look at the circuit breakers for the AC units and figure out how much they draw(it'll be less than the rating of the breaker).
 
Quote Reply

Dbear180

Posts
1,297
Reactions
3,429
Joined
Nov 27, 2017
Points
263
Aug 7, 2018
#3
Your not an electrician, I suggest you shut yer mouth. You didnt even multiply the amps right, you were off by almost 4 lights. IF ANYONE EVER TELLS YOU "PROBABLY" WHEN IT COMES TO ELECTRICITY DO NOT LISTEN TO THEM! I guarantee you he does not know. Anybody who says maybe, or well see, or let's see how it goes, or probably, does not understand they are putting YOUR life in danger. 117!!!! PLUS 30amps PER AC IS 207 AMPS.... yeah you'll probably be ok... gtfo here cant even add & you wanna tell the guy hell probably be ok. Both of you are perfect examples of why we have electrical fires in grow spots.
 
Reactions: 1diesel1, Olyver, RooR5mm and 3 others
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 8, 2018
#4
Dbear180 said:
Your not an electrician, I suggest you shut yer mouth. You didnt even multiply the amps right, you were off by almost 4 lights. IF ANYONE EVER TELLS YOU "PROBABLY" WHEN IT COMES TO ELECTRICITY DO NOT LISTEN TO THEM! I guarantee you he does not know. Anybody who says maybe, or well see, or let's see how it goes, or probably, does not understand they are putting YOUR life in danger. 117!!!! PLUS 30amps PER AC IS 207 AMPS.... yeah you'll probably be ok... gtfo here cant even add & you wanna tell the guy hell probably be ok. Both of you are perfect examples of why we have electrical fires in grow spots.
Click to expand...


Thanks man I appreciate the input. My electrician must of not been good at math ether becuz he said I would be good.
 
Reactions: Jack og
Quote Reply

Dbear180

Posts
1,297
Reactions
3,429
Joined
Nov 27, 2017
Points
263
Aug 8, 2018
#5
Greengiant11 said:
Thanks man I appreciate the input. My electrician must of not been good at math ether becuz he said I would be good.
Click to expand...

I mean if your not running everything at once (say like two rooms on a flip schedule) you will be ok. But if your running all of that theres no way. Sorry I ranted, kinda caught me in a mood lol.
 
Reactions: 1diesel1 and Jack og
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 8, 2018
#6
Dbear180 said:
I mean if your not running everything at once (say like two rooms on a flip schedule) you will be ok. But if your running all of that theres no way. Sorry I ranted, kinda caught me in a mood lol.
Click to expand...



Your fine. I know running to much power is dangerous to me and other around me. So I was making sure. If I was ok. Do u think if I turned like 10 lights on 400 Watts I’d be good
 
Reactions: Jack og
Quote Reply

Dbear180

Posts
1,297
Reactions
3,429
Joined
Nov 27, 2017
Points
263
Aug 8, 2018
#7
Greengiant11 said:
Your fine. I know running to much power is dangerous to me and other around me. So I was making sure. If I was ok. Do u think if I turned like 10 lights on 400 Watts I’d be good
Click to expand...

You'll need a dedicated 50 amps for 10 lights, 60 amps would be better, gives you just a lil more buffer zone before that breaker is on the verge of flipping.
 
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 8, 2018
#8
I have three 8 lighting controllers. Each on there own 50 amp breakers. My main breaker is popping. None of the lighting controllers r.
 
Reactions: Jack og
Quote Reply

Dbear180

Posts
1,297
Reactions
3,429
Joined
Nov 27, 2017
Points
263
Aug 8, 2018
#9
Main breaker like your whole house loses power?
 
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 8, 2018
#10
Dbear180 said:
Main breaker like your whole house loses power?
Click to expand...

Yes
 
Quote Reply

Dbear180

Posts
1,297
Reactions
3,429
Joined
Nov 27, 2017
Points
263
Aug 8, 2018
#11
If your whole house is losing power you may have a major issue. I would call a licensed electrician to check it out. It could be a combination of things.
A bad connection on a major appliance is arcing causing it to get hot & flip.
You have a short circuit in your panel
Your main breaker could be going bad
Your feeders from the power pole may have a bad connection in the panel.

I would really have it looked at by a pro your other guy may have done some not so safe wiring.
 
Reactions: 1diesel1 and Jack og
Quote Reply

Freshone

Posts
1,620
Reactions
6,140
Joined
Jul 6, 2016
Points
263
Aug 8, 2018
#12
Ill throw in my 2 cents,
26x4.5=117 amps,now add in a 20% safety factor=140 amps
5 ton ACs are usually rated at 40 amps but recommend 60amp breaker,lets just call it 50 amps Using the 20% safety factor so 2x50=100amps,so 240 amps PLUS the house,your way over.You can use a flipbox for the lights and run 1/2 at a time and cut your lighting amp draw in half but the ACs still run so your still at 170 amps WITHOUT the house or house AC.
Couple suggestions,
Always use a 20% safety factor on your circuits unless you want to burn shit down(probably why your popping breakers)
Dont worry about how many lights you have,worry about how manys amps you have to run them.
Make sure your wiring,main and subpanels are on point.
Personally id dedicate 50-75 amps for the house(-20% safety factor)=40-60 amps for the house and that leaves you with 125-150 amps for your grow (-20% safety factor) leaving 100-125 amps usable,Now how many lights and ACs can you run with that?
 
Reactions: 1diesel1, Dbear180, PharmHand and 1 other person
Quote Reply

Jack og

Supporter
Posts
2,898
Reactions
5,424
Joined
Jun 11, 2018
Points
263
Aug 8, 2018
#13
Well if the main trips when lights are on, then either there is an undersized breaker and or bad neutral, having dedicated lines to each breaker should interrupt any overload provided it’s properly gauged. Now h whole house tripping out? Brother something is off, I’d suggest a good local electrical contractor pay u a visit ASAP. Till then, I’d suggest cutting back all use on the new system. Mains don’t arbitrarily pop. If they do something serious is wrong.
 
Reactions: Jbellsmoke and Dbear180
Quote Reply

Jack og

Supporter
Posts
2,898
Reactions
5,424
Joined
Jun 11, 2018
Points
263
Aug 9, 2018
#14
Quick question? Did they guy that installed the contactors run an amp load test? Say turn on each and check and note what the load to each is? I’d say perhaps one bad ballast exists, it will pull “ more then designed” amps, would indicate what and where the draw is and what maybe causing this issue. You can do this easily with a amp meter, turn on one and see if that draws the right amps and or if the mains trip. . Likely u will find which one is causing the issue. Isolate and turn everything on and see if that stabilizes . If not then the incoming power maybe an issue. I’ve had a rental property that exhibited that issue , turned out to be a loose neutral from incoming side on the pole. But I do suggest a licensed electrician check it out. Don’t burn ya house down bro! !
 
Reactions: Greengiant11 and Dbear180
Quote Reply

RooR5mm

Posts
146
Reactions
132
Joined
May 8, 2018
Points
43
Aug 9, 2018
#15
:woot::woot::woot:
 
Reactions: Jack og
Quote Reply

Jack og

Supporter
Posts
2,898
Reactions
5,424
Joined
Jun 11, 2018
Points
263
Aug 9, 2018
#16
Yea watch the news, “ thc farmer forum members house up in flames”
Lol. I hope never to see that news bro! Scary that I actually known few folks that have burned their houses down due to too many lights or making bho! And smoking smh! Like really wtf:)
 
Reactions: Dbear180
Quote Reply
P

PharmHand

Posts
846
Reactions
1,641
Joined
Mar 10, 2017
Points
143
Aug 9, 2018
#17
Build a wall,flip flop. Or bring in another 200a service
 
Reactions: 1diesel1, Freshone and Dbear180
Quote Reply

Freshone

Posts
1,620
Reactions
6,140
Joined
Jul 6, 2016
Points
263
Aug 9, 2018
#18
Jack og said:
Yea watch the news, “ thc farmer forum members house up in flames”
Lol. I hope never to see that news bro! Scary that I actually known few folks that have burned their houses down due to too many lights or making bho! And smoking smh! Like really wtf:)
Click to expand...
Only reason i responded is because my kids a fireman and rolls on growfires daily,sometimes more than one,always electrical.
 
Reactions: 1diesel1, Dbear180 and Jack og
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 9, 2018
#19
Ya I’m gonna have someone take a look at it. It was running fine with 21 lights but I just added another lighting controller with 5 more lights. It ran for about a hour then popped the main power breaker. The main breaker was pretty hot also.
 
Reactions: Jack og
Quote Reply
G

Greengiant11

Posts
19
Reactions
8
Joined
Aug 7, 2018
Points
3
Aug 9, 2018
#20
Jack og said:
Quick question? Did they guy that installed the contactors run an amp load test? Say turn on each and check and note what the load to each is? I’d say perhaps one bad ballast exists, it will pull “ more then designed” amps, would indicate what and where the draw is and what maybe causing this issue. You can do this easily with a amp meter, turn on one and see if that draws the right amps and or if the mains trip. . Likely u will find which one is causing the issue. Isolate and turn everything on and see if that stabilizes . If not then the incoming power maybe an issue. I’ve had a rental property that exhibited that issue , turned out to be a loose neutral from incoming side on the pole. But I do suggest a licensed electrician check it out. Don’t burn ya house down bro! !
Click to expand...

No he didn’t. I’m gonna try that out tomorrow thanks.
 
Reactions: Jack og
Quote Reply
Page 1 of 2 · Replies 1–20 of 34
  • 1
  • 2
Next
1 of 2 Next Last

Thread info

Replies 33
Views 3,758
Started Aug 7, 2018
Latest post Aug 10, 2018
Starter Greengiant11
Forum Growroom Design & Setup

Latest posts

  • Grayoldnprouds chant of the ever circling Skeletal Family.
    • Latest: grayoldnproud
    • 21 minutes ago
    Grow Diaries
  • Gmix’s mixed grow mayhem
    • Latest: Itscheese94
    • 23 minutes ago
    Grow Diaries
  • 2026 Outdoor Grows! let's see em!
    • Latest: Hossgrows
    • 59 minutes ago
    General Outdoor Growing
  • itscheese`s cheese thread
    • Latest: Itscheese94
    • Today at 7:06 PM
    Introduce Yourself
  • Help with dropping seedlings please !
    • Latest: Bogota.Mark
    • Today at 6:41 PM
    General Indoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Power Question
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?