Yea, and startup would probablly fry ur shit, lol. 12 lights is 54 amps thru a 60 amp rated setup.. Thats less than 10% safety margin..
There should have been instructions with the CAP MLC-8, or you can log onto their website and look up the installation instructions. 8 guage wire is the minimum you should use, I would recommend using 6 awg. The total current draw for 8 x 1000W ballasts @ 240V will be approximately 40A. Best would be to use a 50A two-pole breaker.