CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 18, 2013
#601
Chrondondalae said:
You are the man CJ. Got another question for you. I was planning on using some H20 coolers for my veg but my dumb ass didn't winterize them in storage. Some froze up and some copper pipes cracked, so I'm fooked on those. Room will have 8k adjust a wings and 4x 8bulb T5's. I do have an extra 5 ton Excel, would that be too big?
Click to expand...

5 ton is a bit oversized but should do ok. Once you get it up and running make sure the unit is not starting and stopping too much. Would like to see it run for 10-15 minutes and be off for at least 10 minutes. Longer run times are ok. But it should be off for at least 10 minutes before it comes back on.
 
Reactions: ftwendy
Quote Reply

Chrondondalae

Posts
223
Reactions
404
Joined
May 26, 2011
Points
63
Aug 18, 2013
#602
Ok, that's good to know for AC's in general.
 
Quote Reply

Haggardass

Posts
712
Reactions
469
Joined
Jun 16, 2012
Points
63
Aug 21, 2013
#603
My question is I have a portable ac vented into the side of my 4x4 tent, i can't have the ac completely shut down at night I still need the fan to run all night, obviously the ac being blown through the side if the tent means it's reading the temp of the room it's in, so my question is, is there a way i can run the thermostat wire out of the ac and into the tent? More so what does this thermostat wire look like where would it be located inside the unit? If you need any more information please let me know, it's a soleus air 8k btu
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 21, 2013
#604
Haggardass said:
My question is I have a portable ac vented into the side of my 4x4 tent, i can't have the ac completely shut down at night I still need the fan to run all night, obviously the ac being blown through the side if the tent means it's reading the temp of the room it's in, so my question is, is there a way i can run the thermostat wire out of the ac and into the tent? More so what does this thermostat wire look like where would it be located inside the unit? If you need any more information please let me know, it's a soleus air 8k btu
Click to expand...

Most likely not. It is digital right?
 
Quote Reply

Haggardass

Posts
712
Reactions
469
Joined
Jun 16, 2012
Points
63
Aug 22, 2013
#605
Correct, but it should still have something that tells it the temp, is that just a sensor?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 22, 2013
#606
Haggardass said:
Correct, but it should still have something that tells it the temp, is that just a sensor?
Click to expand...

Yes it does. Most likely a sensor near intake of indoor coil or on face of coil. Be careful. Extending wire from sensor may change temperature sensor reads.
 
Reactions: Haggardass
Quote Reply

Haggardass

Posts
712
Reactions
469
Joined
Jun 16, 2012
Points
63
Aug 22, 2013
#607
Any idea what it looks like or how i would find it?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 22, 2013
#608
Haggardass said:
Any idea what it looks like or how i would find it?
Click to expand...
Small cylinder maybe 1-2 inches long and about the diameter of a pencil. Find air filter and look behind it on the coil.
 
Reactions: Haggardass
Quote Reply

Haggardass

Posts
712
Reactions
469
Joined
Jun 16, 2012
Points
63
Aug 22, 2013
#609
Thank you
 
Quote Reply

NightShift

Posts
42
Reactions
41
Joined
Oct 26, 2012
Points
18
Aug 26, 2013
#610
Reccomended minisplit unit for an aircooled 6k? I have a window unit right now but I want something with a better energy rating. Also I use c02 so it would be nice to seal the room better.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 26, 2013
#611
NightShift said:
Reccomended minisplit unit for an aircooled 6k? I have a window unit right now but I want something with a better energy rating. Also I use c02 so it would be nice to seal the room better.
Click to expand...

Mitsubushi 2 ton would be excellent with inverter.
 
Quote Reply
S

sicinsane

Posts
75
Reactions
61
Joined
Jul 26, 2012
Points
18
Aug 26, 2013
#612
CannabisJohn said:
Mitsubushi 2 ton would be excellent with inverter.
Click to expand...

hey john where are you purchasing your mini splits at now?
 
Quote Reply

NightShift

Posts
42
Reactions
41
Joined
Oct 26, 2012
Points
18
Aug 26, 2013
#613
CannabisJohn said:
Mitsubushi 2 ton would be excellent with inverter.
Click to expand...


Mitsubishi 2 ton. t 24,000 btu. Do u think that would be overkill for air cooled lights? I use either a 12,000 or 18,000 btu a/c right now with 6 lights and my temps are well under control even in the California summer. Why such a powerful reccomendation?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 27, 2013
#614
sicinsane said:
hey john where are you purchasing your mini splits at now?
Click to expand...

I have a local supply in SoCal.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 27, 2013
#615
NightShift said:
Mitsubishi 2 ton. t 24,000 btu. Do u think that would be overkill for air cooled lights? I use either a 12,000 or 18,000 btu a/c right now with 6 lights and my temps are well under control even in the California summer. Why such a powerful reccomendation?
Click to expand...

I always recommend 4000 btus/hr per 1kw of air cooled lighting and 6000 btus/hr per 1 kw if lights are not air cooled. Most jobs I do are brand new rooms and I want to be sure there is enough a/c for the worst case. Also with inverter type units if it is slightly oversized it will not hurt. Also cost difference is minimal for piece of mind.
 
Reactions: ftwendy, darlingmaster, fishwhistle and 1 other person
Quote Reply

NightShift

Posts
42
Reactions
41
Joined
Oct 26, 2012
Points
18
Aug 27, 2013
#616
CannabisJohn said:
I always recommend 4000 btus/hr per 1kw of air cooled lighting and 6000 btus/hr per 1 kw if lights are not air cooled. Most jobs I do are brand new rooms and I want to be sure there is enough a/c for the worst case. Also with inverter type units if it is slightly oversized it will not hurt. Also cost difference is minimal for piece of mind.
Click to expand...


Yes I agree with you the cost difference is minimal in the initial installation. I pay electricity rates over 300% of baseline which is .35 cents per kilowatt hour so its smart to run as less juice as possible. Thanks for the recommendation. I will consider.
 
Quote Reply
V

vino

Posts
74
Reactions
31
Joined
Mar 5, 2013
Points
18
Aug 27, 2013
#617
I have a few questions about my AC unit and thermostats.
Im running a 5ton york with a zonemaster connecting to 4 zones. All the thermostats are on wall in the room, and I wanted to know if there is a remote sensor that can placed in center of room to get reading from there instead of wall.
Also is it possible to install Nest thermostats on ordinary thermostat gauge?

The rooms are sealed 12wx16wx12h.
6k. Non aircooled.

The blueprint controller image is just an idea of part of my setup. Each room though has an ordinary thermostat, which is only connected to zonemaster. Can it be connected to blueprint sensor? Does the Nest Thermostat have better algorithms to control temp/humid?

Im having a real problem with Temps at night being low and Humidity being high. Im running a 30pint dehu in the room but it definately is not working. Any ideas on a specific Dehu I should get?
 

Attachments

  • IMG_8956.jpg
    96.8 KB · Views: 276
  • IMG_8955.jpg
    94 KB · Views: 292
  • IMG_8909.jpg
    140.2 KB · Views: 296
  • IMG_8908.jpg
    121.2 KB · Views: 278
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 27, 2013
#618
vino said:
I have a few questions about my AC unit and thermostats.
Im running a 5ton york with a zonemaster connecting to 4 zones. All the thermostats are on wall in the room, and I wanted to know if there is a remote sensor that can placed in center of room to get reading from there instead of wall.
Also is it possible to install Nest thermostats on ordinary thermostat gauge?

The rooms are sealed 12wx16wx12h.
6k. Non aircooled.

The blueprint controller image is just an idea of part of my setup. Each room though has an ordinary thermostat, which is only connected to zonemaster. Can it be connected to blueprint sensor? Does the Nest Thermostat have better algorithms to control temp/humid?

Im having a real problem with Temps at night being low and Humidity being high. Im running a 30pint dehu in the room but it definately is not working. Any ideas on a specific Dehu I should get?
Click to expand...

Remote sensor depends on make and model of stat. Not super familiar with Nest stats but I know they use standard stat wire. Can not directly connect the a/c to the Blueprint controller. Should have at least 60-90 pint dehumidication capabilities.
 
Quote Reply
V

vino

Posts
74
Reactions
31
Joined
Mar 5, 2013
Points
18
Aug 27, 2013
#619
CannabisJohn said:
Remote sensor depends on make and model of stat. Not super familiar with Nest stats but I know they use standard stat wire. Can not directly connect the a/c to the Blueprint controller. Should have at least 60-90 pint dehumidication capabilities.
Click to expand...
Ill take a picture of the stat tom. Now if i wanted to switch out stat one that works with a sensor , would you have a recommendation on what setup to use?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Aug 27, 2013
#620
vino said:
Ill take a picture of the stat tom. Now if i wanted to switch out stat one that works with a sensor , would you have a recommendation on what setup to use?
Click to expand...

Yes I would. Can not remember the brand . Been smoking. Will get you info soon.
 
Quote Reply
Page 31 of 119 · Replies 601–620 of 2,371
Prev
  • 1
  • …
  • 29
  • 30
  • 31
  • 32
  • 33
  • …
  • 119
Next
First Prev 31 of 119 Next Last

Thread info

Replies 2,370
Views 421,640
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • Strainshow is back
    • Latest: Strainshow2.0
    • 11 minutes ago
    Introduce Yourself
  • Blazing heat, smoke-filled skies, illegal! What could possibly go wrong?
    • Latest: Oldchucky
    • 33 minutes ago
    General Outdoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Oldchucky
    • 40 minutes ago
    General Outdoor Growing
  • Big Al’s 2025 season indoor/outdoor grow in misery
    • Latest: grayoldnproud
    • 57 minutes ago
    Grow Diaries
  • 2026 Outdoor Grows! let's see em!
    • Latest: grayoldnproud
    • Today at 12:51 PM
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?