Just a heads up for other farmers.

I took the advice of this forum and hired a professionally trained HVAC tech. Hes actually a 63 year old guy who owns his own HVAC company . he also loves to medicate.

My ideal air had a leak and stopped cooling. He found and fixed the leak at the line set connection. Vacuumed. then weighed in a charge. That was all good. However these house tech guys do this thing where they take the temp of the line set and compare it to their read out temp and if its not a 15-20 degree difference they keep adding more refrigerant. He over filled the system and within an hour or two the manifold feeding the evaporator on the inside unit exploded and leaked a bunch of freon into my grow room.

We found the leak and sweated it closed .

Basically paid the guy 560$ to break my minisplit then come back and fix his mistake which he wouldn't admit to making.

My new Mr slim gets delivered today and once I harvest I will replace the ideal air with this unit.

I'm highly tempted to buy gauges and do my own charge
 
Reactions: lollipopman
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Sep 2, 2015
#1,522
FooDoo said:
Just a heads up for other farmers.

I took the advice of this forum and hired a professionally trained HVAC tech. Hes actually a 63 year old guy who owns his own HVAC company . he also loves to medicate.

My ideal air had a leak and stopped cooling. He found and fixed the leak at the line set connection. Vacuumed. then weighed in a charge. That was all good. However these house tech guys do this thing where they take the temp of the line set and compare it to their read out temp and if its not a 15-20 degree difference they keep adding more refrigerant. He over filled the system and within an hour or two the manifold feeding the evaporator on the inside unit exploded and leaked a bunch of freon into my grow room.

We found the leak and sweated it closed .

Basically paid the guy 560$ to break my minisplit then come back and fix his mistake which he wouldn't admit to making.

My new Mr slim gets delivered today and once I harvest I will replace the ideal air with this unit.

I'm highly tempted to buy gauges and do my own charge
Click to expand...
Lmao wow sounds like he was trying to charge with using superheat/subcooling. Which is what you suppose to do. Most that charge that way don't have a clue that they suppose to go by target superheat. If the lines inside blew out and he wasn't the installer it is not his fault. Just my .02.
 
Reactions: FooDoo
Quote Reply
F

FooDoo

Posts
1,278
Reactions
3,159
Joined
Aug 6, 2014
Points
263
Sep 2, 2015
#1,523
@Og Gong the line the cracked and leaked which we had to sweat and solder was inside the plastic casing of the inside air handler. A part that has nothing to do with an install .

In this generic picture off Google , the crack happened on one of the copper pipes on the right side that feed the evaporator

 
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Sep 2, 2015
#1,524
FooDoo said:
@Og Gong the line the cracked and leaked which we had to sweat and solder was inside the plastic casing of the inside air handler. A part that has nothing to do with an install .

In this generic picture off Google , the crack happened on one of the copper pipes on the right side that feed the evaporator

View attachment 533304[/QUOTE
A refrigerant system does not explode by overcharging. If it was running a couple of hours and then ruptured what was the head pressure? The system has a safety high pressure switch that shuts the compressor off if it exceeds the 400-500 psig head pressure. So if the lines ruptured it could of been a small leak or a stress fracture from shipping that was found after the charge. If you weight in a charge and you still have a low suction pressure you may have a refrigerant restriction or low airflow. This is where you troubleshoot with superheat and subcooling. The discharge pressure and suction pressure will give you clues if you are over or under charge, restricted refrigerant line or a airflow problem. If your tech put the system on a vacume did he achieve 500microns? If not there are still leaks in the system or his gauges leaks. I'm not saying it has leaks just trying to give you all the scenarios that can happen. Good luck with it brother.
Click to expand...
 
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Sep 2, 2015
#1,525
Oops my quote is in the quote, have to expand it. I don't know how I did that.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 2, 2015
#1,526
FooDoo said:
Just a heads up for other farmers.

I took the advice of this forum and hired a professionally trained HVAC tech. Hes actually a 63 year old guy who owns his own HVAC company . he also loves to medicate.

My ideal air had a leak and stopped cooling. He found and fixed the leak at the line set connection. Vacuumed. then weighed in a charge. That was all good. However these house tech guys do this thing where they take the temp of the line set and compare it to their read out temp and if its not a 15-20 degree difference they keep adding more refrigerant. He over filled the system and within an hour or two the manifold feeding the evaporator on the inside unit exploded and leaked a bunch of freon into my grow room.

We found the leak and sweated it closed .

Basically paid the guy 560$ to break my minisplit then come back and fix his mistake which he wouldn't admit to making.

My new Mr slim gets delivered today and once I harvest I will replace the ideal air with this unit.

I'm highly tempted to buy gauges and do my own charge
Click to expand...

Ideal Air units are garbage. I had to say that.
Mini splits are critically charged. The amount of refrigerant shipped with unit is on name plate. Also on nameplate should be how much line set it is charged for without adding more refrigerant from factory. All he needs is a scaled not be fucking lazy. Assholes like that give us good techs a bad name. I don't believe the cheap ass Ideal Air units have a high pressure safety. It's possible without that safety that he caused the problem. Sorry it happened to you. Still don't recommend that u install or charge new unit.
 
Reactions: FooDoo and fishwhistle
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 2, 2015
#1,527
Tylrr420 said:
Hey guys I'm thinking I need to upgrade
My mini and would like some opinions. It is an aura 36,000. Back when I installed it it was for 6 air cooled 1000s and I never had a prob cooling them. It has been about 18 months since installation (bought it used with I'm not sure how many hours). And since then i have added a water cooled co2 burner and one more gavita 600. I clean both the hamster cage and the condenser after every run. I take good care of it. I am looking into going to 8 1k air cooled and ripping out the gavita ( it was just a lil test light) I live in Michigan so the new mini split has to be able to operate in the frigid cold if thats the route I go. I'm pretty sure that my current mini split isn't inverter technology either so it would be nice to switch up to something with that for energy concerns. ( cause when it did used to cool the room properly it would be on for 10 minutes and off for maybe 5.) I used to have no problem cooling my room down to 79 and with this summer heat latley I can't get it below 86 . I also have a tech that just recharged it too and that did seem to help for about a month (maybe).
Click to expand...

Make the lazy tech come back out for free. He or she needs to find and repair leak that caused them to recharge unit previously. With that said Aura units are not very good.
 
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Sep 2, 2015
#1,528
Thanks cj I kinda figured you would say that. Can you please tell me what to look for when buying a Mitsubishi? I noticed that some of the 30k plus units are 2-3000 and some are 5-6000? What are you getting for double the price?
 
Quote Reply
F

FooDoo

Posts
1,278
Reactions
3,159
Joined
Aug 6, 2014
Points
263
Sep 2, 2015
#1,529
CannabisJohn said:
Ideal Air units are garbage. I had to say that.
Mini splits are critically charged. The amount of refrigerant shipped with unit is on name plate. Also on nameplate should be how much line set it is charged for without adding more refrigerant from factory. All he needs is a scaled not be fucking lazy. Assholes like that give us good techs a bad name. I don't believe the cheap ass Ideal Air units have a high pressure safety. It's possible without that safety that he caused the problem. Sorry it happened to you. Still don't recommend that u install or charge new unit.
Click to expand...


New unit has landed

 
Reactions: lollipopman
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 2, 2015
#1,530
Tylrr420 said:
Thanks cj I kinda figured you would say that. Can you please tell me what to look for when buying a Mitsubishi? I noticed that some of the 30k plus units are 2-3000 and some are 5-6000? What are you getting for double the price?
Click to expand...

Not sure unless you I could see model numbers or Internet ad.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 2, 2015
#1,531
FooDoo said:
New unit has landed

View attachment 533384
Click to expand...

Now you're talking.
 
Reactions: FooDoo
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Sep 2, 2015
#1,532
https://www.acwholesalers.com/Ductl...5&subCat=cat1033&trail=68436:more+than+30,001



For instance the Mitsubishi on the first row compared to any on the second row
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 2, 2015
#1,533
Tylrr420 said:
https://www.acwholesalers.com/Ductless-Air-Conditioner-Wall-Mounted-Air-Conditioners/cat1028.ac?mainCat=cat22185&subCat=cat1033&trail=68436:more+than+30,001



For instance the Mitsubishi on the first row compared to any on the second row
Click to expand...

That's a P series unit. It is a server room level unit. Heavier duty. Mitsubushi will tell u that we shouldn't run the M series in our rooms and run the P series. IMO that's bullshit. I have had very,very few problems with over 200 M series installed in our industry. So IMO the P series isn't worth the money. LG makes a fine unit also with most of their units having same warranty as Mitshbushi (7 yrs compressor and 5 years rest of unit). Both are similar in price also.
 
Reactions: fishwhistle, sixstring and FooDoo
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Sep 2, 2015
#1,534
Thanks so much man
 
Quote Reply

dexfarm

Posts
53
Reactions
54
Joined
Oct 18, 2014
Points
18
Sep 3, 2015
#1,535
Hey CJ, you never mention these units, are they no good?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 5, 2015
#1,536
dexfarm said:
Hey CJ, you never mention these units, are they no good?
Click to expand...

Only one I've ever seen was broken with only 2 months of use.
 
Reactions: dexfarm
Quote Reply

Doc G

Posts
78
Reactions
38
Joined
Jun 8, 2015
Points
18
Sep 5, 2015
#1,537
i am aware mitsubishi & lg, fujitsu are @ the top of the class for the mini splits.... Currently rocking two lg's. But need a little something for VEG & kitchen so was wondering about a pioneer with inverter technology? any feedback welcome please on the durability and reliability of this brand...
 
Quote Reply

Doc G

Posts
78
Reactions
38
Joined
Jun 8, 2015
Points
18
Sep 5, 2015
#1,538
@ CJ & @ OG GONG
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 5, 2015
#1,539
Doc G said:
i am aware mitsubishi & lg, fujitsu are @ the top of the class for the mini splits.... Currently rocking two lg's. But need a little something for VEG & kitchen so was wondering about a pioneer with inverter technology? any feedback welcome please on the durability and reliability of this brand...
Click to expand...

Never dealt with this brand before. IMO it'll either be a POS or great. Let us know what u think if u get it.
 
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Sep 8, 2015
#1,540
Hey john I was wondering what your opinion was about mounting a mini split condenser to the wall? I've seen it done before and I seen the brackets for sale on eBay specifically for this. I would assume that cleaning the fins out would be a task unless you left a 2 inch gap and used compressed air instead of water. I have a low key spot where there is an inside corner in my house that would be perfect for this application as none of my neighbors would see it. Then again I could just build a fence around my central ac and my mini.
 
Quote Reply
Page 77 of 119 · Replies 1,521–1,540 of 2,371
Prev
  • 1
  • …
  • 75
  • 76
  • 77
  • 78
  • 79
  • …
  • 119
Next
First Prev 77 of 119 Next Last

Thread info

Replies 2,370
Views 421,633
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • Big Al’s 2025 season indoor/outdoor grow in misery
    • Latest: grayoldnproud
    • 1 minute ago
    Grow Diaries
  • G
    I’m Week 4 into Flowering
    • Latest: greentomatoes2025
    • 21 minutes ago
    General Indoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Beazy
    • Today at 7:06 AM
    General Outdoor Growing
  • 2026 Outdoor Grows! let's see em!
    • Latest: IgnorRayMuss
    • Today at 6:50 AM
    General Outdoor Growing
  • Astro Lemonade F1: Grow Journal By Pot Portraits
    • Latest: RoyalQueenSeeds
    • Today at 6:37 AM
    Grow Diaries
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?