#1,921
Surfr said:
I need 9 tons in a sealed room. I have 6-7k to spend. Suggestions?
Click to expand...

Get another 6-7k or go buy China stuff and install yourself. Unless you have a good hook up on equipment, it will be hard to do.
 
Quote Reply

Cali clouds

Posts
267
Reactions
541
Joined
Mar 27, 2016
Points
93
Sep 12, 2016
#1,922
9 tons of air is a easy 6-7k in equipment if you use decent stuff. 4k for a 5 ton is working for wages. Cheap shit never pays off. I bet you could get 9 tons of China mini splits from a hydro shop for around that price
 
Reactions: Wentworth
Quote Reply

Surfr

Supporter
Just cruisin....
Posts
1,025
Reactions
1,224
Joined
Sep 25, 2010
Points
163
Sep 13, 2016
#1,923
I can upfrade units after a few rounds if I need to. I'm honestly just looking for a few 3 ton mini split units to get me by for now. Any suggestions?
 
Quote Reply

Savage Henry

Posts
960
Reactions
1,717
Joined
Sep 27, 2015
Points
143
Sep 13, 2016
#1,924
@Surfr I have the 1.5ton version of this:
It's been working quite well. Definitely a Chinese unit but has the best warranty I've seen on one (7yrs on the compressor, 5 on parts) it's under $2k and if you pick it up at the shipping distribtor instead of getting the lift gate service it'll save another couple bucks.
 
Reactions: Surfr
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 13, 2016
#1,925
I charge about $4500 for a 5 ton York split system installed. That's minimal mark up. All depends on install. No duct work cause it's not needed in almost all cases.
 
Quote Reply

DemonTrich

Posts
6,394
Reactions
15,047
Joined
Feb 20, 2015
Points
313
Sep 13, 2016
#1,926
Reformatting my room yet again.

I have no place for a mini split.

Currently.i use a 14k btu single hose ac. I have it inside my flower room which uses the cold air to help make.more cold air. I placed it outside the wall to use 79* lung room air and it can't cool my.room enough, so I put it back inside the flower room.

Would a dual hose work better for the option of placing the dual hose in the lung room so it's not sucking out cold air from the flower room?

Basically what in wondering is this,
A single hose uses the cool room air to help the single hose work normally, and sucks out same said cool air out the exhaust . Since a dual hose uses "outside air", can it work like I want it? Dual hose on the other side of the flower room, duct thru wall into flower room. All air in flower room gets recirculating and out scrubber.

I'm not quite sure I typed out how I'm thinking.
 
Quote Reply

MSH

Posts
88
Reactions
52
Joined
May 30, 2015
Points
18
Sep 13, 2016
#1,927
Anyone here know of a store that ships splits internationally? Or maybe just know of a few stores that sell splits and I can check for myself if they ship?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 13, 2016
#1,928
DemonTrich said:
Reformatting my room yet again.

I have no place for a mini split.

Currently.i use a 14k btu single hose ac. I have it inside my flower room which uses the cold air to help make.more cold air. I placed it outside the wall to use 79* lung room air and it can't cool my.room enough, so I put it back inside the flower room.

Would a dual hose work better for the option of placing the dual hose in the lung room so it's not sucking out cold air from the flower room?

Basically what in wondering is this,
A single hose uses the cool room air to help the single hose work normally, and sucks out same said cool air out the exhaust . Since a dual hose uses "outside air", can it work like I want it? Dual hose on the other side of the flower room, duct thru wall into flower room. All air in flower room gets recirculating and out scrubber.

I'm not quite sure I typed out how I'm thinking.
Click to expand...

Double hose should always be better.
 
Reactions: DemonTrich
Quote Reply

DemonTrich

Posts
6,394
Reactions
15,047
Joined
Feb 20, 2015
Points
313
Sep 13, 2016
#1,929
I ran the exact same dual hose in a previous sealed, co2 room (8x12x7) with 3x600 and could barely keep under 77. Ac was inside the room, and did create some neg pressure. Panda walls were sucking in. Not catastrophic, but noticable. No issues from it being like that.
 
Quote Reply

Surfr

Supporter
Just cruisin....
Posts
1,025
Reactions
1,224
Joined
Sep 25, 2010
Points
163
Sep 13, 2016
#1,930
Savage Henry said:
@Surfr I have the 1.5ton version of this:
It's been working quite well. Definitely a Chinese unit but has the best warranty I've seen on one (7yrs on the compressor, 5 on parts) it's under $2k and if you pick it up at the shipping distribtor instead of getting the lift gate service it'll save another couple bucks.
Click to expand...

Funny you mention the MrCool units, I was at a shop yesterday looking at those. I can get three of the 3 ton units out the door for $5400...
 
Quote Reply

Savage Henry

Posts
960
Reactions
1,717
Joined
Sep 27, 2015
Points
143
Sep 13, 2016
#1,931
Nice! Let me know if you figure out how to integrate them into an environmental controller. The wifi-controlled app lets you automatically set it for a night time temp but it only works for 8hrs...
 
Quote Reply

mclovin707

Posts
12
Reactions
12
Joined
Dec 3, 2014
Points
3
Sep 20, 2016
#1,932
Hey guys getting ready to start flowering in my new room. I am currently running 6k double ended ac DE hoods. Running a 100pint dehuey in room. All ballasts are outside the room.

Here's my issue have a brand newmitsubishi 48000 btu mini split with 2 24000 btu indoor units 1 on each side of room. This should be plenty of coolingpower. I did a test run today because itwas about 90 degrees out and wanted to make sure I could get the room ice cold if need be with lights on. This is the first time I have fired up the ac with the lights on. Room spiked up to about 92 degrees.The room is fully sealed and insulated as well as double rock and sound proofed.Has a concrete floor too. I'm beginning towonder if my HVAC guys screwed up on the install. Not enough refrigerant???Any thoughts from an HVAC guy inhere???
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Sep 20, 2016
#1,933
mclovin707 said:
Hey guys getting ready to start flowering in my new room. I am currently running 6k double ended ac DE hoods. Running a 100pint dehuey in room. All ballasts are outside the room.

Here's my issue have a brand newmitsubishi 48000 btu mini split with 2 24000 btu indoor units 1 on each side of room. This should be plenty of coolingpower. I did a test run today because itwas about 90 degrees out and wanted to make sure I could get the room ice cold if need be with lights on. This is the first time I have fired up the ac with the lights on. Room spiked up to about 92 degrees.The room is fully sealed and insulated as well as double rock and sound proofed.Has a concrete floor too. I'm beginning towonder if my HVAC guys screwed up on the install. Not enough refrigerant???Any thoughts from an HVAC guy inhere???
Click to expand...

Bad install. That unit should be able to cool 8-9 kW with no problem (maintain canopy at 78-80F where most people want it)
 
Quote Reply
B

boom21

Posts
10
Reactions
3
Joined
Sep 30, 2016
Points
3
Oct 3, 2016
#1,934
Hey John, Thanks for being so helpful on here. I have a 28x28x10 sealed room with 20 gavitas. I am using 2 separate 5 ton tempstars. I was wondering what the pros/cons of putting the airhandler directly in the room hanging from the ceiling or placing the airhandler on top of the room and ducting the circulating air. I have one room with the airhandlers inside the room already and it seems to be affecting the RH alot compared to my past rooms where I ducted in the air with the airhandlers on top of the rooms. Thanks in advance!
 
Quote Reply

Brandonb

Posts
3
Reactions
2
Joined
Oct 3, 2016
Points
3
Oct 3, 2016
#1,935
Hey john i have a 13×20ft sealed room running 10000w thru 8in vented hoods have one daiken mini split with a heat pump also have a inverter for back up with both condensate lines goin outside problem is my outake is pulling air thru the confensate lines causing a reverse flow of the condensation so instead of it draining outside its leaking from the inside unit into the grow room it also shuts the system off not sure if its shorting the system out or wat i have an 8in outake fan blowing the bad air out side and a intake that is bringing air in from a middle room with no fan on it just a damper the lights are vented by 2 8in inline that are vented out into the middle room and then vented outside the middle room which is just a work space which also has a intake to bring in fresh air so that it releives pressure from the air thats being pulled from the grow room
 
Quote Reply

blazer

Posts
1,759
Reactions
4,809
Joined
Dec 22, 2010
Points
263
Oct 3, 2016
#1,936
Put a P trap on your condensate line that should let the line drain properly
 
Reactions: stonestacker
Quote Reply

Brandonb

Posts
3
Reactions
2
Joined
Oct 3, 2016
Points
3
Oct 3, 2016
#1,937
blazer said:
Put a P trap on your condensate line that should let the line drain properly
Click to expand...
Thank you
 
Reactions: stonestacker and blazer
Quote Reply

Brandonb

Posts
3
Reactions
2
Joined
Oct 3, 2016
Points
3
Oct 4, 2016
#1,938
How do i make a p trap with flex hose the condensate hose is outside will this freeze
 
Quote Reply

Herb Forester

Posts
766
Reactions
1,442
Joined
May 6, 2013
Points
143
Oct 5, 2016
#1,939
mclovin707 said:
Hey guys getting ready to start flowering in my new room. I am currently running 6k double ended ac DE hoods. Running a 100pint dehuey in room. All ballasts are outside the room.

Here's my issue have a brand newmitsubishi 48000 btu mini split with 2 24000 btu indoor units 1 on each side of room. This should be plenty of coolingpower. I did a test run today because itwas about 90 degrees out and wanted to make sure I could get the room ice cold if need be with lights on. This is the first time I have fired up the ac with the lights on. Room spiked up to about 92 degrees.The room is fully sealed and insulated as well as double rock and sound proofed.Has a concrete floor too. I'm beginning towonder if my HVAC guys screwed up on the install. Not enough refrigerant???Any thoughts from an HVAC guy inhere???
Click to expand...
What did you use for soundproofing?
 
Reactions: boom21
Quote Reply

BonMassacre

Posts
13
Reactions
23
Joined
Jun 23, 2016
Points
13
Oct 5, 2016
#1,940
Hello everyone! New here. Setting up my first grow and I want an opinion on portable AC units for a small bedroom? I relatively keep the house at 69 degrees and will be using a grow tent in a room at the front of my house. Worried about my furry little friend invading the grow room, I am opting to keep the door closed but worried about too much heat from the exhaust.
Don't have ability to have the duct hanging out of a window so I am deciding on a portable unit that can fit my budget. Does anyone have experience with 3 in ones? It's an Evaporate cooler that is also a fan and humidifier? I already have a humidifier but keeping the room cool, especially since fall just hit and I will be needing to turn the heat up a bit in the home is making me a bit worried about my first grow.

Provided a link to what I'm talking about... Thanks!
https://www.amazon.com/NewAir-AF-31...1475713311&sr=8-3&keywords=evaporative+cooler
 
Quote Reply
Page 97 of 119 · Replies 1,921–1,940 of 2,371
Prev
  • 1
  • …
  • 95
  • 96
  • 97
  • 98
  • 99
  • …
  • 119
Next
First Prev 97 of 119 Next Last

Thread info

Replies 2,370
Views 421,633
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • 2026 Outdoor Grows! let's see em!
    • Latest: IgnorRayMuss
    • 12 minutes ago
    General Outdoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Hossgrows
    • 20 minutes ago
    General Outdoor Growing
  • Astro Lemonade F1: Grow Journal By Pot Portraits
    • Latest: RoyalQueenSeeds
    • 25 minutes ago
    Grow Diaries
  • F
    First Auto grow gg4
    • Latest: fullyauto
    • Today at 5:08 AM
    Introduce Yourself
  • Blazing heat, smoke-filled skies, illegal! What could possibly go wrong?
    • Latest: Lockebox
    • Today at 4:52 AM
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?