@CannabisJohn got a question for ya good sir.
What size ducting and vent registers should I use in this situation?
5 ton water cooled air handler with a plenum, then a Y and going to two vents. Both runs would be about 10 feet and the only turn would be from the duct to the vent.
I was looking at this for ducting.
http://www.homedepot.com/p/Thermafl...00-0003/203767741?N=5yc1vZc4nu#specifications
Use 18x14x14 tee wye. So 18 inch off of plenum to 2-14 inch ducts