#241
Dr.Trichome said:
Little plywood box round that'll bring up your efficiency lots I'd think. Dats kool man. I like it.
Click to expand...

Huh? Please explain?
 
Quote Reply

Dr.Trichome

Posts
104
Reactions
123
Joined
Dec 11, 2013
Points
43
Dec 13, 2013
#242
That fan is hittin the middle of da rad, cage fan moves lots of air.. back it off and box it in, angled at the sides, and it'll shove lots of air throug the there. The ones they use on a car don't move much compared to that one there. It'll rock that thing.
 
Reactions: ttystikk
Quote Reply

Dr.Trichome

Posts
104
Reactions
123
Joined
Dec 11, 2013
Points
43
Dec 13, 2013
#243
I'll bet with that fan you coukd box two of those rads atleast if ya box em in...
 
Quote Reply

donmekka

Posts
358
Reactions
605
Joined
Sep 17, 2013
Points
93
Dec 14, 2013
#244
Guys could i get some opinions on this chiller

Seems like a good deal ....I think...I don't know much about chillers. Any idea how much lighting it could take care of?
 
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 2, 2014
#245
Ok....got some questions for you waterchilling guys as I am about to start installing my 5 ton Banks. Here goes......................


Would a bigger reservoir create problems or make things more efficient? I do plan on heavily insulating my reservoir either way. I also know that a 55 gallon drum is sufficient. Just curious as to if a 275 IBC tote would be better as I am picking one up for a RO reservoir anyways.

On the return manifold, is it as important to stay away from 90 degree turns as it is with the incoming manifold?

On the incoming manifold, would 45's be suitable, or is spa tubing going to be superior?

Last but not least. The chiller itself will be in an enclosed warehouse. I do plan on having the warehouse vented with an attic fan. Is there a recommended cfm for applications such as this?
 
Quote Reply

twist1

Posts
77
Reactions
56
Joined
Sep 19, 2013
Points
18
Jan 7, 2014
#246
@CelticEBE How are you making out with your install? Were you able to do it yourself? Or have to get a contractor?

Mine came in yesterday. Man, this phucker is BIG! LOL! I hope it's all that they say it is.
 
Reactions: CelticEBE and ftwendy
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 8, 2014
#247
twist1 said:
@CelticEBE How are you making out with your install? Were you able to do it yourself? Or have to get a contractor?

Mine came in yesterday. Man, this phucker is BIG! LOL! I hope it's all that they say it is.
Click to expand...
Its slow but steady. I actually had to frame out a drying room before I started anything else because the manifold will be going over the top of it. On top of all that I will be taking down one of my rooms tomorrow. Should have all the plumbing done fairly soon....made like 5 trips to Home Depot and I still need some stuff. :eek: Not gonna need a contractor.....I've got the skills to do it.....I just need the time.

I decided to go with a IBC tote for the reservoir.....I'm just not going to fill it up all the way. I think there will be benefits to having a larger volume of water.
 
Reactions: ftwendy
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 19, 2014
#248
seebobsled said:
Yes Walmart at about this time a year (fall/winter). 5-7 bucks a gal I think. It has a red dye in it.
Super Tech Rv & marine antifreeze squew number 81131 00234. It's manufactured for Walmart and found in auto or sporting department.
Click to expand...

That stuff is no good, pre diluted you have to use it at 100% but it is still diluted. The freeze point and burst rating is too low. That is obviously outdoors in a cold climate. Typically go to your local HVAC Contractor Supply Co. I pay approx 80 bucks a 5 gal bucket. Pricey but it is the real deal. Picked up 35 gallons this past monday to replace fluid I lost due to a broken ball valve. The whole floor was covered in Glycol, Thank goodness nothing sprayed on the plants, they don't take to it well topically to Glycol. However I had Glycol leak into a cloner from a loose cool coil hose clamp and the clones actually came back. You see blue foam in your cloner and your heart sinks. But on the leaves they will straight up die. Ive spoken to the actual manufacturer of the RV Propylene Glycol products and they don't recommend it unless your in a warmer climate for our equipment specs. Going to be down into the negatives here again this week. Id actually only use that in pure desperation.
 
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 19, 2014
#249
CelticEBE said:
Ok....got some questions for you waterchilling guys as I am about to start installing my 5 ton Banks. Here goes......................


Would a bigger reservoir create problems or make things more efficient? I do plan on heavily insulating my reservoir either way. I also know that a 55 gallon drum is sufficient. Just curious as to if a 275 IBC tote would be better as I am picking one up for a RO reservoir anyways.

On the return manifold, is it as important to stay away from 90 degree turns as it is with the incoming manifold?

On the incoming manifold, would 45's be suitable, or is spa tubing going to be superior?

Last but not least. The chiller itself will be in an enclosed warehouse. I do plan on having the warehouse vented with an attic fan. Is there a recommended cfm for applications such as this?
Click to expand...

My 5t chiller is outdoors, 1.5"x1.5"x1" tee off of the pump to the chiller. Chiller returns to rez with flowmeter, all in spa flex to rez and pump (1-1/2" 1HP) located in the garage, riser to the second floor room location is 2" supply, 1.5" return in spa flex to 90 Degree PVC sch 40 Outlet Elbow to Sch 40 PVC Pipe (Plumbing Supply or online purchase lowes HD doesn't stock that size outlet elbow) each outlet runs to either side of the room with one 90 each to the supply manifolds and the 90 back from the returns obviously following the same route. I could have gotten away with one 90 but I wanted the coils in my veg and cloner 35 feet away on an opposing corner.
Seems to work just fine I'm running 20 GPM on my flowmeter solid. Had to replace flow switch, died not letting the circuit to close. Sucked cuz I just topped off rez with newly purchased glycol. Wasn't too messy though. Had some slow trickle leaks using teflon tape, should have used more or just went with the pipe thread compound off the bat. Most threaded connections I changed over to the compound since. I will take some picks of the tubing run one day. May also need a heat gun to get that spa flex over those large barbed fittings. Still trying to find my sweet spot with the chiller temp. I ran the air handler and the chiller temp wasn't set low enough so my coils went to 70-73f. wasn't happy about that.
 
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 19, 2014
#250
Delerium said:
My 5t chiller is outdoors, 1.5"x1.5"x1" tee off of the pump to the chiller. Chiller returns to rez with flowmeter, all in spa flex to rez and pump (1-1/2" 1HP) located in the garage, riser to the second floor room location is 2" supply, 1.5" return in spa flex to 90 Degree PVC sch 40 Outlet Elbow to Sch 40 PVC Pipe (Plumbing Supply or online purchase lowes HD doesn't stock that size outlet elbow) each outlet runs to either side of the room with one 90 each to the supply manifolds and the 90 back from the returns obviously following the same route. I could have gotten away with one 90 but I wanted the coils in my veg and cloner 35 feet away on an opposing corner.
Seems to work just fine I'm running 20 GPM on my flowmeter solid. Had to replace flow switch, died not letting the circuit to close. Sucked cuz I just topped off rez with newly purchased glycol. Wasn't too messy though. Had some slow trickle leaks using teflon tape, should have used more or just went with the pipe thread compound off the bat. Most threaded connections I changed over to the compound since. I will take some picks of the tubing run one day. May also need a heat gun to get that spa flex over those large barbed fittings. Still trying to find my sweet spot with the chiller temp. I ran the air handler and the chiller temp wasn't set low enough so my coils went to 70-73f. wasn't happy about that.
Click to expand...

Should have everything up and running here in a couple of days now. I actually just glued the spa flex to the pvc. I thought about barb fittings but a plumber buddy of mine told me that using pvc glue would work so....
 
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 19, 2014
#251
CelticEBE said:
Should have everything up and running here in a couple of days now. I actually just glued the spa flex to the pvc. I thought about barb fittings but a plumber buddy of mine told me that using pvc glue would work so....
Click to expand...

Awesome Celtic.
2 Chillers in series over a larger rez. U had asked about using larger rez before.
Spa Flex is sch 40 PVC but only flexible same O.D., the stuff rocks because you can use the same exact fittings for either one. (for the non-proffesional plumbers such as myself) I came this close to using glue. Glue is better imo less threaded fittings the better. I used the flex to get it going until i have time to make an uber plumbing setup with all unions.
I was awoken to a weird sound one night at 4AM. A weird sucking sound. Thought it was the dosers out of whack just continually dosing. I inspected it and found a cracked ball valve. My fault overtightened but that one was expensive, dumped an estimated 500+ dollars of glycol all over my room floor.
 
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 19, 2014
#252
Delerium said:
Awesome Celtic.
2 Chillers in series over a larger rez. U had asked about using larger rez before.
Spa Flex is sch 40 PVC but only flexible same O.D., the stuff rocks because you can use the same exact fittings for either one. (for the non-proffesional plumbers such as myself) I came this close to using glue. Glue is better imo less threaded fittings the better. I used the flex to get it going until i have time to make an uber plumbing setup with all unions.
I was awoken to a weird sound one night at 4AM. A weird sucking sound. Thought it was the dosers out of whack just continually dosing. I inspected it and found a cracked ball valve. My fault overtightened but that one was expensive, dumped an estimated 500+ dollars of glycol all over my room floor.
Click to expand...

Damn....that's a hefty spill. I'm in SoCal and it never freezes here, plus everything will be indoors so I am running just a little bit of glycol as "lubricant" for the pump as HI said. I also changed my mind on the IBC tote and decided to go with a 100 gallon reservoir instead. I will post some pics once I have everything installed.
 
Reactions: fishwhistle
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 19, 2014
#253
Sounds like a plan, chiller indoors or just the rez?
 
Quote Reply
S

seebobsled

Posts
266
Reactions
152
Joined
Oct 5, 2010
Points
43
Jan 20, 2014
#254
Delerium said:
That stuff is no good, pre diluted you have to use it at 100% but it is still diluted. The freeze point and burst rating is too low. That is obviously outdoors in a cold climate. Typically go to your local HVAC Contractor Supply Co. I pay approx 80 bucks a 5 gal bucket. Pricey but it is the real deal. Picked up 35 gallons this past monday to replace fluid I lost due to a broken ball valve. The whole floor was covered in Glycol, Thank goodness nothing sprayed on the plants, they don't take to it well topically to Glycol. However I had Glycol leak into a cloner from a loose cool coil hose clamp and the clones actually came back. You see blue foam in your cloner and your heart sinks. But on the leaves they will straight up die. Ive spoken to the actual manufacturer of the RV Propylene Glycol products and they don't recommend it unless your in a warmer climate for our equipment specs. Going to be down into the negatives here again this week. Id actually only use that in pure desperation.
Click to expand...

You are right !
but fine for warmer weather. I average 40deg but can dip to 30 sometimes over night. Moving water has a harder time to freeze. No problems for me.
 
Reactions: Delerium
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 20, 2014
#255
seebobsled said:
You are right !
but fine for warmer weather. I average 40deg but can dip to 30 sometimes over night. Moving water has a harder time to freeze. No problems for me.
Click to expand...

Exactly, and it is a hell of a lot cheaper and more readily available.
 
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 21, 2014
#256
Delerium said:
Sounds like a plan, chiller indoors or just the rez?
Click to expand...
Chiller is indoor. It's in a 1000sqft space and I will be hooking up a 4500cfm attic fan for ventilation. I finished plumbing tonight, but I have to make a Home Depot trip because I got the wrong breakers. I swear I should buy stock in that place.
 
Reactions: aSilvrHaze, twist1 and stonestacker
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 22, 2014
#257
Wooo hoooo!!! Got er up and running! I managed to chill 100 gallons in the time it took me to insulate the tank. Had one faulty nipple and one loose connection so I'd say I did pretty good with the plumbing. 5 ton air handlers ROCK! My flowmeter is pegged out.....so stoked.
 
Reactions: aSilvrHaze and Delerium
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 22, 2014
#258
CelticEBE said:
Wooo hoooo!!! Got er up and running! I managed to chill 100 gallons in the time it took me to insulate the tank. Had one faulty nipple and one loose connection so I'd say I did pretty good with the plumbing. 5 ton air handlers ROCK! My flowmeter is pegged out.....so stoked.
Click to expand...


Say goodbye to root rot.

I'm a mini Hardware store. Have way to much shit. I'd rather spend 2 bucks on a fitting than have to be screwed at 2 AM.
 
Reactions: CelticEBE
Quote Reply

CelticEBE

Posts
1,831
Reactions
2,711
Joined
Feb 11, 2010
Points
263
Jan 22, 2014
#259
Delerium said:
Say goodbye to root rot.

I'm a mini Hardware store. Have way to much shit. I'd rather spend 2 bucks on a fitting than have to be screwed at 2 AM.
Click to expand...
I'm actually a Coco drain to waste guy......I went with the 5 ton water chiller and air handlers because it was my best option as far as cooling two 8k rooms on a flip, my veg room, and a drying room. I could not have done this with traditional hvac and the power that I have.
 
Reactions: Burned Haze, fishwhistle, aSilvrHaze and 2 others
Quote Reply

Delerium

Posts
783
Reactions
754
Joined
Jan 18, 2014
Points
93
Jan 25, 2014
#260
A Pair of hose clamps sure make a difference. Unions and glue!
 
Quote Reply
Page 13 of 20 · Replies 241–260 of 387
Prev
  • 1
  • …
  • 11
  • 12
  • 13
  • 14
  • 15
  • …
  • 20
Next
First Prev 13 of 20 Next Last

Thread info

Replies 386
Views 65,654
Started Jun 22, 2013
Latest post Feb 23, 2024
Starter ttystikk
Forum Advanced Techniques & Problems

Latest posts

  • 2026 Outdoor Grows! let's see em!
    • Latest: EternalSun
    • 9 minutes ago
    General Outdoor Growing
  • J
    1 hitter gummy Skunk it's fire
    • Latest: jrock67
    • 42 minutes ago
    Grow Diaries
  • J
    Is it ready to harvest
    • Latest: josh65
    • 51 minutes ago
    Photography Help
  • how to Bubble washing and tips 2024
    • Latest: Oldchucky
    • 57 minutes ago
    Concentrates & Processing
  • NYC Piff #3 grow from The Clone Conservatory searching for the NYC Haze
    • Latest: GNick55
    • Today at 1:16 PM
    Grow Diaries
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Advanced Techniques & Problems
  • Water Chilling Q & A
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?