CannabisJohn said:
That's a great idea but he still needs cooling.
Click to expand...
Im sorry i was not specific He sells any part of systems, I bought just the mechanical, compressor / evaporator, fans ducting etc. I do not have the insulated "room" i mentioned. the cooler... works great
6 ton capacity, i believe, without looking.. anyway works great for me. good luck
 
Quote Reply

treereek

Posts
20
Reactions
4
Joined
Feb 27, 2010
Points
3
Jan 13, 2015
#1,062
So it doesn't dehumidify? It just cools and humidify? Would love to see pix.
 
Quote Reply
S

Swerv

Posts
4
Joined
Jan 11, 2015
Points
1
Jan 14, 2015
#1,063
CannabisJohn said:
Yes you can get multizone minis. I would do a 3 ton which is the biggest reasonably priced option or do a regular residential 4 ton unit with zone controls. Either way get it professionally installed. The residential unit gives a little cushion on cooling.
Click to expand...
Thanks for the responses guys, much appreciated.
Taking it further, you said "cushion" by that do you mean that the 3 ton may have to be overworked to keep the zone cool. If so/not so does the mini splits or the residential end up being the better option. Rarely (like maybe 10 times a year) does this area see temps above 80 degrees as the highs and the lights would be primarily on during night time hours 7 pm 7 am for flower and the veg on from 6 pm to 12pm. Cost is kind of a factor and I like the smaller footprint of the minis.
If I go the mini rout, I have been kicking around the idea of re-configuring my rooms and possibley just running one room 12x20 with 10 of the 600s and a smaller 4x8 with the last 600. Do yall think that a 3 ton mini would "like" cooling a zone set up that way verses trying to get a mini with dual zone and trying to cool the situation I described in my previous question ?

Was thinking professional installation from the get go...

Thanks again ... Awesome thread :)
 
Quote Reply

dankninja

Posts
486
Reactions
621
Joined
Sep 29, 2014
Points
93
Jan 15, 2015
#1,064
howdy. tryin to cool a vertitube I built, 2 1K hids, and I have a room ac I have converted to accept 6" ducting. any possible fatigue/expansion/damage from this kind of setup cooling the cooltubes? everyone else uses fans...... I've never personally cooled a hot hid bulb with an air conditioner, just curious if I'm gonna cause a fire etc. thanks
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 16, 2015
#1,065
Swerv said:
Thanks for the responses guys, much appreciated.
Taking it further, you said "cushion" by that do you mean that the 3 ton may have to be overworked to keep the zone cool. If so/not so does the mini splits or the residential end up being the better option. Rarely (like maybe 10 times a year) does this area see temps above 80 degrees as the highs and the lights would be primarily on during night time hours 7 pm 7 am for flower and the veg on from 6 pm to 12pm. Cost is kind of a factor and I like the smaller footprint of the minis.
If I go the mini rout, I have been kicking around the idea of re-configuring my rooms and possibley just running one room 12x20 with 10 of the 600s and a smaller 4x8 with the last 600. Do yall think that a 3 ton mini would "like" cooling a zone set up that way verses trying to get a mini with dual zone and trying to cool the situation I described in my previous question ?

Was thinking professional installation from the get go...

Thanks again ... Awesome thread :)
Click to expand...

Yes cushion is extra cooling. Based upon your daytime highs, 3 tons should be plenty if ur room is insulated properly. A dual zone unit is a lot more cost.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 16, 2015
#1,066
dankninja said:
howdy. tryin to cool a vertitube I built, 2 1K hids, and I have a room ac I have converted to accept 6" ducting. any possible fatigue/expansion/damage from this kind of setup cooling the cooltubes? everyone else uses fans...... I've never personally cooled a hot hid bulb with an air conditioner, just curious if I'm gonna cause a fire etc. thanks
Click to expand...

The a/c will probably work hard but shouldn't be a fire or anything like that. Only problem I see is the a/c thermostat is in the unit. Are u installing some other controller to control a/c?
 
Quote Reply
S

Swerv

Posts
4
Joined
Jan 11, 2015
Points
1
Jan 16, 2015
#1,067
CannabisJohn said:
Yes cushion is extra cooling. Based upon your daytime highs, 3 tons should be plenty if ur room is insulated properly. A dual zone unit is a lot more cost.
Click to expand...
Copy copy... Bet you can guess my next question lol...can you recommend a solid 3 ton single zone mini ? Thanks for the help
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 17, 2015
#1,068
Swerv said:
Copy copy... Bet you can guess my next question lol...can you recommend a solid 3 ton single zone mini ? Thanks for the help
Click to expand...

Mitshubushi Mr Slim.
 
Quote Reply
T

Tylrr420

Posts
113
Reactions
85
Joined
Nov 15, 2014
Points
28
Jan 28, 2015
#1,069
Hey CJ. Wow there is a ton of awesome info on this thread. I'm sure I missed it somewhere... But I was wondering if there is a simple rule of thumb for how many btu is required for 1k light vented vs 1k light unvented. For example I have a 36 btu aura and am currently running 6k vented no prob. I want to add 3 600 OR 1000s (if possible) verticals. Also I seen that u said minisplits will run 15 degrees and lower. Should I keep on the forecast and shut my minisplit off I see temps below 15? Could it fuck my condenser up if it gets to cold and I leave it on? ( I have a portable that keeps up in winter but I don't like using it as it is an energy hog.) also auras website says it will cool 8k of lights but doesn't mention if that's barebulb or not
 
Quote Reply
J

JMiller420

Posts
5
Joined
Jan 28, 2015
Points
1
Jan 28, 2015
#1,070
CannabisJohn said:
Well it appears that my thread disappeared from the forum during the server change. So here goes a new one. Ask away about your grow room a/c questions.
Click to expand...

Hey man hows it going, im trying to build out a flowering chamber but im trying to figure out how much space the chamber should have and how much ac i should be using in order to keep it at the right temperature(76 -78 degrese F is what im shooting for),. if you could give me the right dementions for a 4 light ,6 light and 8 light flowering chamber in order to keep it at the right temp it would be super helpful and greatly appreciated,.. im going for 2 week veg (veg room is seperate) then scroging it in the flowering chamber ,going to be using 1000 watt hps open(no lense) hoods each light will be covering a 4x4 area...also should i use ventalation on the hoods if theres no lense?thanks very much for your time ,the help is needed and appreciated !
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 28, 2015
#1,071
Tylrr420 said:
Hey CJ. Wow there is a ton of awesome info on this thread. I'm sure I missed it somewhere... But I was wondering if there is a simple rule of thumb for how many btu is required for 1k light vented vs 1k light unvented. For example I have a 36 btu aura and am currently running 6k vented no prob. I want to add 3 600 OR 1000s (if possible) verticals. Also I seen that u said minisplits will run 15 degrees and lower. Should I keep on the forecast and shut my minisplit off I see temps below 15? Could it fuck my condenser up if it gets to cold and I leave it on? ( I have a portable that keeps up in winter but I don't like using it as it is an energy hog.) also auras website says it will cool 8k of lights but doesn't mention if that's barebulb or not
Click to expand...

4000 btus per hour for 1k of vented lights and 6000 for 1k unvented is what I use. Your unit can run under any temperture but it will have cooling issues below what ever temp its designed to run.
 
Reactions: fishwhistle
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 28, 2015
#1,072
JMiller420 said:
Hey man hows it going, im trying to build out a flowering chamber but im trying to figure out how much space the chamber should have and how much ac i should be using in order to keep it at the right temperature(76 -78 degrese F is what im shooting for),. if you could give me the right dementions for a 4 light ,6 light and 8 light flowering chamber in order to keep it at the right temp it would be super helpful and greatly appreciated,.. im going for 2 week veg (veg room is seperate) then scroging it in the flowering chamber ,going to be using 1000 watt hps open(no lense) hoods each light will be covering a 4x4 area...also should i use ventalation on the hoods if theres no lense?thanks very much for your time ,the help is needed and appreciated !
Click to expand...

I don't do room sizing. But I recommend 6000 btus per hour per 1k unvented lights. So 4 lights need 2 tons of cooling, 6 lights need 3 tons, and 8 lights need 4 tons.
 
Reactions: mauiinfinity, TeterPosh and fishwhistle
Quote Reply
J

JMiller420

Posts
5
Joined
Jan 28, 2015
Points
1
Jan 28, 2015
#1,073
CannabisJohn said:
I don't do room sizing. But I recommend 6000 btus per hour per 1k unvented lights. So 4 lights need 2 tons of cooling, 6 lights need 3 tons, and 8 lights need 4 tons.
Click to expand...
thanks a lot for the info!,..and the size of the room dosnt effect the temp? example,.. would a 6 light setup in a 15x20 be harder to get the right temp then a 6 light setup in a 20x25?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 29, 2015
#1,074
JMiller420 said:
thanks a lot for the info!,..and the size of the room dosnt effect the temp? example,.. would a 6 light setup in a 15x20 be harder to get the right temp then a 6 light setup in a 20x25?
Click to expand...

Bigger room a bit harder to cool but I have enough room in my calculations for either size IMO.
 
Reactions: Frostynugman
Quote Reply
J

JMiller420

Posts
5
Joined
Jan 28, 2015
Points
1
Jan 29, 2015
#1,075
thanks a lot man!
 
Quote Reply
J

JMiller420

Posts
5
Joined
Jan 28, 2015
Points
1
Jan 29, 2015
#1,076
CannabisJohn said:
Bigger room a bit harder to cool but I have enough room in my calculations for either size IMO.
Click to expand...
got another quick one for ya haha,.. theres a lot of ceiling hieght ,..if i were to build 2 chambers 1 stacked on top of the other would that effect the heat in one chamber or the other at all?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 30, 2015
#1,077
JMiller420 said:
got another quick one for ya haha,.. theres a lot of ceiling hieght ,..if i were to build 2 chambers 1 stacked on top of the other would that effect the heat in one chamber or the other at all?
Click to expand...

The higher u go the hotter it is.
 
Quote Reply

dankninja

Posts
486
Reactions
621
Joined
Sep 29, 2014
Points
93
Jan 30, 2015
#1,078
CannabisJohn said:
The a/c will probably work hard but shouldn't be a fire or anything like that. Only problem I see is the a/c thermostat is in the unit. Are u installing some other controller to control a/c?
Click to expand...
it has a thermostat in unit, and a timer, I would add a controller to it, but worried about the gfci on the ac plug. If it doesnt work up to spec ill just do two 6" centrifugals
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Jan 30, 2015
#1,079
dankninja said:
it has a thermostat in unit, and a timer, I would add a controller to it, but worried about the gfci on the ac plug. If it doesnt work up to spec ill just do two 6" centrifugals
Click to expand...

Won't work properly without proper zoning controls.
 
Quote Reply

dexfarm

Posts
53
Reactions
54
Joined
Oct 18, 2014
Points
18
Jan 31, 2015
#1,080
Hey CJ, just wondering with your 6000 btu per 1000 watt light calculation, does that include the ballast in the room or not? And if so how much will that number reduce to if ballasts were outside room? And also what about co2 generation, was that factored in the equation? Using tanks would not increase btu requirements i would think.
Thanks for all the info on this thread, i tried to find the answers reading as much as i can here but 54 pages takes me a while.
Cheers
 
Quote Reply
Page 54 of 119 · Replies 1,061–1,080 of 2,371
Prev
  • 1
  • …
  • 52
  • 53
  • 54
  • 55
  • 56
  • …
  • 119
Next
First Prev 54 of 119 Next Last

Thread info

Replies 2,370
Views 421,640
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • 40 days into cure , no change in smell or flavor
    • Latest: WinJr63
    • 1 minute ago
    Cannabis Infirmary
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Leste
    • 12 minutes ago
    General Outdoor Growing
  • S
    Any tips for my first guerilla grow?
    • Latest: SenshiGrows
    • 13 minutes ago
    General Outdoor Growing
  • Strainshow is back
    • Latest: Strainshow2.0
    • 24 minutes ago
    Introduce Yourself
  • Blazing heat, smoke-filled skies, illegal! What could possibly go wrong?
    • Latest: Oldchucky
    • 46 minutes ago
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?