Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Apr 24, 2015
#1,321
Have your tech get these readings. This will make things more clear.
https://farm4.staticinvalid.com/3213/2900913505_64df73c316_o_d.jpg
 
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Apr 24, 2015
#1,322
Og Gong said:
Have your tech get these readings. This will make things more clear.
Click to expand...
 
Reactions: blazer
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
Apr 24, 2015
#1,323
If your unit uses a sporlan TXV there have been issues with it failing with R410a refrigerant systems.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 24, 2015
#1,324
Offdarips said:
We are using the sman 3 gauges they were reading 500 microns
Click to expand...

Did it hold when pump wasn't on and isolated from system for at least 5 mins?
 
Quote Reply
R

Rollin4rese

Posts
9
Reactions
5
Joined
Dec 4, 2014
Points
3
Apr 24, 2015
#1,325
Didn't see the original thread on this. But can say I am soaking up all the info I can.......I have a 6k air cooled fully sealed 336 sq ft room I have been using 14000 btu portable ac and in order to keep the room between 70 and 75 degrees I have to set my ac at least 10 degrees below that and it runs close to none stop. I would like to use co2 but don't want the ac to run like this. so I planned on purchasing another and adding it to see if that will help. But as I read into the issue I'm feeling portable ac's just don't have what it takes. I am renting my place so changing circuits for a mini split is a lot, and may be out of my financial reach. seems a window mount is the best option at this point. Have a window available but am being told I can build a box to avoid compromising security. Trying to figure out if this is true and effective.
 
Reactions: Frostynugman
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 24, 2015
#1,326
Rollin4rese said:
Didn't see the original thread on this. But can say I am soaking up all the info I can.......I have a 6k air cooled fully sealed 336 sq ft room I have been using 14000 btu portable ac and in order to keep the room between 70 and 75 degrees I have to set my ac at least 10 degrees below that and it runs close to none stop. I would like to use co2 but don't want the ac to run like this. so I planned on purchasing another and adding it to see if that will help. But as I read into the issue I'm feeling portable ac's just don't have what it takes. I am renting my place so changing circuits for a mini split is a lot, and may be out of my financial reach. seems a window mount is the best option at this point. Have a window available but am being told I can build a box to avoid compromising security. Trying to figure out if this is true and effective.
Click to expand...

Window units can let smell out. A window unit is an easy way for a thief to enter.
 
Quote Reply
R

Rollin4rese

Posts
9
Reactions
5
Joined
Dec 4, 2014
Points
3
Apr 24, 2015
#1,327
the window is covered as I have build a room inside of a room, I thought that would be helpful in terms of not being so easy to get through. And I am scrubbing my room with 2 6 inch carbon filters . But know I far from got this down and would like to avoid any problems the best I can. Do you know about building a box for a window unit does that work. And if you have any suggestion please shoot em my way.
 
Quote Reply

EMC2

Posts
60
Reactions
34
Joined
Dec 28, 2012
Points
18
May 1, 2015
#1,328
Hey there,

About to start construction on my second project and had a few questions in regards to using strictly chiller units for my cooling needs.

Room A runs 45' x 16' x 12'

This room will have 24x 1000W DE Gavitas. It will also have 8x 250w or 300w plasmas in 3 months. Room will be split down the middle (45' x 8' x 12') and there will be 8 plants per side.

Room B runs 38' x 21' x 12' ( this room is adjacent to Room A)

This room will have 12x 1000W DE Gavitas + 4x 300W plasmas.

The plan is to get 2x 10-ton compressors along with 3x air handlers.

1x 10-ton compressor + 2x air handlers for Room A
1x 10-ton compressor + 1x air handler for Room B

Will this be enough to handle my rooms?
Would it be better to make this an all-in-one loop or to separate the systems unique to only one room?
Is having narrow rooms (mostly Room A) beneficial to more efficient cooling?
My ceilings are actually 15', is the ceiling height better to stay at 12' or should I go all the way to the top at 15'?

Thank you!!
 
Quote Reply

EMC2

Posts
60
Reactions
34
Joined
Dec 28, 2012
Points
18
May 1, 2015
#1,329
Air handlers are each 5-ton
 
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
May 1, 2015
#1,330
EMC2 said:
Hey there,

About to start construction on my second project and had a few questions in regards to using strictly chiller units for my cooling needs.

Room A runs 45' x 16' x 12'

This room will have 24x 1000W DE Gavitas. It will also have 8x 250w or 300w plasmas in 3 months. Room will be split down the middle (45' x 8' x 12') and there will be 8 plants per side.

Room B runs 38' x 21' x 12' ( this room is adjacent to Room A)

This room will have 12x 1000W DE Gavitas + 4x 300W plasmas.

The plan is to get 2x 10-ton compressors along with 3x air handlers.

1x 10-ton compressor + 2x air handlers for Room A
1x 10-ton compressor + 1x air handler for Room B

Will this be enough to handle my rooms?
Would it be better to make this an all-in-one loop or to separate the systems unique to only one room?
Is having narrow rooms (mostly Room A) beneficial to more efficient cooling?
My ceilings are actually 15', is the ceiling height better to stay at 12' or should I go all the way to the top at 15'?

Thank you!!
Click to expand...
If I were to use a chiller like that it is always best to have a backup system. I would use a primary chiller to do all 3 air handlers and have a back up in case that unit fails.
 
Reactions: EMC2
Quote Reply

KtidyFarms

Posts
57
Reactions
72
Joined
Feb 22, 2015
Points
18
May 1, 2015
#1,331
I'd do the loop as an all in one, you'll have an extra 5 tons of cooling but if one unit goes down you'll still be able to give both rooms some cooling. Chillers are awesome kinda like having an inverter driven system since your unused cooling is returned to the system instead of being wasted. Just my 2 cents.
 
Reactions: EMC2 and Og Gong
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 2, 2015
#1,332
EMC2 said:
Hey there,

About to start construction on my second project and had a few questions in regards to using strictly chiller units for my cooling needs.

Room A runs 45' x 16' x 12'

This room will have 24x 1000W DE Gavitas. It will also have 8x 250w or 300w plasmas in 3 months. Room will be split down the middle (45' x 8' x 12') and there will be 8 plants per side.

Room B runs 38' x 21' x 12' ( this room is adjacent to Room A)

This room will have 12x 1000W DE Gavitas + 4x 300W plasmas.

The plan is to get 2x 10-ton compressors along with 3x air handlers.

1x 10-ton compressor + 2x air handlers for Room A
1x 10-ton compressor + 1x air handler for Room B

Will this be enough to handle my rooms?
Would it be better to make this an all-in-one loop or to separate the systems unique to only one room?
Is having narrow rooms (mostly Room A) beneficial to more efficient cooling?
My ceilings are actually 15', is the ceiling height better to stay at 12' or should I go all the way to the top at 15'?

Thank you!!
Click to expand...

Bring ceilings down to 12 ft. To run Room A at full power (1150 watts per light) I recommend 15 tons. For Room B at full power I recommend about 7.5 tons. I would do multiple units per room (room A do maybe a 10 ton and a 5 ton, or 3- 5 ton units and room B do 2-4 ton units). I recommend this so there is some redundancy and multiple air handlers to handle long rooms. If one unit goes down the whole room doesn't. Also cost of 2- 5 ton units should be less than a 10 ton even with install cost.
 
Reactions: EMC2 and Og Gong
Quote Reply

EMC2

Posts
60
Reactions
34
Joined
Dec 28, 2012
Points
18
May 3, 2015
#1,333
CannabisJohn said:
Bring ceilings down to 12 ft. To run Room A at full power (1150 watts per light) I recommend 15 tons. For Room B at full power I recommend about 7.5 tons. I would do multiple units per room (room A do maybe a 10 ton and a 5 ton, or 3- 5 ton units and room B do 2-4 ton units). I recommend this so there is some redundancy and multiple air handlers to handle long rooms. If one unit goes down the whole room doesn't. Also cost of 2- 5 ton units should be less than a 10 ton even with install cost.
Click to expand...

Thank you kind sir
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 3, 2015
#1,334
EMC2 said:
Thank you kind sir
Click to expand...

If need anything else (such as pricing for equipment and / or install) PM me.
 
Reactions: EMC2
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
May 3, 2015
#1,335
What size dual zone mini split would be appropriate for two 4k rooms on a flip flop? I figure I probably need a 24,000btu heat exchanger in each room, and then a 3 ton unit outside? I've never deal with mini splits before. :/
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 3, 2015
#1,336
bibbles said:
What size dual zone mini split would be appropriate for two 4k rooms on a flip flop? I figure I probably need a 24,000btu heat exchanger in each room, and then a 3 ton unit outside? I've never deal with mini splits before. :/
Click to expand...

As far as I know you can't do that with a 3 ton mini. I agree with 24k per room. So you have 2 choices: do 2 separate units or do a residential 4 ton with proper zoning controls.
 
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
May 3, 2015
#1,337
CannabisJohn said:
As far as I know you can't do that with a 3 ton mini. I agree with 24k per room. So you have 2 choices: do 2 separate units or do a residential 4 ton with proper zoning controls.
Click to expand...
A residential unit would be one of those in-attic, ducted ones, right? And what sort of zoning controls would be needed?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 3, 2015
#1,338
bibbles said:
A residential unit would be one of those in-attic, ducted ones, right? And what sort of zoning controls would be needed?
Click to expand...

Your HVAC guy will know what zoning controls you need (controller, tstats, zone dampers).
 
Quote Reply

Og Gong

Rip Geologic
Posts
1,973
Reactions
6,604
Joined
Mar 27, 2015
Points
263
May 3, 2015
#1,339
bibbles said:
A residential unit would be one of those in-attic, ducted ones, right? And what sort of zoning controls would be needed?
Click to expand...
I would go with a dual zone mini spilt hp 4ton. Only use 1 condenser.
http://www.thermospace.com/ductless_split/ymgi/dual-zone-48000-btu-heat-pump.php
 
Reactions: bibbles
Quote Reply

bibbles

Posts
213
Reactions
105
Joined
Jan 7, 2014
Points
43
May 3, 2015
#1,340
Og Gong said:
I would go with a dual zone mini spilt hp 4ton. Only use 1 condenser.
http://www.thermospace.com/ductless_split/ymgi/dual-zone-48000-btu-heat-pump.php
Click to expand...
That looks good, though the BTU recommendations I'm seeing related to mini splits appear to be lower than those for window units? 24,000 seemed pretty standard, but I'm seeing a lot of people saying 24,000 for six lights, and 18,000 for four when it comes to mini splits.
 
Quote Reply
Page 67 of 119 · Replies 1,321–1,340 of 2,371
Prev
  • 1
  • …
  • 65
  • 66
  • 67
  • 68
  • 69
  • …
  • 119
Next
First Prev 67 of 119 Next Last

Thread info

Replies 2,370
Views 421,633
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • 2026 Outdoor Grows! let's see em!
    • Latest: IgnorRayMuss
    • 14 minutes ago
    General Outdoor Growing
  • Cpurola's Outdoor grow in Southeast Michigan 2026
    • Latest: Hossgrows
    • 22 minutes ago
    General Outdoor Growing
  • Astro Lemonade F1: Grow Journal By Pot Portraits
    • Latest: RoyalQueenSeeds
    • 27 minutes ago
    Grow Diaries
  • F
    First Auto grow gg4
    • Latest: fullyauto
    • Today at 5:08 AM
    Introduce Yourself
  • Blazing heat, smoke-filled skies, illegal! What could possibly go wrong?
    • Latest: Lockebox
    • Today at 4:52 AM
    General Outdoor Growing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?