#161
BrosephStalin said:
Ok thanks a lot, If need be I'll just run 6k. So mount it to blow the length of the room. So does 2 6" high output can-fans mounted on the ceiling pointed towards the opposite wall sound about right to circulate the air? Thanks again man for the help.
Click to expand...

Not sure if fans will work for sure but I believe they will be okay. Try it for a few hours before you put plants in there.
 
Quote Reply

outwest

Supporter
Premium Gardener
Posts
4,629
Reactions
10,152
Joined
Dec 10, 2011
Points
263
May 2, 2012
#162
outwest said:
Got my Danby portable AC today. Setup was super easy. Keeping the AC at 72 keeps the tent at 77. I'm struggling with my own humidity which sucks. I think I just need to get the humidifier more directly into the tent intake. The AC dropped the RH from 55 to 45. I start flowering on Friday, so it should be ok.

outwest
Click to expand...

I forgot to add. . .thanks for all the advice!

outwest
 
Quote Reply

sgt. schultz

Posts
282
Reactions
70
Joined
Feb 19, 2009
Points
28
May 8, 2012
#163
Any real world projected btu's per 1000w plus ambient temp in Deep South? All these spoiled Northern Cali people only guessing in Florida/Georgia area which they are under estimating, I'm sure. Hard to rationalize 11o degrees with 95%RH unless you've been there. 2x1000 with bat wings in 10x10 flower 11ft high and 5x8x11 veg with 400 plus several t-5's in brutal conditions until October at least with fiberglass insulation 3.5". CO2 with sensor from bottles to need 80-84 degrees target range I reckon. CO2 neccessity here in exchange for 6-10 degrees a/c. Is 3 ton enough? Also, unit is the type with compressor outside that has furnace and blower inside from office building. Furnace not neccessary. Thinking put furnace/blower inside flower room with large enough vent to keep veg room 78-80. Hoping that setting furnace/blower unit with return inside flower room keeps CO2 circulating to flower and veg. Do I need to put furnace/blower outside room with return inside room? Sorry for windy question.
 
Quote Reply

500lbs Guerilla

Posts
334
Reactions
273
Joined
Aug 9, 2009
Points
63
May 9, 2012
#164
CJ - I've got a question for ya. Instead of purchasing a 4ton min split, I found 2 dual zone LG 2ton splits for a great price. They were used for only a few months, receipts and all. However all the lines were cut and I need to replace the linesets as well as recharge the units. LG's website specs show 1/4" liquid line and 3/8" gas line is required. I'm looking at purchasing the linesets from Total Home Supply, which is 1/4" liquid, 3/8" suction, and 1/2" insulation. I'm also assuming the entire unit will need to be recharged, as the lines aren't precharged.
Does this sound right to you, or are there other options? Anything else I should stay aware of? I've never dealt with used mini splits before.

LG outdoor unit LMU247HV
LG indoor unit LMN126HVT
Lineset I'm looking at THS14381230FN
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 9, 2012
#165
sgt. schultz said:
Any real world projected btu's per 1000w plus ambient temp in Deep South? All these spoiled Northern Cali people only guessing in Florida/Georgia area which they are under estimating, I'm sure. Hard to rationalize 11o degrees with 95%RH unless you've been there. 2x1000 with bat wings in 10x10 flower 11ft high and 5x8x11 veg with 400 plus several t-5's in brutal conditions until October at least with fiberglass insulation 3.5". CO2 with sensor from bottles to need 80-84 degrees target range I reckon. CO2 neccessity here in exchange for 6-10 degrees a/c. Is 3 ton enough? Also, unit is the type with compressor outside that has furnace and blower inside from office building. Furnace not neccessary. Thinking put furnace/blower inside flower room with large enough vent to keep veg room 78-80. Hoping that setting furnace/blower unit with return inside flower room keeps CO2 circulating to flower and veg. Do I need to put furnace/blower outside room with return inside room? Sorry for windy question.
Click to expand...


It's called a split system. I would use 7000-7500 btus per 1 kw of light which would mean u need a 15,000 or so for flower room and maybe an additional 6-9000 for veg room. So I believe a 2 ton should be good. If you oversize too much then it will cycle too much which is bad.
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 9, 2012
#166
500lbs Guerilla said:
CJ - I've got a question for ya. Instead of purchasing a 4ton min split, I found 2 dual zone LG 2ton splits for a great price. They were used for only a few months, receipts and all. However all the lines were cut and I need to replace the linesets as well as recharge the units. LG's website specs show 1/4" liquid line and 3/8" gas line is required. I'm looking at purchasing the linesets from Total Home Supply, which is 1/4" liquid, 3/8" suction, and 1/2" insulation. I'm also assuming the entire unit will need to be recharged, as the lines aren't precharged.
Does this sound right to you, or are there other options? Anything else I should stay aware of? I've never dealt with used mini splits before.

LG outdoor unit LMU247HV
LG indoor unit LMN126HVT
Lineset I'm looking at THS14381230FN
Click to expand...


If the valves at the outdoor unit were shut when they were disconnected then go for it. If not then avoid it. The oil used in the compressor loves moisture. So if valves were left open the oil is bad and impossible to change.
 
Quote Reply

outwest

Supporter
Premium Gardener
Posts
4,629
Reactions
10,152
Joined
Dec 10, 2011
Points
263
May 9, 2012
#167
Hey CJ - What kind of preventative/regular maintenance should I expect to perform on my portable AC? Thanks.

outwest
 
Quote Reply

sgt. schultz

Posts
282
Reactions
70
Joined
Feb 19, 2009
Points
28
May 9, 2012
#168
CannabisJohn said:
It's called a split system. I would use 7000-7500 btus per 1 kw of light which would mean u need a 15,000 or so for flower room and maybe an additional 6-9000 for veg room. So I believe a 2 ton should be good. If you oversize too much then it will cycle too much which is bad.
Click to expand...

3 ton is free which makes 2 ton kinda out of question. Unless 2 ton window unit (I never know how to seal light out of window unit) is cheaper than installing and charging free 3 ton split (not mini-split). Could I add 1k and be gold? Thanks bro. Not many places to turn for advice in Bible Belt.
 
Quote Reply

El Cerebro

Posts
1,197
Reactions
815
Joined
Jul 8, 2011
Points
113
May 9, 2012
#169
CannabisJohn said:
If you oversize too much then it will cycle too much which is bad.
Click to expand...
Aside from just doing the math, any tips for staying within reasonable intervals? This has been a worry of mine for when I upgrade, was leaning more toward inverter mini hoping that would eliminate some stress with a bigger operating range. Is this correct thinking?
 
Quote Reply

sgt. schultz

Posts
282
Reactions
70
Joined
Feb 19, 2009
Points
28
May 10, 2012
#170
I think I answered my own question. Have always been under-cooled going by Cali estimates even when I added 25%. Gonna run 3 ton, which could be barely enough, and if it's to much, I'll add 1k which would be excellent default. Thanks bro.
 
Quote Reply

500lbs Guerilla

Posts
334
Reactions
273
Joined
Aug 9, 2009
Points
63
May 10, 2012
#171
CannabisJohn said:
If the valves at the outdoor unit were shut when they were disconnected then go for it. If not then avoid it. The oil used in the compressor loves moisture. So if valves were left open the oil is bad and impossible to change.
Click to expand...

Good info! Here's a pic of the valves. Everything is screwed down tight - not so tight that I can't loosen it with my hand, but all the way down. Does that mean the valves are closed?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 10, 2012
#172
outwest said:
Hey CJ - What kind of preventative/regular maintenance should I expect to perform on my portable AC? Thanks.

outwest
Click to expand...

Filter cleaning and condenser coil clean.
 
Reactions: outwest
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 10, 2012
#173
El Cerebro said:
Aside from just doing the math, any tips for staying within reasonable intervals? This has been a worry of mine for when I upgrade, was leaning more toward inverter mini hoping that would eliminate some stress with a bigger operating range. Is this correct thinking?
Click to expand...


If you want to oversize for future or as a just in case do it with a high grade inverter style mini split if possible. The compressor will slow down to match heat load. Can't do that with a regular split system.
 
Reactions: El Cerebro
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 10, 2012
#174
500lbs Guerilla said:
Good info! Here's a pic of the valves. Everything is screwed down tight - not so tight that I can't loosen it with my hand, but all the way down. Does that mean the valves are closed? View attachment 216308
Click to expand...

Look under the large caps. There is a allen wench operated valve in each one. All 4 valves need to be closed. Just pinching the copper tubing is not enough. If you aren't sure, remove caps and attach a pic with caps removed.
 
Quote Reply

outwest

Supporter
Premium Gardener
Posts
4,629
Reactions
10,152
Joined
Dec 10, 2011
Points
263
May 10, 2012
#175
CannabisJohn said:
Filter cleaning and condenser coil clean.
Click to expand...

Awesome. How frequently? It will be running probably until October. Gracias.

outwest
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 10, 2012
#176
Filter check once a month. Condenser check every 3-4 months.
 
Reactions: outwest
Quote Reply
B

bakershredhead

Posts
206
Reactions
15
Joined
Oct 11, 2009
Points
18
May 10, 2012
#177
Hey CJ just posted in the cooling section as I didn't see a sticky for ya there, hopefully you'll have an answer for me.
I was going to renovate my shop which is 24x24 and run 20kw bare bulb but I don't think my 200 amp service will be enough. So I'm thinking of building two rooms 12x24 each and using my prexisting split 3.5 ton a/c, with a motorized damper so it can cool each room when the lights are on. This will save me a bit of cash as I've already got a custom flip box from Olyver (thanks buddy) and all of my ballast taken care of. I'm wondering if anyone can help in building the motorized damper as Excel air wants 2300 for there unit. It seems that the material should be only 300 to 400. I could be way off but I looked at 12 inch motorized dampers and there only 70 a piece. I know there also another part of the unit but 2300 seems pretty steep. Am I missing something here?​
 
Reactions: El Cerebro
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
May 11, 2012
#178
bakershredhead said:
Hey CJ just posted in the cooling section as I didn't see a sticky for ya there, hopefully you'll have an answer for me.
I was going to renovate my shop which is 24x24 and run 20kw bare bulb but I don't think my 200 amp service will be enough. So I'm thinking of building two rooms 12x24 each and using my prexisting split 3.5 ton a/c, with a motorized damper so it can cool each room when the lights are on. This will save me a bit of cash as I've already got a custom flip box from Olyver (thanks buddy) and all of my ballast taken care of. I'm wondering if anyone can help in building the motorized damper as Excel air wants 2300 for there unit. It seems that the material should be only 300 to 400. I could be way off but I looked at 12 inch motorized dampers and there only 70 a piece. I know there also another part of the unit but 2300 seems pretty steep. Am I missing something here?​
Click to expand...


Yes there is another part or two. You'll need another stat and a zoning board. Google residential zoning controls. That should get what you need for $600-800. Still expensive but cheaper than $2300. This , if done properly, will allow either room to call for cooling. There are other ways to do it but I think for a DYI that zoning controls are easiest. PM me if you want to go the hard but possibly less expensive way.
 
Reactions: El Cerebro
Quote Reply

500lbs Guerilla

Posts
334
Reactions
273
Joined
Aug 9, 2009
Points
63
May 12, 2012
#179
CannabisJohn said:
Look under the large caps. There is a allen wench operated valve in each one. All 4 valves need to be closed. Just pinching the copper tubing is not enough. If you aren't sure, remove caps and attach a pic with caps removed.
Click to expand...

Can you tell from this photo?
 

Attachments

  • valve.JPG
    108.1 KB · Views: 212
Quote Reply

sox

Posts
1,954
Reactions
4,963
Joined
Mar 19, 2012
Points
263
May 12, 2012
#180
CannabisJohn said:
All depends on how much it runs. My guess is with only 1200 watts that it won't run a ton so it most likely won't lower it too much but it'll lower it. The humidifier may keep up.
Click to expand...

I put a frigidair portable, 1030w, 9000btu in my room 10-12-8, two 600hps...But its HOT at my grow house, like 85+ all the time.
How often should i run this thing, and do you think ill run into humidity problems?
 
Quote Reply
Page 9 of 119 · Replies 161–180 of 2,371
Prev
  • 1
  • …
  • 7
  • 8
  • 9
  • 10
  • 11
  • …
  • 119
Next
First Prev 9 of 119 Next Last

Thread info

Replies 2,370
Views 421,603
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • J
    Is it ready to harvest
    • Latest: josh65
    • 20 minutes ago
    Photography Help
  • 2026 Outdoor Grows! let's see em!
    • Latest: EastCoastOutdoor
    • 29 minutes ago
    General Outdoor Growing
  • J
    Virginia Growers Thread - Everything VA
    • Latest: josh65
    • Today at 3:18 PM
    Basic Growing Information
  • How Little PPM can they handle?
    • Latest: WinJr63
    • Today at 3:03 PM
    Basic Growing Information
  • how to Bubble washing and tips 2024
    • Latest: WinJr63
    • Today at 2:53 PM
    Concentrates & Processing
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?