Grow Room A/C

  • Thread starter Thread starter CannabisJohn
  • Start date Start date Mar 22, 2012
  • Tagged users Tagged users None

Grow Room A/C

CannabisJohn Mar 22, 2012 2,370 Replies 421,650 Views
Page 106 of 119 · Replies 2,101–2,120 of 2,371
Prev
  • 1
  • …
  • 104
  • 105
  • 106
  • 107
  • 108
  • …
  • 119
Next
First Prev 106 of 119 Next Last

EventHorizan

Posts
15,707
Reactions
49,496
Joined
Jul 6, 2016
Points
438
Apr 19, 2017
#2,101
StonedBlue said:
So where does the air being exhausted come from if not room air? Seems like if you don't want room air being exhausted you'd have to have outside air brought in. That air being exhausted has to come from somewhere right?
Click to expand...
yes see the black duct? It hook to a register in my floor and sucks air thru it, down thru the compressor, and out thru a dryer vent. I can drop my temp to 70 with lights on, 1800 watts hps, plus dealing with the heat when the dehuey kicks on...
 
Quote Reply

EventHorizan

Posts
15,707
Reactions
49,496
Joined
Jul 6, 2016
Points
438
Apr 19, 2017
#2,102
DemonTrich said:
I have a single hose LG 14k portable and it FN rocks! I can get 3x600 to 70* lights on and have the unit cycle on/off. With the 1260cmh it's easy Pease. Can do 68* lights on easily.

But alas, she's a power monger vs a mini split.
Click to expand...
i have a single hose lg and it rocks too... I had to build the intake box of course, but its a beast!
 
Quote Reply

StonedBlue

Supporter
Disabled Vet
Posts
270
Reactions
202
Joined
Jul 27, 2015
Points
43
Apr 19, 2017
#2,103
I don't have one yet but yes a window unit is what I'm talking about.
Where does the air come from that is exhausted out the back? If the only connection to the window is the hose exhausting from back of unit that air has to come from room, no?
 
Reactions: EventHorizan
Quote Reply

EventHorizan

Posts
15,707
Reactions
49,496
Joined
Jul 6, 2016
Points
438
Apr 19, 2017
#2,104
StonedBlue said:
I don't have one yet but yes a window unit is what I'm talking about.
Where does the air come from that is exhausted out the back? If the only connection to the window is the hose exhausting from back of unit that air has to come from room, no?
Click to expand...
i think you might be getting a window unit and a portable confused.. If its a window unit, then you dont need anything, just put it in the window.
If its a portable, and it only has an exhaust then you have to build a box that wraps around the intake vent in the rear(prob closest to bottom) and run a intake to that box. It can be a very tough build.
 
Quote Reply

MikeyMike01

Posts
5
Reactions
6
Joined
Apr 19, 2017
Points
3
Apr 20, 2017
#2,105
CannabisJohn said:
If you're in SoCal why are you trying to be so stealth? One mini split on a warehouse roof doesn't mean anything in socal. It means you have a small area to cool. Your friend's a/c units are gonna fry. Bad way to do it. The condenser needs to be outside
Click to expand...

I'm sub leasing a portion of the warehouse from a friend, he know what I'm doing but he want me to be discreet because the warehouse is part of a multi unit building. I'm planning to do 2 20x10 room with 6 light each. Going to need 4 mini spilt and it's going to bring attention if I have 4 condenser on the roof. Just trying to find way to be stealth as possible. Don't mind putting out the money. @CannabisJohn have u ever heard or use these commercial portable Ac unit?
 
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 20, 2017
#2,106
MikeyMike01 said:
I'm sub leasing a portion of the warehouse from a friend, he know what I'm doing but he want me to be discreet because the warehouse is part of a multi unit building. I'm planning to do 2 20x10 room with 6 light each. Going to need 4 mini spilt and it's going to bring attention if I have 4 condenser on the roof. Just trying to find way to be stealth as possible. Don't mind putting out the money. @CannabisJohn have u ever heard or use these commercial portable Ac unit?
Click to expand...

Why 4 mini splits when you only have 2 rooms? You need 3 tons per room with 6 lights or you can do a single zoned 4 ton conventional split unit to do both rooms. They make commercial portable units but they are super expensive and guzzle electricity.
 
Reactions: MikeyMike01 and Confuten1
Quote Reply

MikeyMike01

Posts
5
Reactions
6
Joined
Apr 19, 2017
Points
3
Apr 20, 2017
#2,107
CannabisJohn said:
Why 4 mini splits when you only have 2 rooms? You need 3 tons per room with 6 lights or you can do a single zoned 4 ton conventional split unit to do both rooms. They make commercial portable units but they are super expensive and guzzle electricity.
Click to expand...

Thanks cannbisjohn, you are right! After talking to more experienced growers at a gathering yesterday they said the same exact thing as you.

Happy 420 guys.
 
Reactions: EventHorizan
Quote Reply

StonedBlue

Supporter
Disabled Vet
Posts
270
Reactions
202
Joined
Jul 27, 2015
Points
43
Apr 20, 2017
#2,108
I can't put it in the window. That is whole point. I thought I could build a box and keep unit hidden.
If i was going to put it in the window I wouldn't be building a box.
 
Reactions: EventHorizan
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 20, 2017
#2,109
MikeyMike01 said:
Thanks cannbisjohn, you are right! After talking to more experienced growers at a gathering yesterday they said the same exact thing as you.

Happy 420 guys.
Click to expand...
Where are u located?
 
Reactions: StonedBlue and EventHorizan
Quote Reply

MikeyMike01

Posts
5
Reactions
6
Joined
Apr 19, 2017
Points
3
Apr 20, 2017
#2,110
CannabisJohn said:
Where are u located?
Click to expand...
Los Angeles county,
 
Reactions: StonedBlue and EventHorizan
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 21, 2017
#2,111
MikeyMike01 said:
Los Angeles county,
Click to expand...

If you need the a/c done right let me know.
 
Reactions: StonedBlue, EventHorizan, DemonTrich and 1 other person
Quote Reply

Confuten1

Supporter
exploitin strengths - perfectin weaknessess
Posts
1,930
Reactions
3,653
Joined
May 19, 2010
Points
263
Apr 21, 2017
#2,112
CannabisJohn said:
If you need the a/c done right let me know.
Click to expand...

And when he says done right , thats an understatement. Hes done several rooms for me. Jon gets down and is an expert in HVAC growroom design and implementation.
What up @CannabisJohn
 
Reactions: StonedBlue, sixstring, EventHorizan and 1 other person
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 22, 2017
#2,113
Confuten1 said:
And when he says done right , thats an understatement. Hes done several rooms for me. Jon gets down and is an expert in HVAC growroom design and implementation.
What up @CannabisJohn
Click to expand...

Thanks for the kind words. What's up?
 
Reactions: StonedBlue and EventHorizan
Quote Reply

MikeyMike01

Posts
5
Reactions
6
Joined
Apr 19, 2017
Points
3
Apr 23, 2017
#2,114
CannabisJohn said:
Thanks for the kind words. What's up?
Click to expand...

Thanks guys, will keep that in mind
 
Reactions: StonedBlue and EventHorizan
Quote Reply

EventHorizan

Posts
15,707
Reactions
49,496
Joined
Jul 6, 2016
Points
438
Apr 23, 2017
#2,115
StonedBlue said:
I can't put it in the window. That is whole point. I thought I could build a box and keep unit hidden.
If i was going to put it in the window I wouldn't be building a box.
Click to expand...
well post a pic of the one your thinking about using..
 
Reactions: StonedBlue
Quote Reply

StonedBlue

Supporter
Disabled Vet
Posts
270
Reactions
202
Joined
Jul 27, 2015
Points
43
Apr 24, 2017
#2,116
Ifound a good explanation and diagram on ig at https://www.icmag.com/ic/showthread.php?t=95491
It does say however, not to use a single box in most circumstances but two sprays boxes, one in one out.
 
Reactions: EventHorizan
Quote Reply

DemonTrich

Posts
6,394
Reactions
15,047
Joined
Feb 20, 2015
Points
313
Apr 24, 2017
#2,117
I'll need to swap out or upgrade my current 14k but portable. Might look into a window shaker and do the box mod.
 
Reactions: StonedBlue and EventHorizan
Quote Reply

EventHorizan

Posts
15,707
Reactions
49,496
Joined
Jul 6, 2016
Points
438
Apr 24, 2017
#2,118
StonedBlue said:
Ifound a good explanation and diagram on ig at https://www.icmag.com/ic/showthread.php?t=95491
It does say however, not to use a single box in most circumstances but two sprays boxes, one in one out.
Click to expand...
Seems simple enough... I understand now what you want.
 
Reactions: StonedBlue
Quote Reply

bdank

Posts
59
Reactions
48
Joined
May 4, 2013
Points
18
Apr 24, 2017
#2,119
Has anybody ever dealt with a quietside. Something happened to my mini split where it cycles power on both head units (Very fast on off cycles) and won't stay heating or cooling (switches itself). Got a u8 error which i can't find an explanation for as well. Thought the out side condenser unit got fried from a past brown out problem but replaced it yesterday $$ and its doing the exact same thing? My last guess is humidity messed up the indoor head units but idk. The cooling and heating do work, when the unit stays set on one mode, but that doesn't last. model : qsfmo-q4
 
Reactions: StonedBlue
Quote Reply

CannabisJohn

Posts
1,063
Reactions
696
Joined
Jun 19, 2010
Points
113
Apr 24, 2017
#2,120
bdank said:
Has anybody ever dealt with a quietside. Something happened to my mini split where it cycles power on both head units (Very fast on off cycles) and won't stay heating or cooling (switches itself). Got a u8 error which i can't find an explanation for as well. Thought the out side condenser unit got fried from a past brown out problem but replaced it yesterday $$ and its doing the exact same thing? My last guess is humidity messed up the indoor head units but idk. The cooling and heating do work, when the unit stays set on one mode, but that doesn't last. model : qsfmo-q4
Click to expand...

Not sure but check this out. https://www.manualslib.com/manual/811907/Quietside-Qs09-Vp115.html?page=33#manual. Not your model but most likely same error code meaning for both units. I would also turn off power and check all wiring connections of power wiring to outdoor unit and also wiring between indoor and outdoor unit. If you already replaced that board then contact Quietside tech support.
 
Reactions: EventHorizan
Quote Reply
Page 106 of 119 · Replies 2,101–2,120 of 2,371
Prev
  • 1
  • …
  • 104
  • 105
  • 106
  • 107
  • 108
  • …
  • 119
Next
First Prev 106 of 119 Next Last

Thread info

Replies 2,370
Views 421,650
Started Mar 22, 2012
Latest post Jan 10, 2024
Starter CannabisJohn
Forum Growroom Design & Setup

Latest posts

  • Eternal Sun 2026 outdoor garden grow
    • Latest: Beazy
    • Today at 12:30 AM
    General Outdoor Growing
  • 40 days into cure , no change in smell or flavor
    • Latest: logic
    • Yesterday at 11:38 PM
    Cannabis Infirmary
  • 2026 Outdoor Grows! let's see em!
    • Latest: EternalSun
    • Yesterday at 11:36 PM
    General Outdoor Growing
  • Tumble stumbles upon a Spider Farmer clip on fan.. Growing Blue Cheese, North Thunderfuck, Cali Blues, and Bruce Banner #2
    • Latest: Tumbleweed375
    • Yesterday at 11:36 PM
    Grow Diaries
  • What Is the Best Way to Improve and Maintain Topsoil for a Healthy Garden?
    • Latest: compostmike
    • Yesterday at 11:25 PM
    Organic Soil
  • Home
  • Forums
  • Medical Cannabis Cultivation
  • Growroom Design & Setup
  • Grow Room A/C
  • Contact us
  • Terms and rules
  • Privacy policy
  • Help
  • Home
Community platform by XenForo® © 2010-2026 XenForo Ltd.
Menu
Log in

Sign up

  • Home
  • News
  • Classifieds
  • Forums
    • What's new Featured content New posts New Articles New articles New products Latest activity
  • Social
  • Strains
  • Live
  • Learn
  • Brands
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?