Yes they are inverter type with a heat pump. When the unit trips the E1 code it shuts off the compressor. We have to then power off the unit & turn the unit back on to reset it. There's only one service valve for the suction line, the liquid line has no service valve. When I installed the units I vacuum, then pump nitrogen to check for leaks & vacuum again and open the service valve. They all trip at different times it could be hot or cold outside. Don't know what pressure cause the error code because we don't know when the unit going to trip I waited for 8 hours and the unit runs fine and then come back later to find it trip E1. The line sets are 15 ft long which the units come factory charged for. My next step is recover 1 oz of freon out of one unit and 2 oz out of another to see if that works if not I can then put the freon back in. Do you think since there such a high heat load the unit needs less freon to operate.